Topic: Grounding on legacy system.

User: SKhaja, Location: Illinois

Asked on: Friday, October 31, 2025 at 3:36 pm EDT
Answered on: Friday, October 31, 2025 at 3:41 pm EDT

Question: Gentlemen,Have a question here about converting a TN-C ground system to TN-S.we want to run 4/C cables plus ground cable to an existing main junction box that only has cables for 3-phase and neutral. This junction box sends cables to two existing service mains.can any one give some advice on how to proceed on this as per the NEC?My initial thinking has been to install a earth terminal board and connect to the ground at main jb, run the separate ground wires from JB to existing two service mains.Thanks in advance for the input.

Okay, let's break down the situation and how to approach converting a TN-C (combined neutral and earth) system to a TN-S (separate neutral and earth) in a manner that's generally compliant with the NEC, recognizing that local interpretations can vary. This situation also assumes you are in the US and subject to NEC requirements. If not, your local electrical codes take precedence.

Understanding the Difference: TN-C vs. TN-S TN-C (Protective Multiple Earthing - PME, also called PEN)

The neutral and protective earth (ground) functions are combined into a single conductor (PEN conductor). This is common in some older installations. The downside is that a broken PEN conductor can put fault current on equipment chassis.


TN-S (Separate Protective Earth)

The neutral and protective earth (ground) are entirely separate conductors from the supply transformer onwards. This is generally considered safer as it provides a dedicated path for fault current.

The Goal

To separate the neutral and ground conductors and provide a dedicated equipment grounding conductor to your new circuits.

Here's a step-by-step approach, following general NEC principles (always consult a qualified electrician for on-site evaluation and code compliance)


Safety First: De-energize the Existing Main Junction Box.
This is absolutely critical. Use appropriate lockout/tagout procedures to ensure the power is off and remains off while you're working. Verify with a meter.2. Identify Existing Conductors

Clearly identify the existing phase conductors (L1, L2, L3) and the neutral conductor. The neutral conductor is likely a PEN conductor if it's a TN-C system.3.

Assess the Existing Grounding Electrode System (GES)

You need to know how the original system was grounded.

Existing Ground Rods/Plates/Concrete Encased Electrode

Is there a ground rod, plate, or concrete-encased electrode connected to the neutral at the main service entrance? This is mandatory in most NEC-compliant services.


Metal Water Pipe

Is the grounding electrode conductor connected to a metal water pipe? If so, there will likely be additional requirements.

Sizing of Grounding Electrode Conductor

What size is the existing grounding electrode conductor? You'll likely need to maintain or upgrade this depending on the service size.4.

Install the Equipment Grounding Terminal Bar



Location

Within the existing main junction box. It must be electrically connected to the metal enclosure of the junction box.

Connection to Enclosure

Ensure a solid, low-impedance connection between the terminal bar and the metal enclosure. Clean the metal surfaces and use appropriate hardware for a good electrical bond.


Size

Size the terminal bar appropriately for the number and size of the equipment grounding conductors you will be connecting to it.5.

Connect the Grounding Electrode Conductor to the Terminal Bar

This is a critical step. The grounding electrode conductor (from the ground rod, water pipe, etc.) must be connected to this new ground bar. The size of this conductor is dictated by NEC Table 250.66 (based on the size of the service entrance conductors).
6.


Separating the Ground and Neutral



This is where it gets tricky and requires careful planning. You cannot simply separate the neutral and ground in the existing main junction box without further modification to the service. The neutral-to-ground bond must remain at the service entrance (where the utility provides the service).
The existing main junction box is unlikely to be your service entrance. If you are only adding circuits to an existing panel you are not converting to a TN-S system. You are simply adding an equipment grounding conductor to new branch circuits, which is always a good practice. The neutral and ground will remain bonded in the existing service panel. If you want to convert the entire system to TN-S

This requires a more significant change, potentially involving a new service disconnect switch, a new neutral-ground bond at that service disconnect, and running separate neutral and ground conductors from that new disconnect to your existing main junction box and service mains.

This is a significant undertaking, and you MUST consult with a qualified electrical engineer or master electrician with experience in service upgrades.
7. Running New 4/C + Ground Cables

Connect the phase conductors (L1, L2, L3) and the neutral conductor to the appropriate terminals in the main junction box. Connect the equipment grounding conductor (the separate green or bare wire) to the newly installed equipment grounding terminal bar in the junction box. Run these 4/C+G cables to your two existing service mains. At the service mains, connect the phase conductors and neutral as before, and connect the equipment grounding conductor to the ground bar in those service mains.

Do NOT bond the neutral to the ground in these downstream service mains.
The neutral-ground bond must only occur at the service entrance.8. Review Existing Downstream Subpanels/Panels

Examine any downstream subpanels. Verify that the neutral and ground are not bonded in these subpanels. In a properly wired system, the neutral and ground are only bonded at the service entrance.9.

Testing



Ground Resistance

Test the ground resistance of the grounding electrode system. The NEC doesn't specify a maximum ground resistance, but a low resistance to earth is desirable (25 ohms or less is a common target).


Continuity

Verify continuity between the grounding terminal bar in the main junction box, the grounding terminals in the two service mains, and the enclosures of all equipment.

Voltage Drop

Check voltage drop under load on the new circuits to ensure proper sizing of conductors.

Important Considerations and Cautions



Overcurrent Protection

Ensure all new circuits have appropriate overcurrent protection (circuit breakers or fuses) sized according to the ampacity of the conductors.

Arc-Fault Circuit Interrupters (AFCIs) and Ground-Fault Circuit Interrupters (GFCIs)

Consider whether AFCI and/or GFCI protection is required for the new circuits, based on the NEC requirements for the specific locations they will serve.


Documentation

Keep detailed records of all work performed, including conductor sizes, grounding electrode system details, and test results.

Permitting and Inspection

Obtain any necessary permits and have the work inspected by a qualified electrical inspector.


Aluminum Conductors

If using aluminum conductors, use the appropriate connectors and anti-oxidant compounds.

Existing System Condition

The age and condition of the existing electrical system may necessitate upgrades beyond simply adding the new circuits.

Why You Need a Qualified Electrician



Code Compliance

Electrical codes are complex and constantly evolving. A qualified electrician will ensure the work meets all applicable requirements.

Safety

Working with electricity is inherently dangerous. A qualified electrician has the training and experience to perform the work safely.


System Compatibility

An electrician can assess the existing electrical system and ensure that the new circuits are compatible with it.*

Liability

If the work is not performed correctly, it could create a safety hazard and expose you to liability.In summary, carefully plan the separation of neutral and ground, ensure a robust grounding electrode system, connect the equipment grounding conductors correctly, and

always
consult with a qualified electrician to ensure a safe and code-compliant installation. The core principle is to ensure a low-impedance path for fault current to return to the source, tripping the overcurrent protective device. Flag for review