Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 2KVA XFRMR Question

User: Yorgo

Asked on: Wednesday, November 5, 2025 at 7:47 am EST
Answered on: Wednesday, November 5, 2025 at 8:13 am EST

Question: We have over a hundred dock doors at a facility that is getting upgraded dock fans. The new fans have FLA of 9a. The existing are FLA 3a, and are currently tied into the dock leveler controller, via control transformer (500va). This is clearly not an option anymore. What I'm thinking for a resolution is to utilize 2kva step-down transformers (480 to 120), tying into the dock leveler circuit, which is on a 30a 3ph circuit. I'd like to make this a cord/plug setup too, to avoid GEC connections, since this would require aerial work. Does this seem doable, or am I missing something? The purpose of this and not new dedicated 120v circuits is because of the giant labor factor and aerial work, at a place with very limited elevated work windows.If this is feasible, how could I implement Prim and Sec overcurrent protection, in the smallest way possible? Need to consider limited wall space. I did find a company, Larson Electronics that make the xfrmr with cord on prim and sec, and has sec OCP but not on the primary. These people want an arm and leg too, but I'm assuming it's at least a listed unit. With their unit, all I'd need to add is primary OCP. Thought??

Okay, let's break down the dock fan upgrade situation and your proposed solution, addressing the feasibility, code considerations, and how to implement overcurrent protection (OCP) effectively and compactly.

Analysis of the Situation



Problem

Existing dock leveler controllers with a small control transformer (500VA) cannot handle the increased current draw (9A FLA) of the new dock fans. Connecting the new fans to the existing controller would overload the transformer, potentially damaging the controller and creating a fire hazard.


Goal

Provide a safe and code-compliant power supply for the new dock fans with minimal disruption and labor, leveraging the existing dock leveler circuit.

Constraint

Limited access for aerial work significantly increases the cost and time of installing completely new dedicated 120V circuits.

Feasibility of Your Proposed Solution

Your idea of using 2kVA step-down transformers (480V to 120V) tied into the existing dock leveler 30A, 3-phase circuit is
potentially feasible, but

requires careful consideration
of several factors:1. Load Calculation

This is the most crucial step. Each 2kVA transformer can supply a maximum of: 2000VA / 120V = 16.67 Amps at 120V. Since each fan draws 9A FLA, each 2kva transformer can handle a max of 1 fan, if you want any room for inrush.
2.


Transformer Loading

Running a transformer continuously at its maximum capacity can shorten its lifespan and increase the risk of overheating. It's generally recommended to keep transformer loading below 80%. In this case, the fans are rated for 9a, and the transformer can supply 16.67, which is roughly 54%.
3.


Voltage Drop

Consider voltage drop, especially if the 480V source is already experiencing voltage drop due to other loads. Excessive voltage drop can damage the fans.4.

Code Compliance

You
must comply with the National Electrical Code (NEC) and any local codes. This is non-negotiable.

Implementation Considerations and NEC Requirements


Overcurrent Protection (OCP)

This is absolutely essential on both the primary (480V) and secondary (120V) sides of the transformer.


Primary OCP

The primary OCP protects the transformer itself from overload and short-circuit faults.

Secondary OCP

The secondary OCP protects the 120V circuit and the fan from overloads and short circuits.2.

Disconnect Means

You need a readily accessible disconnect means for each transformer or fan, or group of fans fed by the same transformer.3.

Grounding

Proper grounding is critical for safety. The transformer enclosure must be grounded. The secondary (120V) side must be grounded as well (unless it's a separately derived system where grounding is not required, but this is less common and requires careful engineering).4.

Cord and Plug Connection

While the cord and plug approach saves on labor, it's crucial to ensure:
The cords are heavy-duty, appropriately rated for the environment (e.g., oil-resistant if necessary). The plugs and receptacles are of the correct voltage, amperage, and configuration (NEMA). Strain relief is properly implemented at both the transformer and fan ends to prevent damage to the cords and connections.5.

Working Space

Even with wall-mounted transformers, ensure you have adequate working space around the equipment as required by the NEC (110.26).
6.


Enclosure Rating

Choose transformers and enclosures suitable for the environment (e.g., NEMA 3R for outdoor use or dusty environments).

Addressing Your Specific Questions



Larson Electronics Unit

The Larson Electronics unit with secondary OCP is a good start, but the lack of primary OCP is a significant issue. You
must add primary OCP. Their high price may be justified by the integration, listing, and cord/plug setup. Research their product listing to verify that it's UL/ETL listed.

Primary and Secondary OCP in a Small Space



Fuses

Fuses are often the smallest OCP solution. You can use compact fuse holders or fuse blocks. For the primary (480V), use appropriately rated fuses and fuse holders. For the secondary (120V), a standard fuse holder or even a small circuit breaker panel can be used depending on the number of circuits.


Miniature Circuit Breakers

While slightly larger than fuses, miniature circuit breakers offer the convenience of resetting after a trip. Look for DIN-rail mountable miniature circuit breakers.

Combination Fuse/Disconnect Switches

These combine the function of a fuse holder and a disconnect switch in a single unit, saving space and simplifying wiring.


Transformer Location and Mounting

Mounting as high as possible can help save space, but consider the working space requirements.

3 Phase Balancing

If you plan to have any kind of even distribution of dock doors utilizing the transformers, it would be a good idea to balance the loads across the phases. If one phase has a much larger load than the other two, this may cause issues and trip the upstream breaker.

Recommended Approach


Precise Load Calculation

Determine the exact FLA and starting current (inrush) of the new fans. Consult the manufacturer's specifications.2.

Transformer Selection

Choose a 2kVA transformer (or slightly larger) that meets your requirements. Look for units that are UL/ETL listed.3.

OCP Selection and Placement



Primary OCP

Calculate the primary current of the transformer: 2000 VA / 480V = 4.17 Amps. Use a fuse or circuit breaker sized no larger than 125% of the primary current (NEC 450.3(B)). 4.17 x 1.25 = 5.21 amps. Use a 5 or 6 amp fuse/breaker.

Secondary OCP

The secondary current is 16.67. Based on the 9A FLA fan rating, and per NEC, using an OCP of 125% would yield an OCP rating of 11.
25. So use a 15A breaker.4.


Wiring and Connections

Use appropriately sized conductors (THHN or similar) for both the primary and secondary circuits. Ensure all connections are secure and properly insulated.5.

Grounding

Properly ground the transformer enclosure and the secondary neutral (if required for your separately derived system).6.

Labeling

Clearly label all components and circuits.7.

Inspection

Have the installation inspected by a qualified electrical inspector to ensure compliance with the NEC and local codes.

Important Considerations



Licensed Electrician

This work must be performed by a qualified and licensed electrician. Improper electrical work can be dangerous and illegal.*

Permits

Obtain all necessary electrical permits before starting the work.

Summary:


Your proposed solution is potentially feasible with careful planning and execution. Prioritize safety and code compliance above all else. A well-designed and properly installed system will provide a reliable and safe power supply for your new dock fans. Flag for review

Previous Question Next Question