Question: ok I need some help im arguing with my PM who is a master electrician about a name plate that doesn't make sense. It says 208v/230v and for the mocp it says 40a/50a. My argument is that the higher voltage would get the smaller mocp. His is that they correlate how they were printed on the name plate. Can any one tell me who is correct?

You are correct. Let's break down why

Understanding the Nameplate
Voltage (208V/230V)

This indicates the equipment is designed to operate at either 208 volts or 230 volts.


MOCP (40A/50A)

MOCP stands for "Maximum Overcurrent Protection." This is the maximum size breaker or fuse allowed to protect the equipment's circuit.

The Relationship Between Voltage and Current


The key principle here is this: For a given amount of power (watts), higher voltage means lower current (amps). This is based on the fundamental power equation: `Power (Watts) = Voltage (Volts) x Current (Amps)`Why You Are Correct

Because the equipment will be drawing the same amount of power, but at two different voltages. You can verify this by solving for amps (I) in the power equation. To reiterate, the power drawn should be the same at both voltages. `Power (P) = V I` at 208v `I = P / 208` at 230v `I = P / 230`If "P" (power) is held constant, then as "V" increases, "I" must decrease.Therefore, to reiterate: The lower the voltage, the higher the current. The higher the voltage, the lower the current.

So, the higher voltage of 230v should correlate to the LOWER MOCP, which is 40A.Why Your PM's Argument is Flawed

Your PM's argument that the correlation is based on the order in which they were printed on the nameplate is incorrect and potentially dangerous. Nameplates are designed based on electrical principles, not arbitrary formatting choices. Following his logic could lead to:
Overfusing at 208V

If you use a 50A breaker at 208V when the equipment only needs a 40A breaker, you risk damaging the equipment during an overload. The 50A breaker might not trip quickly enough to protect the wiring and components.

Nuisance Tripping at 230V

If you use a 40A breaker at 230V when the equipment needs a 50A breaker you might have nuisance tripping of the breaker, and a risk of damaging the equipment from inadequate power.

How to Resolve This
1. Refer to the Equipment Manual

The equipment's instruction manual should explicitly state the correct MOCP for each voltage. This is the ultimate authority.2.

Contact the Manufacturer

If the manual is unclear or missing, contact the equipment manufacturer's technical support department. They can provide the correct MOCP information.3.

If Manual is missing and manufacturer unavailable: Calculate the Current Draw

Calculate the current that the equipment will draw at both voltages. You can do this if you know the power (in watts) of the equipment. Use the power equation (Watts = Volts x Amps). Then, choose the MOCP that is appropriate for that current level, according to the National Electrical Code (NEC). The MOCP should always be sized appropriately for the current draw, and to protect the equipment.

Example


Let's say the equipment draws 8,000 watts:
At 208V

Amps = 8000 / 208 = 38.46 amps. A 50A MOCP would be excessive, and would not protect the wiring/equipment properly.*

At 230V

Amps = 8000 / 230 = 34.78 amps. A 40A MOCP would be acceptable and safer.

In Conclusion


You are correct. The higher voltage (230V) should be associated with the lower MOCP (40A). Always prioritize safety and consult the equipment manual or manufacturer for clarification. Don't rely on assumptions based on how information is formatted on a nameplate.

Important Note: Always consult the National Electrical Code (NEC) and any local codes for specific requirements related to overcurrent protection. This explanation is for informational purposes and should not be considered a substitute for professional electrical advice. Flag for review