Question: I need to install a 100amp 3 pole breaker with shunt trip accessory in its own enclosure in a xray room that will serve the xray equipment, the breaker is being feed from the main panel. I need an e-stop button to engage the shunt trip coil to trip the breaker incase of an emergency, this shunt trip accessory is rated 120v (same as the breaker.) My question is, can I supply 120v from 1 of the legs on the load side of the breaker to a n/o e-stop which will energize the shunt trip coil and trip the breaker when the button is engaged? The breaker being used is Siemens ED43B100L and the shunt trip accessory is S01ED60. I don't want to have to run a circuit from the main panel for the shunt trip reason being is dedicated circuit breaker for the shunt trip could be manually turned off at the main panel and would disable the emergency power off and won't trip the shunt trip breaker incase of an emergency.

Okay, let's break down this scenario and address your question about wiring the shunt trip on your Siemens breaker for the X-ray room's emergency stop.

Understanding the Requirements and Concerns



Emergency Stop Function

The primary goal is to provide a reliable emergency stop function for the X-ray equipment by immediately de-energizing it via the shunt trip breaker.


Shunt Trip Reliability

You're rightly concerned about the reliability of the shunt trip circuit. Using a separate breaker from the main panel introduces the risk of that breaker being switched off, rendering the E-stop useless.

Siemens ED43B100L Breaker & S01ED60 Shunt Trip

This gives us a specific point of reference for compatibility and specifications.


120V Shunt Trip Coil

The shunt trip coil requires a 120V supply to activate.

Your Proposed Wiring Method

You're proposing to take 120V from one of the load-side legs of the breaker itself, run it through a normally-open (N/O) E-stop button, and then to the shunt trip coil. When the E-stop button is pressed, it would close the circuit, energizing the shunt trip and tripping the breaker.

Analysis and Answer



Yes, your proposed method of sourcing the 120V for the shunt trip from the load side of the breaker powering the X-ray equipment IS a valid and acceptable approach, AND addresses your concern about disabling the E-stop by accidentally switching off another breaker.
Here's why it works and why it's a good solution


Reliability

Since the shunt trip power is derived directly from the breaker feeding the X-ray equipment, the E-stop cannot be disabled without also disabling the X-ray equipment itself. This ensures the E-stop functionality is always tied to the power state of the X-ray machine. This is exactly what you want.2.

Functionality

When the E-stop button is pressed, it closes the circuit, immediately sending 120V to the shunt trip coil. The shunt trip then mechanically trips the breaker, cutting off power to the X-ray equipment.3.

Simplicity

This method is relatively simple to implement.

Important Considerations and Best Practices



Wiring Diagram

Highly recommended: Create a clear, labeled wiring diagram for this circuit and keep it with the electrical documentation for the X-ray room. This will make troubleshooting and maintenance much easier in the future.

Enclosure

The enclosure for the breaker and E-stop button needs to be appropriate for the environment of the X-ray room. Ensure it meets any required IP ratings for dust or moisture protection.

Wire Size

Use appropriately sized conductors for the shunt trip circuit. While the current draw of the shunt trip coil will be relatively low, use a minimum of 14 AWG THHN or similar wire. Remember to consider the length of the wiring run when determining the appropriate wire size to avoid excessive voltage drop.


Secure Wiring

Securely route and terminate all wiring within the enclosure using proper strain relief and connectors.

Testing

After installation, thoroughly test the E-stop functionality. Verify that pressing the E-stop button reliably trips the breaker and de-energizes the X-ray equipment. Document these tests.


Labeling

Clearly label the E-stop button and the breaker enclosure to indicate its purpose (e.g., "X-Ray Equipment Emergency Stop").

Local Codes & Regulations

ALWAYS check with your local electrical codes and regulations to ensure that your installation meets all applicable requirements. This is crucial, especially in medical facilities where safety is paramount. You may need to have the installation inspected and approved by a qualified electrical inspector.


Normally Open (N/O) E-Stop Button

Double-check that you are using a normally open (N/O) E-stop button. When pressed, it closes the circuit to energize the shunt trip. This is opposite of what you need. The wiring method for the e-stop button need to be "fail safe" in the event that the e-stop button wires are cut and no longer connected to the e-stop button, the e-stop button should trip the shunt trip breaker, meaning you need to use a "Normally closed" e-stop button.

Siemens Documentation

Consult the Siemens documentation for both the ED43B100L breaker and the S01ED60 shunt trip accessory for any specific wiring recommendations or warnings.


Proper E-Stop Button

Be sure to select an E-Stop button that is clearly identifiable, easily accessible, and prominently displayed. The button should be a "mushroom head" type, typically red, and designed for quick and easy activation in an emergency.

Wiring Schematic


Here's a basic schematic of the wiring:1. Load Side Breaker Terminal

Connect one side of your 120V wiring (e.g., the "hot" or "line" wire) to one of the load-side terminals of the Siemens breaker.2.

To E-Stop Button

Run this wire to one terminal of the NORMALLY CLOSED E-stop button.3.

From E-Stop Button

Run a wire from the other terminal of the NORMALLY CLOSED E-stop button to one terminal of the shunt trip coil on the breaker.4.

Neutral

Connect the other side of the 120V wiring (e.g., the "neutral" wire) to the other terminal of the shunt trip coil.

In summary

Your proposed wiring method is a sound and practical approach to ensure a reliable and tamper-resistant emergency stop function for the X-ray equipment. Just be sure to follow best practices, consult local codes, and create thorough documentation. Remember SAFETY FIRST. If you are not completely comfortable with electrical wiring, it's always best to hire a qualified electrician.

Disclaimer:
This information is for general guidance only. Consult with a qualified electrician or electrical engineer for specific design and installation instructions. Flag for review