Question: I have been dealing with some residential installations utilizing PCS protection of main service panel. The issue I am having a hard time making a decision on is if the PCS supply limit can be 100% of the bus bar rating.For instance one installation is a 200A MSP with a 200A 80% main breaker. Pretty cut and dry standard home install. Solar is landed on the lowest position in the panel and would not comply with any of the 705.12 sections. For this reason they have opted to implement PCS to curtail solar supply at the predefined limit. This limit can be set at 100% of the bus bar rating correct(200A)? The PCS is just taking the sum of supply currents and curtailing the PV when load reaches the PCS limit. I cannot see how allowing the solar to operate between 160A-200A would cause issues on the panel as in this range the solar would only be taking load off the main breaker. I feel like there are a lot of moving parts here but I cannot find a corner of this problem that leaves the panel in a worse position than not having any solar, or maxing out the 120% rule.
You're thinking about this the right way, and your logic is sound. Here's a breakdown of why you can likely set the PCS limit to 200A in your scenario, and some considerations to keep in mind
Why 200A Limit (Bus Bar Rating) is Generally Acceptable:
PCS Functionality
The critical aspect of a PCS is that it actively limits the total current supplied to the load side of the panel to the configured limit. In your scenario, if the house load is only pulling 100A, the solar can output up to 100A. If the house load suddenly increases to 180A, the solar will curtail itself to only supply 20A to stay within the 200A limit. This is what protects the panel from being overloaded.
Main Breaker Protection
The 200A main breaker protects the panel from excessive current draw from the utility side. If the house load, including solar backfeed, exceeds 200A, the main breaker will trip, regardless of what the PCS is doing.
"Shedding" Load
Effectively, the PCS "sheds" solar output when the load approaches the limit. This is a key difference from simply relying on breaker protection or the 120% rule.
Load Balancing
Modern PCS systems often measure the current on each phase and adjust the solar output accordingly to maintain balanced loading. This is an additional layer of safety and stability.
Confirmation
The language and requirements for power control systems are still evolving. To make sure that you meet local AHJ expectations, you should contact them and confirm that setting the PCS supply limit to 100% of the bus bar rating will be acceptable. Also check if they will require any specific commissioning tests or documentation.
Important Considerations and Potential Issues
Equipment Listing and Instructions
Crucially, you must verify that the PCS equipment you are using is listed (UL 1741 or equivalent) and approved for use as a current-limiting device. The manufacturer's instructions for installation and configuration must support the 200A limit in your application. If the manufacturer's documentation explicitly states a lower limit, you must adhere to that.
Installation Quality
The PCS must be installed correctly, with proper wiring and grounding. The current sensors need to be accurately placed to measure the total current. Any errors in installation can compromise the PCS's ability to limit current.
Commissioning and Testing
Before commissioning the system, thoroughly test the PCS to ensure that it is functioning correctly. Simulate various load conditions to verify that the PCS properly curtails solar output when the limit is approached.
Coordination with Utility
The utility company has its own grid interconnection requirements. They may have specific limits on backfeed current that you must adhere to, even with a PCS. Always coordinate with the utility before commissioning the solar system.
Future Load Growth
Consider the possibility of future load increases in the house. If the homeowner plans to add a large appliance (e.g., electric vehicle charger, heat pump) in the future, the 200A limit may become a constraint. In such cases, it might be prudent to set the limit slightly lower than the bus bar rating to provide a buffer.
Neutral Current
Ensure the system is designed to handle neutral currents appropriately. Unbalanced loads, especially in residential settings, can lead to significant neutral current. The panel and PCS must be rated to handle this.
In summary:
If the PCS is properly listed, installed according to the manufacturer's instructions, and commissioned with thorough testing, setting the current limit to the bus bar rating (200A in your case) is generally acceptable. This provides the homeowner with maximum solar benefit while ensuring the panel is protected from overload. However, always prioritize safety, follow the manufacturer's instructions, and coordinate with the AHJ and utility company. Flag for review