Topic: Leaving ABB VFDs off

User: Saturn_Europa, Location: Fishing Industry

Asked on: Saturday, November 1, 2025 at 4:55 pm EDT
Answered on: Saturday, November 1, 2025 at 4:55 pm EDT

Question: I work on a large fishing boat. There are 3 very expensive ABB VFDs that run deck winches. We’ve seen ground fault failures with the VFDs during ship yard maintenance. During this time, the VFDs are not in use and but are powered on. The main switch board had a ground fault and we traced the fault back to the ABB VFDs. The only solution was to replace the VFDs.Is it better to turn off the power to the VFDs if we’re not going to be using them for a few months?During ship yard maintenance there’s lots of welding and blackouts when switching from shore power to generator.The only downside I can see to leaving the VFDs powered down is possibly condensation accumulation.

You're right to be concerned about the ground faults in your ABB VFDs during shipyard maintenance. Replacing them is a costly and time-consuming solution, so prevention is key. Here's a breakdown of why powering down the VFDs is likely the best strategy in your situation, and how to mitigate the condensation risk

Why Powering Down is Probably the Best Approach
Welding and Electrical Noise

Shipyards are notoriously noisy environments electrically. Welding, especially, can generate significant voltage transients (spikes) and harmonic distortion that can damage sensitive electronic components like those in VFDs. Even if the VFDs are "idle," their internal circuits are still active and vulnerable when powered on. These transients can stress the insulation, potentially contributing to ground faults.


Power Fluctuations

The constant switching between shore power and generators, coupled with potential brownouts or blackouts, can also stress the VFD components. Voltage dips and surges are not good for delicate electronics.

Ground Fault Propagation

A ground fault elsewhere in the system could propagate to the VFDs if they are powered on. Even with good grounding practices, the interconnected nature of the electrical system means that a fault can "find" a path through the VFD.


Component Degradation

Even when idle, powered-on electronic components experience some degree of degradation over time due to heat and electrical stress. Removing the power source eliminates this.

Warranty Considerations

Check your warranty terms. Some warranties might be voided if the equipment is powered on unnecessarily during maintenance or under adverse conditions.

Addressing the Condensation Concern


Condensation is a valid concern, especially in a marine environment. Here's how to mitigate it:1. Thorough Inspection

Before powering down, carefully inspect the VFDs for any existing signs of moisture or corrosion. Note their condition for comparison upon reactivation.2.

Desiccant Packs

Place plenty of desiccant packs (silica gel or similar) inside the VFD enclosures. These will absorb moisture. Use a type of desiccant that changes color to indicate saturation. Replace the desiccant regularly during the shutdown period.3.

Ventilation (Controlled)

Ensure the VFD enclosures have some form of ventilation
without allowing direct entry of moisture. A small vent with a hydrophobic (water-repellent) filter can allow air circulation while preventing water ingress. If possible, leave the cabinet doors slightly ajar if the environment is not too harsh, and the air is dry.4.

Heaters

A better option than ventilation is to install small "anti-condensation" heaters inside the VFD cabinets. These are low-wattage heaters designed to maintain a slightly higher temperature inside the enclosure than the ambient air, preventing condensation. Thermostatically controlled heaters are best, so they only operate when needed.5.

Regular Monitoring

If possible, have someone inspect the VFDs periodically during the shipyard stay. Check the desiccant condition, look for any signs of moisture, and ensure the ventilation or heaters are working properly.6.

Pre-Power-Up Inspection

Before powering up the VFDs after the shipyard stay, perform a thorough inspection.
Remove and inspect the desiccant packs. Check for any signs of moisture or corrosion inside the enclosures. Test the insulation resistance of the VFD input and output terminals with a megohmmeter (megger) to ensure there are no ground faults or insulation breakdown. This is critical before applying power.7.

Gradual Power-Up

After confirming everything looks good, power up the VFDs gradually. If possible, start with just the control power (if separate) to allow the internal circuits to warm up slowly. Then, apply the main power. Monitor the VFDs closely for any signs of trouble.

Recommendations
1. Power Down During Shipyard

Given the risk factors (welding, power fluctuations, potential for ground fault propagation), powering down the VFDs during shipyard maintenance is the most prudent approach.2.

Implement Moisture Control

Use a combination of desiccant packs, ventilation/heating (if appropriate), and regular monitoring to prevent condensation.3.

Pre-Power-Up Inspection

Emphasize the importance of a thorough pre-power-up inspection, including megger testing, to catch any problems before you energize the VFDs.4.

Documentation

Keep detailed records of all inspections, maintenance, and power-down/power-up procedures. This will help you track the VFDs' condition and identify any potential problems early on.5.

Consult ABB:
Consider reaching out to ABB for specific recommendations on long-term storage and protection for your VFD models. They may have specific guidelines or recommended practices for your equipment. They might also suggest some input chokes or transient voltage surge suppressors.By taking these precautions, you can significantly reduce the risk of ground faults and extend the lifespan of your valuable VFDs. Flag for review