User: Inspired, Location: Vermont
Asked on: Monday, November 3, 2025 at 7:08 pm EST
Answered on: Monday, November 3, 2025 at 7:11 pm EST
Question: I got a call from the supervisor at POCO stating that his inspectors were concerned that the main lug meter combo load center I installed did not meet code.It is a 12 space Eaton MB1212L200BTSThe only breaker installed in it is the one that feeds the service entrance (4 wire) cableI installed the load center so that the customer would have the option of installing a car charger outside without running circuit back out of the house.They are concerned that there is no main shut off for the bus located in the meter comboI figured since everything can be shut off from outside the house it was OKNot to mention if it was against code, why is it being produced?Can anyone help to shed some light on how I can go about my next discussion with POCOTIA
Okay, let's break down this situation and how to approach your conversation with the POCO (Power Company).
Understanding the Issue
The core of the POCO's concern is the lack of a main overcurrent protection device (circuit breaker or fused switch) inside the meter combo load center itself, protecting the busbars within that load center. While you have the main service disconnect outside at the meter, the POCO is likely interpreting code to require another level of protection at the load center.
Why the Concern? Busbar Protection
The busbars in a load center have a specific ampacity rating (in your case, likely 200A). Without a main breaker inside the load center, there's a theoretical risk of overloading the busbars if the sum of the breakers installed exceeds the busbar rating, especially if someone were to add more breakers in the future without proper load calculation. A short circuit internal to the load center could also damage the busbars before the upstream disconnect operates.
Local Disconnect
It provides a convenient local disconnect for service or maintenance within the load center itself. Imagine needing to work inside the load center; turning off the main disconnect outside leaves the entire load center de-energized, which might be inconvenient. A local main breaker allows you to de-energize just the load center while keeping the rest of the service powered.
Local Code Interpretation
It's important to remember that while the NEC (National Electrical Code) is the model code, local jurisdictions (cities, counties, states) can amend or interpret it. The POCO's inspectors may have a specific interpretation or local rule that is driving their concern.
Why it is Being Produced?
Meter combo load centers like the MB1212L200BTS are produced because they can be code-compliant under certain conditions. It comes down to the specific installation and interpretation of the code by the local authority having jurisdiction (AHJ).
Relevant Code Sections
While the exact code section driving their concern depends on your local jurisdiction's adoption and interpretation of the NEC, here are some areas to consider: NEC 230.71(B) Grouping of disconnects. It may require that all service equipment rating not to exceed the total service of the panel. NEC 230.91 Available Short-Circuit Current. NEC 230.95 Ground-Fault Protection of Equipment. If the service is 1000 amps or more, this section applies. NEC Article 408: Switchboards, Switchgear, and Panelboards. This article covers the general requirements for panelboards, including overcurrent protection. NEC 408.36 Overcurrent Protection.Talking to the POCO
Here's a strategic approach:1. Remain Calm and Respectful
Start by acknowledging their concern and demonstrating a willingness to understand their perspective. Avoid getting defensive.2.
Ask for Clarification
Politely ask the supervisor specifically which code section they believe is being violated. Say something like, "I understand your concern. Could you please point me to the specific NEC section or local amendment that requires a main breaker inside this type of meter combo load center?" The goal is to understand their reasoning.3.
Explain Your Rationale
Clearly articulate your understanding of the code and why you believed the installation was compliant. Emphasize that: The main service disconnect is located outside at the meter, providing a means to de-energize the entire service. The primary purpose of the load center is to provide a convenient, pre-wired location for a future car charger circuit, minimizing the need to run new circuits from inside the house. (If applicable) You performed a load calculation and the existing service is sufficient to support the additional load of the car charger.4.
Offer Solutions (If Necessary)
Depending on their response, be prepared to offer solutions. Some possibilities include:
Install a Main Breaker
This is the most straightforward, albeit potentially costly, solution. You'd need to select a breaker with an appropriate ampacity rating (likely 200A) and install it in the load center.
Provide a Load Calculation
Demonstrate that even with the maximum possible load from the car charger, the total service load will remain within the ampacity rating of the service conductors and equipment. This might satisfy their concern about overloading the busbars.
Ask for a Variance (Less Likely)
In some cases, you might be able to request a variance from the code, especially if you can demonstrate that the installation provides an equivalent level of safety. However, variances are typically granted only in exceptional circumstances.5.
Document Everything
Keep a record of all communication with the POCO, including dates, times, names of individuals, and the specific code sections discussed.6.
Escalate (If Necessary)
If you're unable to reach a satisfactory resolution with the supervisor, you may need to escalate the issue to a higher authority within the POCO or to the local electrical inspector.
Important Considerations Load Calculation is Key
Always perform a thorough load calculation to ensure that the existing service is adequate for the intended load. This is crucial for code compliance and safe operation.
Local Amendments and Interpretations
Be aware that local jurisdictions can have their own amendments to the NEC, and their interpretations of the code may differ. Always consult with the local electrical inspector or AHJ to ensure compliance.
In Summary
The POCO's concern likely stems from a desire to protect the busbars within the meter combo load center and to provide a convenient local disconnect. The key is to understand their specific concerns, explain your rationale, and be prepared to offer solutions. A clear understanding of the NEC, local amendments, and a willingness to work with the POCO will increase your chances of a successful resolution. Good luck! Flag for review