Question: How would you handle this situation? Top of panel is about 6'. Spec says to use RGS below 7'6" so I'd have about 1' 6" of RGS. Would you really transition( think you'd be help to it for that short of a distance), use RGS for the entire run, write RFI or just run EMT the entire way.
Okay, let's break down this situation and the options, considering NEC (National Electrical Code) compliance, practicality, and cost-effectiveness.
Understanding the Situation Panel Height
Top of the panel is 6 feet from the floor (or grade).
Specification
RGS (Rigid Galvanized Steel conduit) is required below 7'6" (7.5 feet).
RGS Run Length
This leaves you with a very short run of RGS - about 1.5 feet (7.5' - 6' = 1.5').
Goal
Decide on the best conduit method for the entire run from the panel.
Options and Considerations1. Transition to EMT for the rest of the run
Pros
Potentially less expensive than RGS for the entire run.
Cons
Transitioning is impractical and could be a violation
1.5' is a very short distance to install a transition fitting. It's likely to be awkward, potentially not fully supported, and could even be against the spirit of the specification (which presumably requires RGS for protection in a vulnerable zone).
Code Issues
Consider 314.28(A) if this is a junction box with conductors of size #4 AWG and larger, the short length of the RGS run may not meet code requirements for sufficient length based on conductor size and number of bends.
Aesthetics
Might look less professional to have a transition in such a short distance.
Labor
Labor to make a clean and secure transition.
Overall
I would advise against this.2. Use RGS for the Entire Run
Pros
Compliance
Meets the specification without question.
Simplicity
No transitions to worry about. Easier to install overall (though RGS is heavier to work with).
Durability
RGS provides excellent physical protection.
Aesthetics
Consistent appearance.
Cons
Cost
RGS is more expensive than EMT.
Weight
RGS is significantly heavier and harder to work with, especially on longer runs.
Overkill
May be unnecessary if the upper portion of the run is in a protected location.3.
Write an RFI (Request for Information) / Clarification
Pros
Addresses the Ambiguity
Asks the specifying engineer/architect/client for clarification.
Potential Cost Savings
If the specification intent is purely for physical protection near the floor, they might approve EMT for the entire run, or a shorter section of RGS if the area above the panel is in a non-vulnerable location.
Defines Expectations
Gets the final answer from the responsible party, avoiding future issues.
Documents the Decision
Provides a record of the approved solution.
Cons
Time Delay
Requires waiting for a response.
No Guarantee
The RFI might be rejected, and you'll still need to comply with the original spec.4.
Use EMT for the Entire Run
Pros
Cost
EMT is less expensive than RGS.
Ease of Installation
EMT is lighter and easier to bend/cut/thread.
Cons
Violates Specification
Directly contradicts the requirement for RGS below 7'6".
Potential Rejection
Highly likely to be rejected by the inspector.
Recommendation
The best approach is almost always to write an RFI. Here's why:1. Clarify the Intent
The 7'6" requirement likely has a reason behind it (e.g., physical protection from impacts, water, etc.). Understanding the why helps you propose a sensible alternative, if one is acceptable.2.
Propose a Solution (in the RFI)
In your RFI, don't just ask the question. Instead, suggest a reasonable alternative, depending on the situation. For example: "The specification requires RGS conduit below 7'6". The top of the panel is at 6', resulting in only a 1.5' RGS run, which makes a transition impractical. We propose [
Option A
using RGS for the entire run] or [
Option B
using RGS for the run from the top of the panel to the floor, then transitioning to EMT higher up. Note: Option B requires additional support near the transition.] Please advise if either of these options is acceptable, or if the intent of the RGS specification can be achieved through other means."
Without more context, my thought process would be
If the spec MUST be RGS below 7'6", then write the RFI and recommend running RGS from the top of the panel to the floor and transition to EMT above the 7'6" mark.
If the RFI comes back denying any changes, then you'll be forced to use RGS for the entire run. While it might be overkill, you're complying with the specification, and that's ultimately the most important thing.
Important Considerations
Local Codes
Always check your local electrical codes for any additional requirements or restrictions on conduit types.
Environment
Consider the environment the conduit is in. Is it exposed to moisture, chemicals, or physical damage? This can influence the best choice.*
Accessibility: Will the conduit be easily accessible for future maintenance or modifications?Let me know if you have more details about the environment or application, and I can refine my recommendation! Flag for review