User: Alwayslearningelec, Location: NJ
Asked on: Tuesday, November 4, 2025 at 8:08 am EST
Answered on: Tuesday, November 4, 2025 at 8:08 am EST
Question: When terminating bus duct into gear as shown I would imagine you need to attach wire to the end of bus duct and terminate that wire to the gear bus?
You are correct, in most cases. You generally cannot directly connect the bus duct to the gear bus in the way you might imagine (like simply bolting them together end-to-end). Here's a breakdown of the typical process and why it's done this way
Typical Termination Process:
1. Transition Section (Tap Box/Termination Box)
The bus duct typically terminates into a tap box or termination box specifically designed for this purpose. This box is attached to the end of the bus duct run.2.
Flexible Connection
Inside the tap box, there will be a method to connect from the bus bar within the bus duct to the gear's main bus. This is frequently done with
flexible bus jumpers. These jumpers are typically: Copper braid/strap
Offers flexibility to accommodate misalignments, thermal expansion/contraction, and vibration.
Insulated conductors (wires)
May be used, especially for lower ampacities, or when a higher degree of isolation is desired. Must be properly sized and rated for the application.3.
Termination to Gear Bus
The flexible jumpers are then connected to the gear's main bus bars. This is usually done with:
Bolted connections
The jumper has a terminal lug on the end that's bolted to the gear bus.
Compression connectors
Similar to lugs, but compressed onto the conductor, typically requiring a specific tool.
Why Flexible Connections are Used
Misalignment
It's rare that the bus duct and the gear line up perfectly. Flexible connections allow for some physical misalignment.
Vibration
Mechanical equipment (like the gear itself) can vibrate. Rigid connections would transmit that vibration to the bus duct, potentially causing stress and damage. Flexible connections absorb some of the vibration.
Thermal Expansion/Contraction
Bus duct and gear components will expand and contract with temperature changes. A rigid connection would put significant stress on the system as these components move at different rates. Flexible connections allow for this movement.
Ease of Installation
Flexible connections make installation easier, especially in tight spaces. They also make future maintenance and replacement easier.
Electrical Isolation (Sometimes)
While not always the primary reason, in some installations, the flexible connectors (especially when using insulated conductors) can provide a degree of electrical isolation between the bus duct and the gear.
Ampacity Matching
The bus duct and gear may have different ampacity requirements at their connection point. Flexible conductors and lugs are chosen to properly handle the current flow.
Important Considerations
NEC and Local Codes
Follow all applicable electrical codes (like the NEC in the US) and local regulations.
Manufacturer's Instructions
Always follow the bus duct and gear manufacturer's installation instructions. They will specify the approved connection methods and materials.
Ampacity Rating
Ensure that all conductors, connectors, and the tap box itself are properly rated for the intended current.
Short-Circuit Current Rating
The entire connection system must be able to withstand the available short-circuit current at that point in the system.
Proper Termination
Properly torque all bolted connections to the manufacturer's specifications.
Inspection
After installation, carefully inspect all connections for tightness, proper insulation, and any signs of damage. Infrared scanning is often used to check for hot spots after the system is energized.
In summary: While you don't directly connect the bus duct to the gear bus in a rigid fashion, you are correct that you need to transition from the bus bars inside the duct to a suitable conductor (usually a flexible jumper) that is then terminated to the gear's bus bars. This is done inside a tap box/termination box specifically designed for this purpose. Remember to consult the manufacturer's documentation and applicable codes for proper installation procedures. Flag for review