Question: Where capacitors are installed in motor circuits (does not exempt factory installations) conductors shall com0ly with 460.8 and 460.9460.8 capacitor circuit shall be not less than 135% of capacitor ratingApparently nec is referring to capacitors added to a circuit but not motors factory installed with capacitors but doesnt pit this in text
You are correct in your understanding of the intent of the NEC sections you cited. Let's break down why: Scope of 460.8 and 460.9: These sections within Article 460 (Capacitors) deal specifically with the installation of capacitors as components of an electrical system. They address things like: Conductor sizing for capacitor circuits (460.8) Overcurrent protection (460.9) Disconnects (460.8(c)) Why Factory-Installed Capacitors are Exempt (Implicitly): UL Listing and Integrated Design: When a motor is manufactured with capacitors as an integral part of the motor assembly, the entire unit is typically UL-listed (or equivalent). UL standards ensure the entire motor system (including the capacitors and associated wiring within the motor housing) meets safety requirements. The motor manufacturer is responsible for sizing components to work together. The factory installed capacitors are part of the motor. Manufacturer's Responsibility: The motor manufacturer is responsible for the proper design and protection of the motor and its components. Adding capacitors to the motor circuit is not the responsibility of the installer but the engineer. In essence, Article 460 deals with field-installed capacitors.In summary:
The NEC 460.8 and 460.9 cover the specific case of adding capacitors to a motor circuit, not those already built into the motor from the factory, as the components inside the motor are considered a complete, listed assembly. Flag for review