User: Oswar Ramos, Location: Ohio
Asked on: Tuesday, November 4, 2025 at 9:17 am EST
Answered on: Tuesday, November 4, 2025 at 9:21 am EST
Question: I hope this message is going well.Is my pleasure to ask you this question. I work with a General Electrical Contractor, and I have this situation in the building. We've a cable trade and a MC cable running in parallels through a MOD (Equipment distribution) with 600 volts breaker and the cable running through there are of 350 kcmil each one. I did an observation for this because I said that the cable trade has to have a Bonding jumper to the enclosure, per code (see section 250.96) and per specification of the building. The trade partner told me that as "Bonding jumper from cable tray to enclosure" reference 392.60 option 2 states said, each multiconductor cable with individual EGC conductor, are ties to the equipment that is going to. However, I just let you know that they Bonded the cable tray and ties back to the ground grid along with the individual pieces of equipment.My question is, according to your knowledge this cable trade has to be bonding to the enclosure??
Okay, let's break down this situation and address your question about bonding the cable tray to the enclosure. You're right to be concerned and to question the practice.
Here's a summary of the key points and considerations, followed by a recommendation
The Setup
You have a cable tray running parallel MC cables, each 350 kcmil, protected by a 600V breaker, passing through a MOD (equipment distribution enclosure). The MC cables each have an individual EGC (Equipment Grounding Conductor) and are connected to the equipment they serve. The cable tray itself is bonded back to the ground grid.
Your Concern
You believe the cable tray must be bonded to the enclosure per NEC 250.96 and building specifications.
The Trade Partner's Argument
They are relying on NEC 392.60 option 2, arguing that since each MC cable has its own EGC connected to the equipment, a separate bond to the enclosure is not necessary for the cable tray.
Let's Analyze the Codes
NEC 250.96 (Bonding Other Enclosures)
This section requires bonding of metal enclosures containing service conductors and equipment grounding conductors when necessary to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed.
NEC 392.60 (Grounding and Bonding)
This section is specific to cable trays. Option 2 of 392.60 states that the cable tray can be considered bonded if: The cable tray sections are mechanically connected.
Each multiconductor cable running in the tray has an equipment grounding conductor (EGC) that is properly terminated at both ends. This is what your trade partner is relying on.
Key Considerations and Counter-Arguments
Building Specifications
You mentioned the building specifications require bonding. This is a very important factor. If the specification explicitly requires the cable tray to be bonded to the enclosure, then the code allows for the exclusion described on the book as long as the building specs are met first. Always adhere to the more stringent requirement.2.
Redundancy and Fault Current Capacity
While 392.60 Option 2 allows not bonding the tray to the enclosure, bonding the tray to the enclosure provides an additional path for fault current. This redundancy is generally a good practice, especially in high-current situations like you describe with 350 kcmil conductors and 600V breakers. Having multiple paths for fault current lowers impedance and improves clearing speed.3.
Cable Tray as a Bonding Conductor
Even if the MC cables each have an EGC, the cable tray itself, if properly bonded, provides a low-impedance path for fault current to return to the source. The integrity of that tray and connections may be higher over time.4.
Future Expansion
Consider future scenarios. If cables without individual EGCs are added to the tray later, the tray will definitely need to be bonded.5.
Mechanical Integrity
A direct bonding jumper connection can provide mechanical support to the cable tray system, enhancing its stability.
My Recommendation
Yes, the cable tray should be bonded to the enclosure.
Here's why: Building Specifications Override
Your mention of the building specification is critical. If it requires bonding, follow the specification.
Enhanced Safety
Bonding provides a redundant, low-impedance fault current path, improving safety and fault clearing speed.
Best Practice
Especially with 600V systems and large conductors, erring on the side of caution and providing robust grounding and bonding is the best practice.
Future-Proofing
Bonding the tray now avoids potential issues if cable types change in the future.
How to Proceed
Re-Review the Building Specification
Carefully examine the exact wording of the specification regarding bonding of cable trays and enclosures.2.
Consult with the Engineer of Record (EOR)
If there's any ambiguity in the specification or code interpretation, consult with the project's electrical engineer. They have the ultimate authority on the design and code compliance. Document their response.3.
Document Everything
Keep a record of your observations, the code sections in question, the trade partner's argument, and any communication with the engineer or other authorities.
In summary: While NEC 392.60 Option 2 might allow you to not bond the tray, the presence of a conflicting building specification, the improved safety of a redundant bonding path, and general best practices strongly suggest that you should* bond the cable tray to the enclosure. The building specification is the most important determining factor, followed by a consultation with the engineer of record if needed. Flag for review