Topic: Wire Size

User: Alwayslearningelec, Location: NJ

Asked on: Friday, October 31, 2025 at 2:54 pm EDT
Answered on: Friday, October 31, 2025 at 3:00 pm EDT

Question: I know I'm sure I've asked this before, shame on me.So if the breaker is 150A but the combo starter at the exhaust fan is 200A and fan HP is 60HP at 480v. what is the order/ process of sizing.I don't see a FLA in the EF schedule but I believe you start by calculating the motor load(amps), then you size the OCPD? But there are two, the starter and the breaker.The wire should be sized to the 200A starter/disco or 150A breaker?

Okay, let's break down the process for sizing the conductors, overload protection, and short-circuit and ground-fault protection (OCPD) for this 60HP, 480V exhaust fan motor. This is a common source of confusion, so don't worry about having asked before. It's better to get it right.Here's the correct sequence and reasoning

1. Determine the Motor's Full-Load Amps (FLA):
You cannot rely on the nameplate amps for sizing anything other than the motor overload protection. You MUST use the values from NEC Table 430.250. This table provides the standard FLA values for motors based on HP and voltage. For a 60HP, 480V motor, the FLA from Table 430.250 is 77 Amps. This is crucial.2. Size the Motor Overload Protection

The motor starter/combo starter contains the

motor overload protection
. This is a separate function from the breaker, which protects against short circuits and ground faults. NEC 430.32 governs motor overload protection. Typically, you use overload relays (often bimetallic or electronic) in the starter. The overload protection is sized based on the motor's nameplate FLA. Since you do not have this, you should be looking into how to aquire this, ask the engineer of the fan, look at the manufacture. If you still do not have this, you can make some assumptions as the NEC states in 430.6(A)(1) NEC 430.6(A)(1) states the following, For standard motors, the values given in Table 430.247, Table 430.248, Table 430.249, and Table 430.250 shall be used instead of the actual current rating marked on the motor nameplate Because of this the overload can be sized at 125% of the 77 Amps FLA from the table. 77 1.25 = 96.25A3. Size the Branch-Circuit Conductors (Wires)



NEC 430.22
governs conductor sizing for motor circuits. The conductors must have an ampacity of at least 125% of the motor FLA (from Table 430.250, not the motor nameplate, and not the starter size). Therefore, the required ampacity is 77 Amps 1.25 = 96.25 Amps. Select the wire size based on the appropriate ampacity table (NEC 310.16) for the conductor insulation type and installation conditions (temperature rating, conduit type, etc.). You'll likely need at least a #3 AWG copper conductor (check the ampacity table for your specific situation).4. Size the Branch-Circuit Short-Circuit and Ground-Fault Protective Device (Breaker)

This is the breaker that protects the entire branch circuit from short circuits and ground faults, including the conductors, starter, and motor.

NEC 430.52
governs the sizing of this breaker. This is the section that allows you to use a breaker significantly larger than the motor FLA to accommodate motor starting inrush current. For a standard motor, you can use a non-time-delay fuse up to 300% of the motor FLA, or an inverse time breaker up to 250% of the motor FLA. (Check the specific motor code letter on the motor nameplate; it may limit this percentage). Calculate

Breaker: 77 Amps 2.50 = 192.5 Amps

Select the next higher standard breaker size

In this case, the next higher standard breaker size to 192.5A is

200 Amps
.5. Verify the Starter/Disconnect Rating

The starter/disconnect (the combo starter) must have an ampacity rating

equal to or greater than 115% of the motor's FLA
. This ensures it can handle the continuous load of the motor. NEC 430.110(A) states the disconnecting means shall have an ampere rating of at least 115 percent of the full-load current rating of the motor. In your scenario, the starter/disconnect is rated at 200A which is already greater than the 115%Summary for your situation



Motor FLA (from NEC Table 430.250)

77 Amps

Conductor Ampacity

96.25 Amps (use wire sized accordingly - likely #3 AWG copper)


Motor Overload Protection

Sized to 96.25A or below.

Branch-Circuit Breaker

200 Amps


Starter/Disconnect Rating

200 Amps (Adequate)

Important Considerations



Motor Nameplate

While you use Table 430.250 for most calculations,
always refer to the motor nameplate for the motor's service factor, temperature rating, and code letter. The code letter impacts the maximum breaker size.

Ambient Temperature

Derate conductor ampacity if the ambient temperature is higher than the temperature rating of the conductor insulation.

Conduit Fill

Ensure the conduit is properly sized for the number and size of conductors.


Voltage Drop

Calculate voltage drop to ensure it's within acceptable limits. Excessive voltage drop can damage the motor.

Local Codes and Regulations

Always comply with all applicable local codes and regulations.

In Summary


FLA from Table

Use the
Table* value for conductor sizing and breaker sizing.2.

Conductors

Sized at 125% of the FLA from the Table.3.

Breaker

Sized per 430.52 (usually up to 250% for inverse time breakers) based on the motor FLA from the Table.
4.


Overloads

Based on motor nameplate FLA.5.

Starter/Disconnect:
Must be rated at least 115% of the motor FLA from the table.Following this process ensures you comply with the NEC and provide adequate protection for the motor and the electrical system. If you are uncomfortable doing this calculation, hire a professional electrician to do so. Flag for review