Topic: HVAC System / LED Dimmers Not Getting Along

User: A/A Fuel GTX, Location: WI & AZ

Asked on: Friday, October 31, 2025 at 6:34 pm EDT
Answered on: Friday, October 31, 2025 at 6:35 pm EDT

Question: Have a customer with a new home with a high end HVAC system. DC, variable speed, etc. When the system is in the cooling mode, the LED's in recessed cans throughout the house flicker randomly. The dimmers controlling the cans are LED rated. I recall a previous job awhile back where the well pump had the same effect on LED's/Dimmers. I believe the well guy had to put some kind of filter on the constant pressure well pump to alleviate the problem. Has anyone else had this problem? TIA

You're on the right track. What you're describing is likely harmonic distortion being introduced into the electrical system by the variable speed HVAC system (similar to what you saw with the well pump). Here's a breakdown of the problem and potential solutions

Understanding the Problem: Harmonic Distortion
What it is

Variable speed drives (VFDs) like those in your HVAC and well pumps chop the AC sine wave to control motor speed. This creates harmonics – frequencies that are multiples of the fundamental frequency (60 Hz in the US). These harmonics distort the voltage and current waveform.


How it affects LEDs

LED drivers are sensitive to voltage fluctuations. Harmonic distortion can cause the LED drivers to malfunction, leading to flickering, dimming, or even premature failure. Dimmers amplify the issue.

Why it's worse with modern systems

High-efficiency appliances and systems, while great for energy savings, often incorporate VFDs and other technologies that can generate harmonics.


Common Suspects

Variable-speed HVAC systems (compressors, fans) Variable-speed well pumps LED Lighting Solar Inverters Large banks of electronic devices (computers, servers) Electric Vehicle Chargers

Troubleshooting Steps
1. Confirm the Source



Isolate the issue

Does the flickering
only occur when the HVAC is running in cooling mode? If you can, temporarily disable the HVAC (or lower the speed) and see if the flickering stops.

Check voltage

Use a multimeter to monitor the voltage at the affected LED fixtures. Look for voltage fluctuations or irregularities when the HVAC is running. A true RMS meter is best.

Harmonic Analyzer

The ideal solution is to use a harmonic analyzer to measure the total harmonic distortion (THD) on the electrical system. This will quantify the problem and help you confirm the HVAC system as the source. An electrician with experience in power quality analysis should be able to do this.2.

Examine the HVAC System



Installation

Verify the HVAC system was installed correctly, following the manufacturer's instructions. Proper grounding is crucial.

Wiring

Check for loose connections or undersized wiring in the HVAC system's circuit.


Manufacturer Support

Contact the HVAC manufacturer or installer. They may be aware of known issues with that model and have recommended solutions.

Potential Solutions


Here are the most likely fixes, ranging from simpler to more complex:1. HVAC System Filter



Line Reactor or Harmonic Filter

This is often the most effective solution. A line reactor or harmonic filter installed on the HVAC system's incoming power line will reduce the amount of harmonic current injected into the electrical system.


Sizing

The filter must be properly sized for the HVAC system's horsepower/amperage and the level of harmonic distortion. Consult with an electrical engineer or power quality specialist to determine the correct size.

Installation

It should be installed as close to the HVAC unit as possible, on the line side of the disconnect.


Cost

Will Vary, but it may be worth a try before replacing the LEDs.2.

LED-Specific Solutions



Higher Quality LEDs

Replace the existing LED fixtures with higher-quality LEDs that are less susceptible to voltage fluctuations. Look for LEDs with better power factor correction (PF > 0.9).


LED Drivers with Harmonic Filtering

Some LED drivers are specifically designed to filter out harmonics.

Dedicated Circuits

If possible, put the LED lighting on a separate circuit from the HVAC system. This can help isolate the LEDs from the harmonic interference. This could also mean a 2-pole breaker to power the lights from the other phase, although this will require moving the neutral along with the hot.3.

Neutral Conductor



Adequate Sizing

Ensure that the neutral conductor for the affected circuits is adequately sized. Harmonic currents can overload the neutral conductor, leading to voltage distortion.

Dedicated Neutral

Consider running a dedicated neutral conductor for the LED lighting circuits back to the electrical panel.4.

Whole-House Solutions (More Complex and Expensive)



Harmonic Mitigation Panel

A harmonic mitigation panel installed at the main electrical panel can filter out harmonics from the entire electrical system. This is a more comprehensive solution but also more expensive.

Isolation Transformer

An isolation transformer can isolate the electrical system from the utility power, reducing the amount of harmonic distortion that enters the home.5.

Other Considerations



Dimmers

While you say they are LED-rated, try a different brand/model of LED dimmer. Sometimes, compatibility issues exist between specific LED fixtures and dimmers. Test with a standard (non-dimmable) LED to see if that resolves the issue.

Grounding

Verify that the entire electrical system is properly grounded. Poor grounding can exacerbate harmonic problems.

Important Notes



Consult an Expert

This type of problem is best addressed by an electrician with experience in power quality and harmonic mitigation. They can accurately diagnose the source of the problem and recommend the most effective solution.

Documentation

Document all troubleshooting steps, measurements, and solutions that you try. This will be helpful for future reference and for communicating with other professionals.


Safety:
Always follow proper electrical safety procedures when working with electrical systems.Good luck! This can be a tricky problem, but with a systematic approach, you should be able to find a solution. Flag for review