Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Tray Bonding for separate tray systems

User: JO9715, Location: Virginia

Asked on: Tuesday, November 4, 2025 at 12:26 pm EST
Answered on: Tuesday, November 4, 2025 at 12:27 pm EST

Question: If you have two separate tray systems with cables being interchanged between trays (All cables are Fiber optic or controls), however both trays are bonding to the building ground ring is it required to also install bonding jumpers between each one of the tray systems where cables change paths? Current inspector is stating that at the points of transition it creates a discontinuous tray system and needs bonding jumpers added at all locations.

Your inspector's interpretation is debatable, but leaning towards the conservative (and arguably safer) side. Here's a breakdown of the arguments and relevant code references

Arguments for Bonding Jumpers (Inspector's Position):
Discontinuous Run and Induced Currents

The inspector's main concern is that even though both tray systems are grounded to the building ground ring, the physical separation where cables transition creates a
discontinuity in the metal raceway system. This discontinuity, however minor, can impede the flow of fault currents and potentially allow for the development of voltage differences between the tray sections, especially during a fault event or if there's significant electromagnetic interference (EMI). These voltage differences could pose a safety hazard to personnel and equipment.

Electromagnetic Compatibility (EMC)

While you mention fiber optic and control cables, the inspector might be considering the potential for electromagnetic interference. A well-bonded cable tray system acts as a shield against EMI. Any discontinuities in the tray system's bonding can compromise its effectiveness as a shield. This could potentially affect the performance of sensitive control systems.

NEC (National Electrical Code) and Local Amendments

While the NEC doesn't explicitly address cable tray bonding requirements in the exact scenario you describe, the underlying principle of
equipotential bonding is a core tenet. The inspector likely believes that the jumper reinforces this principle.

"Best Practice" and Enhanced Safety

Even if not strictly required by code, adding bonding jumpers is a "best practice" approach that enhances the overall safety and reliability of the system. It provides an additional measure of protection against fault currents and voltage differentials.

Arguments Against Bonding Jumpers (Your Position)



Multiple Grounding

Since both tray systems are already bonded to the building's ground ring, they are effectively at the same potential. This reduces the need for redundant bonding.


Type of Cables

Fiber optic cables are non-conductive, so they don't contribute to fault current issues or induce voltage in the tray. Control cables typically carry low voltage/current and are less likely to induce significant currents in the tray or cause dangerous voltage differences.

NEC is not clear on this scenario
: You are correct, the NEC is not definitive on this specific situation.

Relevant NEC References (These might be used by the inspector to justify their position, even if indirectly)



NEC Article 392: Cable Trays



392.7 Bonding

This section emphasizes the importance of bonding cable tray systems to ensure electrical continuity and to provide a low-impedance path for fault currents. While it doesn't specifically address transitions, the underlying principle applies. The inspector might argue that the transition
introduces impedance.

392.7(A)

"Cable trays shall be mechanically continuous and electrically continuous..."

NEC Article 250: Grounding and Bonding



250.4(A)(3)

"Electrical equipment and wiring shall be installed in a manner that creates a low-impedance ground-fault current path...." This reinforces the idea of a continuous and low-impedance path.

250.96(A)

"Metal cable tray systems shall be bonded as required in 250.96(A) and (B)."


NEC Article 300: Wiring Methods



300.10: "Electrical Continuity of Metal Raceways and Enclosures."
This general requirement applies to all raceways (including cable trays, by extension) and reinforces the need for electrical continuity.

How to Proceed


Review Local Amendments

The NEC is a
minimum standard. Your local jurisdiction might have adopted amendments that specifically address cable tray bonding in greater detail. Check with your local electrical authority.2.

Request Specific Code Citation

Politely ask the inspector to provide a specific code section that
explicitly requires the bonding jumpers in your scenario. This will force them to justify their position.3.

Provide Documentation

Gather any relevant documentation that supports your position. This could include:
The manufacturer's specifications for the cable tray systems, especially regarding bonding requirements. Engineering calculations or analyses that demonstrate the effectiveness of the existing grounding system and the lack of potential for dangerous voltage differences.4.

Offer a Compromise (if necessary)

If you're unable to convince the inspector otherwise, consider offering a compromise. Perhaps bond the trays only at the
most significant* transition points (e.g., where there's a large number of cables transferring between trays).5.

Escalate (if necessary)

If you believe the inspector's interpretation is incorrect and you've exhausted all other options, you may need to escalate the issue to a higher authority within the inspection department.

In conclusion:


The inspector's position is based on a conservative interpretation of the NEC and a focus on ensuring maximum safety and electrical continuity. While your argument that the existing grounding system provides adequate bonding has merit, the inspector's concern about potential discontinuities and the need for a continuous low-impedance path is also valid.Adding bonding jumpers, while potentially not strictly required, provides an extra layer of safety and redundancy. The cost of these jumpers is relatively low compared to the potential risks of a poorly bonded system. If you can't get the inspector to change their mind, it might be worth considering installing the jumpers to avoid further delays and potential conflicts.Good luck! Flag for review

Previous Question Next Question