User: yesterlectric, Location: PA
Asked on: Sunday, November 2, 2025 at 8:30 pm EST
Answered on: Monday, November 3, 2025 at 1:14 am EST
Question: Hate that this may be a duplicate but I searched some and didn't see this one answered on the forum.This came up in a conversation about a design review recently and while I thought I knew the answer I felt I couldn't prove it. When applying 215.2 you perform 2 calculations and use the larger of the two:215.2A1: ampacity for the non-continuous load plus 125% of the continuous load (unless the breaker/assembly is rated for operation at 100% continuous load).215.2A2: ampacity for the maximum load to be served after the application of any adjustment or correction factorsMy question is related to 215.2A1. It would make sense that we would not need to apply adjustment (derating) for bundling for this section 215.2A1 because the bundling does not so much occur in the panelboard but occurs more in the conduit, cable trench, wireway, etc. However, what about correction (derating) for ambient temperature? I think not just like we do not derate the panelboard but it doesn't seem to be concretely worded to remove all doubt.
You've hit on a common point of confusion with Article 215. Let's break it down to provide a clearer understanding.
Your Understanding is Largely Correct
215.2(A)(1) vs. 215.2(A)(2)
It's absolutely crucial to perform both calculations and use the larger result. This is the key to properly sizing the feeder.
Adjustment Factors (Bundling)
You are correct in thinking that adjustment factors for bundling are generally NOT applied in 215.2(A)(1). The purpose of this section is to ensure the feeder has sufficient capacity to handle the calculated load, considering continuous loads at 125% (or 100% for appropriately rated OCPD/assemblies). Bundling derating addresses the impact of conductors heating each other up when they are physically close together over a significant length. The effects of bundling are more relevant to the portion of the circuit AFTER the panelboard.
Correction Factors (Ambient Temperature)
This is the core of your question, and where the nuance lies.
Ambient Temperature Correction and 215.2(A)(1)
While there isn't language specifically exempting 215.2(A)(1) from temperature correction in the code,
it is generally accepted industry practice to NOT apply ambient temperature correction to the conductor ampacity used in this calculation.
Here's the rationale for that industry-accepted approach:1. Focus on Load
215.2(A)(1) is fundamentally about ensuring the feeder can supply the calculated load. It's designed to ensure the feeder source has enough capacity.2.
Ambient Temperature Effects Elsewhere
Ambient temperature is primarily affecting the conductor itself. Since the portion of the circuit being discussed here is within the panelboard or immediately leaving it, the goal is to ensure the source is sufficient. The impacts of ambient temperature are then considered and addressed by the provisions of 310.15, which address how conductors are installed.
3.
Where to Correct
The impact of ambient temperature on conductors is addressed when sizing the conductors downstream of the panelboard, where they are installed, and for longer runs, the ambient temperature will have an impact. Therefore, ambient temperature corrections are more relevant when calculating the ampacity based on the installation conditions of the conductors (as in 215.2(A)(2) and 310.15). This is where you factor in conduit fill, bundling, and ambient temperature along the entire run of the conductors.4.
Panelboard Rating
It's also critical to remember that the panelboard itself has a maximum ambient temperature rating. This is separate from the conductor ampacity calculations, but equally important. You must ensure the panelboard is installed in an environment that meets its listing requirements.5.
310.15. In general you can use 310.15 as a guide for addressing ambient temperature.
When Might You Consider It?
Although not required, there are certain special cases where you might consider applying ambient temperature correction in 215.2(A)(1): Extremely High Panelboard Ambient
If the panelboard is installed in a location with an exceptionally high ambient temperature (approaching or exceeding the equipment rating), you might choose to be more conservative and apply a correction factor in addition to the panelboard's own temperature limits. This would be a judgment call based on specific conditions.
High-Density, Fully-Loaded Panelboards
In a very densely packed panelboard where many high-current breakers are continuously loaded, the internal temperature of the panelboard could be significantly higher than the surrounding ambient. Again, this is an extreme case.
Unusual Circumstances
As the engineer, there may be very unique circumstances where you decide that this calculation should be addressed, however, it would not typically be required.
In Summary
Always perform both 215.2(A)(1) and 215.2(A)(2) calculations. Generally, do not apply ambient temperature correction factors in 215.2(A)(1). Focus on applying ambient temperature and adjustment factors in 215.2(A)(2) and 310.15 based on the actual installation conditions of the conductors along their entire run. Always ensure the panelboard is installed within its listed ambient temperature limits.
Important Disclaimer: Electrical codes and interpretations can vary, and this information is for educational purposes only. Always consult with a qualified electrical engineer or inspector for specific project requirements and local code interpretations. Flag for review