User: Cartoon1, Location: Florida
Asked on: Tuesday, November 4, 2025 at 4:17 pm EST
Answered on: Tuesday, November 4, 2025 at 4:18 pm EST
Question: Hello All,I have a 208/120V, 3 phase system, rated 225A for a small sandwich shop. I provided 4/0 cables that is rated for 230A copper. The reviewer comments: wire sizes are insufficient for the electrical panel ampacity please resize to comply with NEC 310.15 (C)(1). So they want to derate feeder to 80%. Please let me know what you think about this.Thank you,
Okay, let's break down this NEC requirement and see why the reviewer is likely correct.
Understanding the NEC 310.15(C)(1) and 80% Rule
NEC 310.15(C)(1) (formerly 310.15(B)(7)) addresses the ampacity of conductors used for feeders and service conductors that supply the entire load of a dwelling unit. It permits a reduction in ampacity, but only under specific circumstances, and it does not force a reduction or derating in your situation. It's a potential allowance, not a requirement to derate.
However, the reason the reviewer is bringing this up is likely due to the continuous load provision in NEC 210.19(A)(1) for branch circuits and 215.2(A)(1) for feeders NEC 215.2(A)(1) - Feeders
Feeders supplying continuous loads, or any combination of continuous and noncontinuous loads, must have an ampacity not less than the noncontinuous load plus 125% of the continuous load.
Continuous Loads
A "continuous load" is defined as a load where the maximum current is expected to continue for three hours or more. In a sandwich shop, things like refrigeration, HVAC, and some lighting often fall into this category.
The Implication
If your reviewer believes that a significant portion of the 225A load will be continuous (and in a sandwich shop, it's highly probable), then the feeder conductors must be sized to handle 125% of the continuous load. This is essentially the same as derating the conductors to 80% of their ampacity when supplying 100% continuous load.
Example
Let's say the calculated continuous load for the sandwich shop is 150A. Non-continuous load: 75A Continuous Load: 150A Required Feeder Ampacity: 75A + (1.25 150A) = 75A + 187.5A = 262.5AIn this example, 4/0 conductors rated at 230A would not be sufficient, as they are less than the required 262.5A. You would need a larger conductor size.
Why the Reviewer is Likely Correct (and what to do)
The reviewer is probably concerned that you haven't accounted for the continuous load requirement. They are likely interpreting the load as largely continuous (and frankly, in a sandwich shop, that's a reasonable assumption without further information).
Here's what you need to do
Review Load Calculations Carefully
You need to very carefully review your load calculations and specifically identify which loads are considered continuous (3 hours or more). Provide documentation to support your assumptions.2.
Document Continuous vs. Non-Continuous Loads
Clearly separate the continuous and non-continuous loads in your calculations.3.
Calculate Required Feeder Ampacity
Using NEC 215.2(A)(1), calculate the required feeder ampacity based on the continuous and non-continuous loads.
4.
Check Conductor Ampacity
Verify that the ampacity of your 4/0 conductors (230A) is sufficient to handle the calculated required feeder ampacity after considering the continuous load requirements.5.
If 4/0 is Insufficient
If your calculations show that 4/0 conductors are undersized, you will need to increase the conductor size to one that meets the NEC requirements. Consider 250 kcmil copper, which is rated for 255A in most cases.6.
Communicate with the Reviewer
Once you've reviewed your calculations, communicate with the reviewer. Explain your assumptions about continuous loads and present your calculations. If you can justify the 4/0 conductors, great. If not, acknowledge the need for larger conductors and submit revised drawings.
Important Considerations
Overcurrent Protection
Don't forget that the overcurrent protection (the 225A breaker in this case) must also be sized appropriately based on the conductor ampacity and the load. You generally can't have an overcurrent device larger than the conductor ampacity unless specific exceptions apply.
Voltage Drop
While you're re-evaluating conductor size, double-check for voltage drop. A long feeder run to a heavily loaded panel can experience unacceptable voltage drop, which may necessitate even larger conductors.
Local Amendments
Be aware of any local amendments to the NEC that might affect these requirements.
In summary, the reviewer's comment is a valid concern, driven by the NEC's requirements for continuous loads. You need to provide a clear and accurate load calculation that accounts for continuous loads to demonstrate compliance. If you cannot demonstrate that 4/0 is adequate while meeting all NEC requirements, then you must increase the conductor size. Flag for review