User: jmcdtx, Location: Jonestown, TX
Asked on: Monday, November 3, 2025 at 11:20 am EST
Answered on: Monday, November 3, 2025 at 11:23 am EST
Question: i need to run a 60 amp sub panel from my outdoor main panel. the wiring will run up the outside wall in conduit and enter the attic and terminate in my garage on the other side of the house. about a 80 foot run. my question is what size of aluminum SER should i use? 6-6-6-4 or 4-4-4-2?
Okay, let's break down the wire sizing for your 60 amp subpanel using aluminum SER cable, considering the 80-foot run and the potential for voltage drop.
Understanding the Requirements
60 Amp Service
This is the amperage your subpanel needs to support.
Aluminum SER Cable
You're using aluminum as the conductor material, which has a higher resistance than copper, requiring larger wire sizes for the same amperage.
80 Foot Run
This distance is crucial for calculating voltage drop.
Voltage Drop
Electricity loses voltage as it travels through a wire. Excessive voltage drop can cause appliances to malfunction, lights to dim, and can damage motors. A common guideline is to keep voltage drop under 3% for branch circuits and 5% for feeders (like your subpanel feed).
Code Considerations (NEC - National Electrical Code)
NEC Table 310.16 (Ampacity of Conductors)
This table dictates the ampacity (maximum current-carrying capacity) of different wire sizes based on the insulation type and ambient temperature.
NEC 310.15(B)(3)(a) Adjustment factors
This section talks about ambient temperature and the need to adjust ampacity based on high ambient temps.
NEC 215.2(A)(1)(a) Voltage Drop
This is where the voltage drop recommendations are.
Sizing Based on Ampacity (Ignoring Voltage Drop Initially)
For a 60 amp circuit using aluminum conductors, you'll typically need at least a #4 AWG aluminum wire (refer to NEC Table 310.16 for specific insulation types and temperature ratings).
Voltage Drop Calculation - The Key Factor!
Because of the 80-foot run, voltage drop becomes a significant concern. We need to calculate if the #4 AWG aluminum will result in excessive voltage drop. There are a few ways to do this:1. Online Voltage Drop Calculators
Several online calculators are available. Search for "voltage drop calculator" and input the following: Amps: 60 Voltage: 120V (since it is assumed your running 120/240v and you are running one leg) Wire Gauge: Start with #4 AWG Aluminum Wire Length: 80 feet Conductor Material: Aluminum Phase: Single Phase Power Factor: Assume 0.8 (a typical value for many loads)2.
Manual Calculation (Using a Formula)
Voltage Drop (VD) = (2 K I D) / CM VD = Voltage Drop (in volts) K = Resistance of Aluminum (approx. 17 ohms per circular mil foot at 75°C - you may need to look up a more precise value) I = Current (Amps) = 60 D = One-way distance (feet) = 80 CM = Circular Mils (cross-sectional area) of the wire. For #4 AWG Aluminum, CM is approximately 41,740. For #2 AWG Aluminum, CM is approximately 66,360.Calculate the voltage drop using the #4 and #2 AWG aluminum values, then calculate the percentage: Percentage Voltage Drop = (VD / Voltage) 100 Voltage = 120 (again assuming this is one leg)3.
SER Cable Configuration
6-6-6-4 : would be two #6 hots, #6 neutral and #4 bare ground 4-4-4-2 : would be two #4 hots, #4 neutral and #2 bare ground
Analysis and Recommendation
After performing the voltage drop calculation, you'll likely find that #4 AWG aluminum results in a voltage drop exceeding 3%. Because of this I recommend the
4-4-4-2 SER Cable. This will ensure sufficient ampacity and minimize voltage drop to acceptable levels for your 60 amp subpanel.
Important Safety Considerations
Always de-energize the main panel before working on any electrical wiring. Obtain the necessary permits from your local electrical inspector. Follow all applicable codes and regulations. If you're not comfortable working with electricity, hire a qualified electrician. Use properly rated breakers in both the main panel and the subpanel. Ensure all connections are tight and secure. Use appropriate fittings and connectors for the conduit and cable.* Properly ground the subpanel.Disclaimer:
I am an AI chatbot and cannot provide professional electrical advice. This information is for general guidance only. Consult with a qualified electrician for specific recommendations tailored to your situation and local codes. Incorrect wiring can be dangerous and could cause fire or electrical shock. Flag for review