User: Lbartowski, Location: MN
Asked on: Monday, November 3, 2025 at 9:16 am EST
Answered on: Monday, November 3, 2025 at 9:18 am EST
Question: Do both 1 and 2 hour rated walls required fire rated "putty packs" on any 1900 boxes that penetrate these walls?
The requirement for fire-rated putty packs on 1900 boxes (or any electrical box) penetrating a fire-rated wall depends on a few factors, and the answer isn't a simple yes or no. Here's a breakdown
Key Considerations:
Listing of the Wall Assembly
The most important factor is the
specific UL or other recognized testing lab listing for the fire-rated wall assembly. The listing will detail exactly what components are allowed, and how they must be installed to maintain the fire rating. This includes the type of wall board, studs, insulation, and crucially, penetrations. Penetration Types Allowed
The wall assembly listing will specify what types of penetrations are permitted (e.g., electrical boxes, pipes, ducts), and under what conditions. It will dictate:
Box Size and Type
Often, only specific box sizes and materials (metal vs. non-metallic) are allowed.
Box Spacing
There may be restrictions on how close boxes can be to each other within the wall, and how close they can be to the wall's edge.
Fill Material
This is where putty pads come in. The listing will specify if putty pads, fire-rated caulk, mineral wool, or other firestopping materials are required around the box. It will specify the required thickness and UL listing number.
Box Mounting
The listing may specify how the box must be mounted to the studs (e.g., using specific screws, clips, or brackets).
The Box Itself
The fire-rating listing will specify the box type rating and whether it needs to be inherently fire-rated.
General Guidelines, But DON'T Rely on These Alone
Maintaining Continuity
The general principle is that any penetration of a fire-rated wall should not compromise the wall's ability to resist fire and smoke spread. The penetrations themselves cannot create weak points in the wall.
Putty Pads as a Common Solution
Putty pads are a common and relatively inexpensive way to seal around electrical boxes to prevent the passage of fire and smoke. However, they are not a universal requirement.
In Summary
Consult the Fire-Rated Wall Assembly Listing
This is the only way to know for sure what's required. Get the specific UL (or other lab) listing number for the wall and carefully review the installation instructions and penetration details.2.
No Listing, No Approval
If there's no specific detail in the wall assembly listing covering electrical box penetrations, you'll need to consult with the fire marshal or building inspector for clarification and approval. They may require additional testing or a different solution.
Important Considerations
"Fire-Rated" Products are NOT All the Same
Just because a product is labeled "fire-rated" doesn't mean it's suitable for every situation. The product must be specifically listed for use in the specific fire-rated wall assembly.
Inspection
Fire-rated construction is carefully inspected. Improperly installed penetrations can lead to failing an inspection.
Therefore, the answer is "it depends on the specific wall assembly listing." You must* consult the listing documents to determine if putty pads or other firestopping materials are required for electrical boxes penetrating the wall. If the listing does not specify and allows for electrical box penetrations, then consult with the local authorities. Flag for review