Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Load On Strut

User: Alwayslearningelec, Location: NJ

Asked on: Tuesday, November 4, 2025 at 12:00 pm EST
Answered on: Tuesday, November 4, 2025 at 12:00 pm EST

Question: I's like to put (8) 4" PVC Coated RGS on one of these Durablock racks. They each have 4 #600 XHHW. Seems the load limit is 1000 lbs. How can I determine how much load these conduits/wire create?

Okay, let's break down how to calculate the weight of your conduit and wire to ensure you're within the Dura-Block rack's load limit.1. Determine the Weight of the Conduit (PVC Coated RGS)



Find the weight per foot

You'll need to consult the manufacturer's specifications for the specific type of 4" PVC Coated Rigid Galvanized Steel (RGS) conduit you're using. This information can usually be found on the manufacturer's website (e.g., Allied Tube & Conduit, Wheatland Tube, etc.) or in their catalogs. Look for a table or section that provides the weight per foot (lbs/ft) for 4" PVC Coated RGS conduit.

Important

Different manufacturers and even different wall thicknesses (if applicable) can affect the weight.


Example

Let's say, for the sake of example, the weight is 4.5 lbs/ft. This is an estimated value; you MUST find the specific weight for your conduit.



Determine the length of each conduit section

Since you didn't specify conduit length, let's assume that each conduit section is 10 feet long.


Total Conduit Length = 8 conduits x 10 feet per conduit = 80 total feet of conduit

Calculate the total weight of the conduit

Multiply the weight per foot by the total length.


Example

Total conduit weight = 4.5 lbs/ft 80 feet = 360 lbs

2. Determine the Weight of the Wire (#600 XHHW)



Find the weight per foot

Similar to the conduit, you'll need to find the weight per foot for #600 XHHW wire. This information is also available from wire manufacturers (e.g., Southwire, General Cable, Prysmian, etc.) in their catalogs or on their websites. Look for the weight in lbs/ft or lbs/1000 ft.

Important Considerations



Copper vs. Aluminum

#600 XHHW wire can be copper or aluminum. Copper is significantly heavier than aluminum. Make sure you're using the correct weight for the conductor material.

Insulation

The weight includes the insulation. XHHW insulation is common, but specify the correct type.


Example

Let's say, for the sake of example, that #600 XHHW copper wire weighs 2.0 lbs/ft. This is an estimated value; you MUST find the specific weight for your wire.

Determine the total length of wire

Each conduit has four #600 wires.


Total Wire Length (per conduit)

4 wires/conduit 10 ft/wire = 40 feet per conduit

Total Wire Length (all conduits)

40 feet/conduit 8 conduits = 320 feet of wire

Calculate the total weight of the wire

Multiply the weight per foot by the total wire length.

Example

Total wire weight = 2.0 lbs/ft
320 ft = 640 lbs

3. Calculate the Total Weight

Add the total conduit weight and the total wire weight.

Example

Total weight = 360 lbs (conduit) + 640 lbs (wire) = 1000 lbs

4. Compare to the Dura-Block Load Limit

Compare the total calculated weight to the Dura-Block's load limit (1000 lbs in your case).

Example

In our example, the total weight is exactly 1000 lbs, which is at the maximum load rating for your Dura-Blocks.

Important Safety Considerations and Recommendations



Safety Factor

It's

highly recommended
to operate well below the maximum load limit. A safety factor of 2 or more is generally advisable, especially for long-term installations. Consider de-rating the load limit by 50% (using a safety factor of 2) or even more, particularly if there's a chance of dynamic loading (vibration, impacts, etc.). In this case, I would strongly discourage using these for these applications with the values listed. Exact Specifications



Do not rely on estimated weights.
Get the exact weight specifications from the manufacturers of your specific conduit and wire. Minor variations can add up significantly when dealing with heavy loads. Installation

Ensure the Dura-Blocks are installed correctly and on a stable, level surface. Uneven weight distribution can significantly reduce their load-bearing capacity.


Consult an Engineer

If you have any doubts about the load-bearing capacity or the suitability of the Dura-Blocks for your application, consult a qualified electrical or structural engineer. This is especially important for critical installations or where safety is a primary concern.

Future Expansion

Consider any potential future additions to the conduit system when calculating the load. It's better to be oversized than overloaded.


Support Spacing

Ensure the spacing between your supports is appropriate for the conduit size and load, as recommended by the conduit manufacturer and relevant codes (e.g., NEC).*

Dynamic Loads

If the conduit system is subject to vibration, wind, or other dynamic forces, this can significantly increase the stress on the supports. You'll need to account for these dynamic loads in your calculations.

In summary, follow these steps


Obtain precise weight data for your specific conduit and wire from the manufacturers.
2. Calculate the total weight of the conduit and wire.3. Compare the total weight to the Dura-Block's load limit.4. Apply a significant safety factor.5. Consult an engineer if you have any doubts.

By carefully considering these factors and performing accurate calculations, you can ensure the safety and reliability of your conduit support system. Using the estimated values here shows you would be right at the limit. I highly recommend not using them. Consider a different approach. Flag for review

Previous Question Next Question