User: Isaiah, Location: Baton Rouge
Asked on: Tuesday, November 4, 2025 at 11:34 am EST
Answered on: Tuesday, November 4, 2025 at 11:34 am EST
Question: The contractor is running 3/4” RMC steel conduit thru sheet metal type vertical studs to 4x4 outlet boxes at multiple locations - question is, do the rules of conduit supports apply per 344.30? Some of the pipe clamps are around 6’ from the boxesEnviado desde mi iPhone utilizando Tapatalk
Yes, the rules of conduit supports in 344.30 apply to RMC run through sheet metal studs to 4x4 outlet boxes.Here's why and some considerations: 344.30 Applies
344.30 covers the requirements for the support of RMC. There's no exception listed that excludes it based on running through metal studs or terminating at 4x4 boxes. Therefore, 344.30 must be followed.
Spacing of Supports
344.30(B)(2) specifies the maximum spacing for RMC supports: For 3/4" RMC, the maximum spacing is
10 feet. The 6-Foot Spacing Issue
If your clamps are 6 feet from the 4x4 boxes, you're within the 10-foot maximum. However, you also need to consider the requirement of support
within 3 feet of a box, fitting, or termination (344.30(A)). Support within 3 feet of the box (344.30(A))
This is where the 6-foot spacing from the box becomes a problem. You MUST have a support within 3 feet of each 4x4 box. The box itself doesn't count as a support unless it's specifically listed and designed to support conduit without additional supports. Since you are running RMC, the box will need to be independently supported within 3 feet.
Sheet Metal Studs as Supports? Running the conduit through the sheet metal studs can help with stability, but typically these are not considered compliant supports for the purposes of meeting 344.30. The sheet metal studs themselves need to be securely attached to the building structure, and the way the conduit passes through them isn't usually a listed or approved method of conduit support. You need actual listed conduit clamps/straps, and a method of attaching to the studs to be compliant.
In summary, the contractor needs to
Provide a support (conduit clamp) within 3 feet of each 4x4 box. This is non-negotiable.2. Ensure that the distance between any support and the next support does not exceed 10 feet. If the distance between the support within 3 feet of the box and the next support exceeds 10 feet, they will need to add another support.
Important Considerations for Steel Studs
Fasteners
Use appropriate fasteners for attaching the conduit clamps to the steel studs. Self-tapping screws designed for steel studs are common.
Stud Strength
Verify that the steel studs are adequately sized to handle the weight of the RMC, especially if multiple conduits are running through them. Overloading the studs could compromise their structural integrity.
Holes in Studs
Make sure that the holes for the conduit through the studs are properly sized and deburred to prevent damage to the conduit and wiring.
Recommendation:
The contractor should add additional conduit supports within 3 feet of each 4x4 box. This will bring the installation into compliance with 344.30 and ensure the conduit is properly supported. A good approach is to use a conduit clamp near the box, attached with self-tapping screws to the metal stud.If you are unsure, consult with a qualified electrical inspector for clarification and guidance specific to your local codes and regulations. Flag for review