User: Alwayslearningelec, Location: NJ
Asked on: Monday, November 3, 2025 at 1:27 pm EST
Answered on: Monday, November 3, 2025 at 1:28 pm EST
Question: IS it necessary to upsize the EGC size for multiple sets as the schedule below calls for. I also suspect that in some cases the upsizing in the EGC may require larger conduit. I thought the EGC was based on OCPD size. I have 7 sets of feeder 380B. So I guess I would need #250 or 500 EGC thus I don;t think 3-1/2" conduit would work for 4 #500.
Okay, let's break this down and address your concerns about EGC (Equipment Grounding Conductor) sizing for multiple parallel feeder sets. You are correct to question the requirement to upsize the EGC beyond what the overcurrent protection device (OCPD) size initially suggests. Here's a structured approach
Understanding the Rules
General Rule (Based on OCPD)
250.122(A) and Table 250.122 usually dictates the minimum EGC size based on the rating of the overcurrent protective device (OCPD) protecting the circuit. This is your starting point.
Parallel Conductors (Crucial)
250.122(F) states that where conductors are installed in parallel in multiple raceways or cables, the equipment grounding conductor shall be installed in parallel in each raceway or cable. Further, each parallel EGC must be sized based on the adjusted overcurrent protection device rating as if all the conductors were installed in a single raceway.
Increased Size for Voltage Drop (Rare, but Possible)
250.122(B) allows for increasing the EGC size if necessary to limit voltage drop. This is not common but can arise in very long runs. If you have a significant voltage drop concern, this might factor in, but it's usually addressed separately.
Analyzing Your Situation1. Determine OCPD Size
What is the size of the overcurrent protective device (circuit breaker or fuses) protecting all seven sets of your 380B feeders? This is critical information. Let's assume, for the sake of illustration, that the total OCPD protecting the parallel feeder sets is 1200A.2.
Apply Table 250.122 (Initial Size)
Looking at Table 250.122, for a 1200A OCPD, the minimum EGC size would be a 3/0 copper conductor. This is if all the conductors were in a single conduit.3.
Parallel EGCs and Adjustments (Key Step)
Since you have 7 parallel sets, you must have an EGC in each of those raceways. Each EGC must be sized as if the entire 1200A OCPD was protecting only the conductors in that raceway. The
rule from 250.122(F) says that the EGC must be sized based on the OCPD protecting the circuit even if each of the individual conductors in the feeder sets are rated less than the OCPD.4. Practical Example
Example Assumptions
: You have 7 sets of parallel 380B feeders. Each feeder set is in its own conduit. The OCPD protecting all 7 feeder sets is 1200A. Table 250.122 dictates a minimum 3/0 Copper EGC for a 1200A OCPD, if it were a single conduit.
Therefore
You must have a minimum 3/0 copper EGC in each of the 7 conduits.
Conduit Fill
You are right to be concerned about conduit fill. This leads us to the next point.
Conduit Fill Considerations NEC Chapter 9, Table 4 and Annex C
These sections of the NEC govern conduit fill. You need to calculate the cross-sectional area of your conductors (including insulation) and compare it to the allowable fill percentage for the conduit type you are using.
Derating
Remember that if you have more than three current-carrying conductors in a conduit, you may need to derate the ampacity of the conductors per NEC 310.15(C). This can potentially affect your conductor size selection in the first place.
Addressing Your Specific Conduit Question
You mentioned 4 #500 conductors in 3-1/2" conduit. Let's analyze:1. #500 Conductor Area
According to NEC Chapter 9, Table 5A, a #500 THHN copper conductor has an approximate cross-sectional area of 0.7073 sq. in.
2.
Total Conductor Area
4 0.7073 sq. in. = 2.8292 sq. in.
3.
3-1/2" Conduit Fill
For more than two conductors, the maximum fill is 40%. From NEC Chapter 9, Table 4, a 3-1/2" Schedule 40 PVC conduit has an area of 9.753 sq. in. 40% of 9.753 sq. in. is 3.9012 sq. in. Since 2.8292 is much less than 3.9012, you can fit four #500 THHN conductors in 3-1/2" schedule 40 PVC conduit.
4. Now you have to add the area of the EGC. If you're using a 3/0 copper EGC, each has an area of 0.3247 sq. in. so 2.8292 + 0.3247 = 3.1539 sq. in.
5. For 3-1/2" EMT conduit, you have 11.883 sq. in of area. 40% of that is 4.7532 sq. in.
6.
Your concerns regarding needing a 250 or 500 kcmil EGC are highly unlikely and probably a mistake. Using 3/0 Copper EGC should be more than sufficient.Summary and Recommendations1. Confirm OCPD Size
Absolutely critical. Everything hinges on this.2.
Apply 250.122(F) Correctly
Size the EGC in each raceway as if the total OCPD were protecting that raceway.3.
Conduit Fill Calculation
Perform accurate conduit fill calculations including the EGC to ensure compliance with Chapter 9.4.
Consider Alternatives
If conduit fill becomes a problem, explore using larger conduit, or, if practical, grouping more feeder sets into a single, larger conduit (while still ensuring EGC compliance).
Important Considerations Licensed Professional
This type of design must be performed by a qualified and licensed electrical engineer or electrician who understands the NEC thoroughly. Errors in this area can be dangerous.
Local Amendments
Be aware of any local amendments to the NEC in your jurisdiction.
Coordination Study
For large systems with parallel feeders, a coordination study is often recommended to ensure proper overcurrent protection and selective coordination.
Disclaimer: Consult a qualified professional for your specific installation.* Flag for review