Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Ghost voltage in an MCC

User: dweekly07, Location: Iowa

Asked on: Tuesday, November 4, 2025 at 9:48 pm EST
Answered on: Tuesday, November 4, 2025 at 9:52 pm EST

Question: We're doing a factory dismantle and rewire, and ran into a weird one today. Both electrical rooms have capacitor banks, and all MDP breakers have been de- energized except to the house lighting panel and a few others. Breaker feeding MCC-3 is off and locked out. We have detected voltage intermittently in the feeds to that MCC. Weird voltages too (A-B 200V, A-C 212V, B-C 12V, A-G 278V, B-G 76V, C-G 66V). All downstream switches and breakers are open on MCC-3, voltage persists, so it seems to be coming from the line side in the MDP. Cap bank breaker is open, as well as feed breaker to MCC-3. Levels seem too high for induction. Any other ideas? Also, voltage readings go to zeros for no discernible reason. Literally witnessed it tested at zero, left the site, and my guy called me back to show me the voltage reasons in- person. Where is this backfeed coming from?!?

This is a tricky situation, but let's break down the potential causes and how to troubleshoot them. The intermittent and strange voltage readings strongly suggest a combination of capacitive coupling, possibly some weak inductive coupling, and potentially a problem with your grounding system. Here's a systematic approach

1. Rule Out Measurement Error First and Foremost:
Verify Meter Functionality

Before chasing ghosts, ensure your multimeter is functioning correctly. Use a known, stable voltage source (like a wall outlet or a properly working piece of equipment) to verify it gives accurate readings. Try another meter if possible. Some meters are more sensitive to "phantom voltages" than others. A low impedance meter setting can help bleed these voltages down and show the real state of the line.


Meter Impedance

High impedance multimeters are easily influenced by capacitive coupling. Try a low impedance multimeter (often labeled "LoZ" or similar) if available. This will load the circuit and bleed off some of the capacitive voltage if that's the main source. If the LoZ meter shows significantly lower or no voltage, capacitive coupling is likely the culprit.

Grounding Point

Ensure you have a good, solid ground connection when taking measurements. Use a verified grounding point (e.g., a building steel member bonded to ground, a properly grounded receptacle ground). A poor ground reference can give you erroneous voltage readings.

2. Analyze the Voltage Patterns



Phase-to-Phase Imbalance

The drastically different phase-to-phase voltages (200V, 212V, 12V) are highly unusual and indicate a significant imbalance. This, coupled with the phase-to-ground variations, makes me suspect grounding issues are playing a big part.

Intermittency

The fact that the voltage disappears entirely and reappears is the key clue. This rules out most direct backfeed scenarios.

3. Suspects and Troubleshooting Steps (in order of likelihood)



Capacitive Coupling (Very Likely)



Parallel Runs

Long parallel runs of de-energized conductors near energized conductors are a breeding ground for capacitive coupling. The closer the conductors and the longer the run, the more significant the effect. Even with breakers open, the conductors in your MDP/MCC are essentially acting as capacitors.


Capacitor Banks

Even though the breaker for the capacitor bank is open, the capacitors themselves can still retain a charge for a period of time.

EXTREME CAUTION: DO NOT ASSUME THEY ARE DISCHARGED. VERIFY WITH A PROPER CAPACITOR DISCHARGE TOOL (NOT JUST A MULTIMETER) BEFORE TOUCHING ANY COMPONENTS OF THE CAPACITOR BANK.
Even with the breaker open, leakage currents and inductive/capacitive coupling could slowly recharge them to a non-lethal but measureable voltage. Mitigation



Grounding

The best way to deal with capacitive coupling is to provide a path to ground.

Temporarily connect a grounding conductor (use appropriately sized wire) to all three phases of the de-energized MCC feed. Leave it connected while working and measuring. This will bleed off the capacitively coupled voltage.
Do this after verifying that the MCC-3 breaker is indeed open and locked out. Shielding

In extreme cases, shielding the de-energized conductors can help, but this is rarely practical in existing installations.


Grounding Issues (Highly Likely and Contributing to Strange Readings)



Poor Grounding at the MCC

Verify the ground connection to MCC-3 itself. Is it solid? Is there corrosion? A high-resistance ground path will allow capacitively coupled currents to create voltage differences.


Neutral-Ground Bond Issues

In your electrical system, there's likely only one point where the neutral and ground are bonded (typically at the main service entrance). If there are multiple neutral-ground bonds, or if the original bond is compromised, circulating neutral currents can flow through the ground system, creating voltage differences. This is a dangerous situation and needs immediate attention from a qualified electrician.

Stray Neutral Currents

Even without multiple bonds, stray neutral currents from other loads can create voltage drops in the ground system.


Testing



Ground Resistance Test

Measure the resistance of the grounding system at MCC-3. It should be very low (ideally less than 1 ohm).


Neutral-Ground Voltage

Measure the voltage between the neutral and ground conductors at various locations in the system. Ideally, this should be close to zero. Significant voltage indicates a problem.

Inductive Coupling (Less Likely, but Possible)



Proximity to High-Current Conductors

If the conductors feeding MCC-3 run very close to high-current conductors feeding other equipment, some inductive coupling is possible.

Mitigation

Less effective than dealing with capacitive coupling. Moving conductors further apart (if possible) would help.


Backfeed from Unexpected Sources (Less Likely, but Important to Rule Out)



Control Circuits

Could there be a control circuit that is
supposed to be isolated but is somehow energized and backfeeding into the MCC-3 feed? Trace all control wiring connected to the MCC to ensure it is isolated.

Shared Neutrals

Are there any circuits that share a neutral with the MCC-3 feed? A fault on one circuit could cause voltage to appear on the other.

Testing

Visually inspect all wiring and connections associated with MCC-3. Use a voltage tester to check for unexpected voltage sources.

4. Actions to Take Immediately



Safety First

Treat all conductors as energized until proven otherwise. Wear appropriate PPE (Personal Protective Equipment).

Isolate the MCC-3 Feed

Double-check that the breaker feeding MCC-3 from the MDP is open and locked out. Verify this with a multimeter
right at the terminals of the breaker.

Consult with a Senior Electrician/Engineer

This is not a situation to be taken lightly. Seek expert advice from someone experienced in industrial power systems.

Document Everything

Keep detailed records of all measurements, observations, and actions taken.

5. Step-by-Step Troubleshooting Procedure


Verify Meter and Ground Connection.
2. De-energize EVERYTHING you can easily isolate and de-energize in the area and re-check the voltage. This will help narrow down the source.3. Ground the MCC-3 Feed

As described above, temporarily ground all three phases of the MCC-3 feed to bleed off capacitive voltage. This is a
temporary measure for troubleshooting only.4.

Check Grounding System

Perform ground resistance tests and neutral-ground voltage measurements.5.

Trace Wiring

Carefully trace all wiring connected to MCC-3, looking for potential backfeed sources or shared neutrals.6.

Investigate Capacitor Banks

Thoroughly inspect the capacitor banks, ensuring they are properly discharged (using appropriate tools) and that there are no signs of damage or leakage.7.

Consult Documentation

Review the original electrical drawings and schematics for the factory to identify potential sources of backfeed or grounding issues.

Important Cautions



Lockout/Tagout

Follow proper lockout/tagout procedures to ensure that circuits cannot be accidentally energized while you are working on them.

Capacitor Discharge

NEVER assume capacitors are discharged. Use a proper capacitor discharge tool and follow all safety precautions.


Qualified Personnel:
All electrical work should be performed by qualified and licensed electricians.This is a complex situation, and a systematic approach is essential. By carefully following the troubleshooting steps outlined above, you should be able to identify the source of the backfeed and resolve the issue. Good luck, and be safe! Remember, when in doubt, consult with a qualified professional. Flag for review

Previous Question Next Question