Question: Hello!I am finishing a commercial project in Florida, a large grocery store. There is a 3 phase, 20 amp 208 v GFCI protected (breaker) circuit feeding a mixer. The mixer is a cord and plug connection. The electrical coordinator is claiming the mixer has some sort of problem with Square D QOB breakers and they have problems with it tripping the breakers at other store locations with Square D gear but not with other brands of gear for example Siemens. I have not witnessed this personally. We explained, removing the code compliant breaker and installing a non GFCI breaker was not something we were willing to do for safety reasons and the code compliance issue. Now he is asking for us to still remove the GFCI breaker and install a non GFCI breaker, install a 3 pole disconnect adjacent to the mixer, and hard wire the mixer to the disconnect. My question here is, does this method (hard wired to a disconnect) alleviate the GFCI requirement? I have read 210.8(b) (2023) and it does not clearly state this. At least I am not comprehending it in this way. In my opinion, I still believe it is still required to be GFCI protected. Any help is greatly appreciated. Thanks
You're absolutely right to be concerned and to push back on this. The electrical coordinator's proposed solution is not a safe or code-compliant way to address the GFCI tripping issue. Here's a breakdown of why, and why the GFCI requirement likely still applies
Why Their Proposed Solution is Flawed:
GFCI Protection is for Personnel Safety
The purpose of GFCI protection is to protect people from electrical shock hazards. Hardwiring a mixer doesn't change the fact that a fault to ground could still occur within the mixer's motor or internal components, potentially exposing someone to a dangerous shock. The disconnect only allows you to de-energize the circuit for maintenance; it doesn't provide ground-fault protection.
Likely Still Requires GFCI Protection
210.8(B) (2023 NEC) covers GFCI protection for personnel in commercial and industrial locations. Depending on the specific application and location of the mixer within the grocery store, it very likely falls under the requirements of 210.8(B). (B) clearly states the scope of locations GFCI protection is required in other than dwelling units. Grocery stores are not exempt from that section.
Ignoring the Root Cause
Simply removing the GFCI protection and adding a disconnect is a Band-Aid solution. It doesn't address the reason why the GFCI is tripping in the first place. There is a reason the breaker is tripping. Ignoring it is like disabling a smoke detector because it keeps going off when you burn toast – you're masking a potentially dangerous problem.
Code Violation
As you pointed out, removing the GFCI protection would almost certainly violate the NEC, potentially putting your company at risk for liability.
Why You're Correct
GFCI Protection Still Applies
Your understanding of 210.8(B) is correct. A disconnect does not negate the requirement for GFCI protection if the location and equipment type fall under the scope of that section.
Focus on the Problem
The correct approach is to identify and resolve the reason the GFCI is tripping. This could be:
Faulty Equipment
The mixer itself might have a ground fault. Meggering (insulation resistance testing) the mixer's motor windings to ground is essential.
Wiring Issues
Inspect the wiring from the breaker to the mixer for any damage, loose connections, or moisture ingress.
GFCI Sensitivity
While less likely, some GFCI breakers can be overly sensitive. However, swapping brands should be a last resort after all other possibilities have been ruled out. This is also why it is hard to condemn the breaker brand.
Your Next Steps
Document Everything
Document the electrical coordinator's request in writing. State clearly that you cannot remove the GFCI protection without violating code and potentially creating a safety hazard.2.
Insist on Troubleshooting
Insist on a thorough investigation of the mixer and its wiring. This should involve:
Megger Testing
A qualified electrician should use a megohmmeter to test the insulation resistance of the mixer's motor windings. This will identify any ground faults.
Visual Inspection
A careful inspection of all wiring, connections, and the mixer itself for signs of damage or moisture.
Voltage and Current Readings
With the mixer running (if possible), measure voltage and current on each phase to check for imbalances that could indicate a problem.3.
Consult with a Qualified Electrical Engineer (if needed)
If the problem persists after troubleshooting, consider bringing in a qualified electrical engineer to analyze the situation and provide recommendations.4.
Consider a Different GFCI Breaker (as a last resort)
If, and only if, all other possibilities have been ruled out, then you might consider a different brand of GFCI breaker. Some GFCI breakers are more tolerant of nuisance tripping. However, this should be done with caution and only after verifying that the new breaker is compatible with the system and provides adequate protection.
Make sure any replacement breaker is UL-listed for the application.5. Contact the AHJ (Authority Having Jurisdiction)
If the electrical coordinator continues to pressure you to violate code, consider contacting the AHJ for guidance. They can provide an objective interpretation of the code and help resolve the dispute.
In summary, do not remove the GFCI protection. The correct approach is to find and fix the underlying problem causing the tripping. This is the safest and most code-compliant solution. Flag for review