Topic: Voltage Drop for Robust Telecom Equipment

User: YouConduit!, Location: Midwest

Asked on: Wednesday, November 5, 2025 at 3:18 pm EST
Answered on: Wednesday, November 5, 2025 at 3:18 pm EST

Question: Dealing with a remote location where the 120/240V, 1-phase, 100A distribution panelboard is ~300 feet away from the utility meter. This is a 100A service.All of the loads are very robust equipment with nominal voltage ranges of 200-250VAC for the 240V loads and 100-130VAC for the 120V loads. Load calcs add up to 8kVA. Typical usage is <1/2 of that.What size should the service conductors be? Without considering voltage drop, I would say CU #2s. Should the cables be upsized for voltage drop if all of the equipment is manufactured for a broad range of voltages (well below what it should ever see)?

This is a good question that highlights the trade-offs between code compliance, cost, and practical considerations. Let's break down the calculations and address the voltage drop.1. Ampacity Requirement

You have a 100A service. NEC 310.16 dictates the ampacity of conductors. Copper #2 THHN is rated for 95A (75°C rating, which is usually the terminal temperature rating to use). This would be technically insufficient. Copper #1 THHN is rated for 110A (75°C rating) and would be code-compliant for a 100A service.

2. Voltage Drop Calculation



NEC Recommendation

The NEC recommends (but doesn't mandate) limiting voltage drop to 3% for feeders and 5% overall (feeder + branch circuits). Since this is the service conductor, we'll focus on the feeder (service) voltage drop limit of 3%.


Calculating Voltage Drop

Use the following formula to estimate voltage drop:VD = (2 K I D) / CMWhere: VD = Voltage Drop (in volts) K = Approximate resistance of the conductor (Ohms·CM per foot at operating temperature - use 12.9 for copper). I = Current (in amps) - Let's use 50% of your panelboard rating, or 50A as your "typical" load, and then check with a 100A load. D = One-way distance (in feet) = 300 ft CM = Circular Mils (conductor size in circular mils; see a wire ampacity chart or NEC Table 8)

Calculations



For #1 Copper (CM = 83,690)

VD (50A) = (2 12.9 50 300) / 83690 = 4.62 Volts VD (100A) = (2 12.9 100 300) / 83690 = 9.24 Volts

For 1/0 Copper (CM = 105,500)

VD (50A) = (2 12.9 50 300) / 105500 = 3.67 Volts VD (100A) = (2 12.9 100 300) / 105500 = 7.33 Volts

For 2/0 Copper (CM = 133,100)

VD (50A) = (2 12.9 50 300) / 133100 = 2.91 Volts VD (100A) = (2 12.9 100 300) / 133100 = 5.82 Volts

Voltage Drop Percentage

Calculate the voltage drop percentage relative to the starting voltage: VD% = (VD / Voltage) 100 Assuming 240V nominal: #1 Copper: 50A: (4.62/240) 100 = 1.93% 100A: (9.24/240) 100 = 3.85% #1/0 Copper: 50A: (3.67/240) 100 = 1.53% 100A: (7.33/240) 100 = 3.05% #2/0 Copper: 50A: (2.91/240) 100 = 1.21% 100A: (5.82/240) 100 = 2.43%

3. Analysis & Recommendation



Code Compliance

At a
minimum, you need #1 Copper to meet the 100A service requirement.

Voltage Drop



#1 Copper

At 50A, the voltage drop is 1.93%, which is acceptable. At 100A, it exceeds the 3%
recommended limit.

#1/0 Copper

At 50A, the voltage drop is 1.53%, which is acceptable. At 100A, it is slightly above 3%.

#2/0 Copper

Keeps voltage drop under 3% even at 100A.


Your Specific Situation

You stated that the equipment is designed to handle a broad voltage range. Therefore, a larger voltage drop is less of a concern compared to locations with sensitive electronics.

Recommendation

Given your specific circumstances, here's my suggestion:1.

#1/0 Copper

This is a good compromise. It's slightly more expensive than #1, but it provides a larger margin for future load growth and keeps voltage drop reasonably low (especially under typical usage). If you are highly confident that your loads will remain consistently low, #1 Copper will still be within compliance, but it's a much smaller safety margin.2.

#2/0 Copper

If you are very concerned about future load increases or want to minimize voltage drop regardless of equipment voltage tolerance, then #2/0 is the best choice.3.

Document

Document your voltage drop calculations and the rationale for your conductor selection. Keep this documentation with the electrical panel. This is essential for future reference and for any inspections.4.

Monitoring (Highly Recommended)

After installation, measure the voltage at the panelboard under both typical and maximum expected load conditions. This will confirm your calculations and provide valuable data for future troubleshooting or system upgrades. If you find the voltage drops more than anticipated, you can revisit the conductor size.5.

Consider Aluminum

If the cost of copper is prohibitive, you could investigate aluminum conductors. Aluminum conductors require a larger gauge for the same ampacity and voltage drop as copper. Be extremely careful with terminations when using aluminum to prevent oxidation and loosening. Use appropriate anti-oxidant paste and torque all connections to the manufacturer's specifications.

Important Considerations



Local Codes

Always check with your local electrical inspector or authority having jurisdiction (AHJ) for their specific requirements. They may have more stringent voltage drop rules or other local amendments.


Conduit Fill

When upsizing conductors, ensure that the conduit is adequately sized to accommodate the larger wires. Refer to NEC Chapter 9 for conduit fill requirements.

Cost Analysis

Get pricing for all conductor sizes and factor in the cost of conduit and labor. The cost difference may make a larger conductor size more appealing.


Future Load Growth

Consider any potential future expansion of the electrical system. It's often more cost-effective to oversize the conductors slightly during the initial installation than to replace them later.*

Grounding:
Ensure that the grounding conductor is sized appropriately according to NEC 250.122 based on the overcurrent protective device (100A breaker).By carefully considering these factors, you can select the appropriate conductor size for your remote location, ensuring both code compliance and reliable performance. Good luck! Flag for review