Question: Any thoughts on the following.240 volt floor heat that has been operational for 5 years.Abruptly stopped.Ohms readings are within Mfgr specsVoltage input correct.T-stat was swapped with one that’s operational in another part of the house.. Did not heat with that either.Haven’t seen the job. This info is from the owner who had a reputable electrician look at the situation.Thanks

Okay, based on the information provided, here's a breakdown of potential issues and troubleshooting steps that could be considered, even though a reputable electrician has already been there. Sometimes a fresh perspective can spark a new idea.

The Problem

240V floor heating stopped working suddenly despite good resistance readings and proper voltage input. A known good thermostat didn't solve the problem.

Possible Causes & Troubleshooting (Beyond the Obvious)



Hidden Break in the Heating Wire



The Trickiest Issue

While the overall resistance reads okay, there could be a very localized break in the heating wire itself. This is often temperature related. When the heat is called for and the wire energizes, this can be enough to keep the flow of electricity from working properly, causing it to "shut down."

Testing

An insulation resistance test, also known as a megger test, needs to be conducted on the cable itself. The megger test is a High-Voltage test, so be careful. The megger will help to identify any breakdown in the wire's insulation.


Infrared Camera

A thermal camera can sometimes reveal hot spots or cold spots along the heating cable. This might pinpoint the location of a break or short. This is often the best method.

Loose Connection (Really Check Everything)



Double-Check

Even though an electrician was there, REALLY double-check all connections at the thermostat, at the junction box where the heating element connects to the power, and any other intermediary points. A loose connection that's just barely making contact might pass a voltage test but fail under load. Look for signs of arcing, discoloration, or melted insulation.

Tighten Everything

Even if connections
look good, tighten them. Use the correct torque settings if known.

GFCI/AFCI Issues (If Applicable)



Nuisance Tripping

While you said voltage is correct, is it
consistently correct? Is the floor heat circuit protected by a GFCI or AFCI breaker? It might be tripping intermittently, even if it's not always tripped when the owner checks. Try temporarily bypassing the GFCI/AFCI (for testing purposes only and with extreme caution). Note: This should only be done by a qualified electrician.

Check for Other Loads

Are there any new appliances or electrical work done recently on the same circuit or near the floor heat circuit? Interference could be an issue.

Connection to Slab



Corrosion

Check to see if there is corrosion where the heating cable goes into the slab. If the cable can be accessed you can also try a continuity test.

Bad Heating Cable (Even with Okay Resistance)



Resistance Drift

Sometimes, the resistance can be within the manufacturer's specified range, but still be slightly off, or it can fluctuate erratically. A small change in resistance can impact the heating output significantly.

Short to Ground

Although you have a good resistance reading between the conductors, there might be a short between one of the conductors and the grounding/shielding of the cable. This can sometimes be detected with a megger test (insulation resistance test).


Specific Cable Type (If Known)



Self-Regulating Cables

If it's a self-regulating cable (less common for floor heat but possible), it might be malfunctioning. These cables adjust their heat output based on temperature, and a failure in the self-regulating mechanism could cause it to stop working.


Installation Issues (Long Shot, but Possible After 5 Years)



Overlapping Cables

If the heating cables were installed too close together or overlapping, this could create a hot spot and eventually lead to a cable failure. This would be hard to diagnose without tearing up the floor.


Damage During Installation

Even though it worked for 5 years, there could have been a small nick or cut in the cable during installation that finally degraded to the point of failure.

Recommendations


Insulation Resistance Test (Megger)

This is the most critical test to perform, as it can reveal insulation breakdown that a standard resistance test won't catch.2.

Careful Visual Inspection

A methodical visual inspection of all connections, wires, and the cable itself (where accessible) is essential. Look for any signs of damage, overheating, or corrosion.3.

Infrared Camera Scan

If possible, use an infrared camera to look for hot spots or cold spots along the cable when it's supposed to be heating.4.

Document Everything:
Meticulously document all readings, tests, and observations. This will help in troubleshooting and potentially in filing a warranty claim if the cable is still under warranty.Let me know if you have any other questions. Flag for review