Topic: Service grounding

User: Darho, Location: Cookeville

Asked on: Wednesday, November 5, 2025 at 5:17 pm EST
Answered on: Wednesday, November 5, 2025 at 5:29 pm EST

Question: So concerning the post in facebook about service grounding. If you ground the meter can and rely on the neutral to be the bond jumper between the meter and the disconnect as the diagram illustrates. What happens if by chance you lose your neutral between the meter can and the disconnect? Where does the voltage return to. There is no ground conductor anymore so wouldn’t all grounded metal appliances then become charged by the current seeking to go to ground?

You've identified a very serious potential safety hazard related to relying solely on the neutral conductor for bonding between the meter can and the disconnect. Let's break down the scenario

The Standard Setup (And Why It's a Problem if the Neutral Fails):
Service Grounding

The meter can is grounded to a grounding electrode (ground rod, water pipe, etc.). This provides a low-impedance path to earth for fault currents.


Neutral-Ground Bond at the Service Disconnect

The neutral conductor is bonded to the grounding system (equipment grounding conductors and the grounding electrode system) at the service disconnect (typically a main panel).

Neutral as the Bonding Conductor (Problem!)

In the setup you described, the
only path for fault current to return to the source (the transformer) from the meter can is the neutral conductor between the meter and the disconnect. This is the critical weakness.

What Happens If You Lose the Neutral Between the Meter and Disconnect?


This is where things get dangerous:1. Fault Current Can't Return via the Neutral

If a hot wire comes into contact with the metal enclosure of the meter can, or any grounded metal equipment connected to it, a fault current will try to flow. However, the neutral is now broken.2.

Voltage on Grounded Metal

The fault current will seek
any path back to the source (the transformer supplying the service). Since the neutral path is gone, the grounded metal parts become energized. This means the meter can, any metallic conduits connected to it, and even grounded appliances connected to the system within the building can rise to a dangerous voltage level relative to earth.3.

Elevated Ground Potential

The grounding electrode system (ground rod, water pipe) will now be carrying fault current. This raises the potential of the earth around the electrode, creating a shock hazard for anyone who touches grounded metal parts and the earth at the same time.4.

Risk of Electrocution

Anyone touching the energized metal parts (meter can, appliances, pipes) and a grounded object (earth, water faucet connected to a metallic pipe that's grounded) will create a circuit and be subjected to a potentially lethal electric shock.

Why This is a Code Violation and Extremely Dangerous



Improper Bonding

Electrical codes (like the NEC in the US) require a dedicated equipment grounding conductor (EGC) between the meter can and the service disconnect. The primary bonding path must not rely solely on the neutral conductor. The neutral is for carrying normal load current, not for safely carrying fault current. Relying on it for fault current is problematic due to it possibly being disconnected or improperly sized.

Lost Neutral Hazards

The potential for a lost neutral is a well-known hazard, and codes are specifically designed to mitigate it. Relying solely on the neutral as the bonding path defeats these safety measures.


Voltage Drop

While not as critical as safety, the neutral conductor is not designed to carry the amperage of a ground fault. If the neutral is a insufficient size it could burn open as well.

The Correct Way to Wire It


Grounding Electrode System

Properly install a grounding electrode system (ground rod, water pipe electrode, etc.) at the meter can and at the service disconnect.2.

Equipment Grounding Conductor (EGC)

Run a dedicated, properly sized equipment grounding conductor (EGC) from the meter can to the service disconnect. This EGC provides the primary low-impedance path for fault current back to the source. This conductor can be a wire, conduit, or other approved grounding path.3.

Neutral-Ground Bond at the Service Disconnect (and only there)

The neutral conductor is bonded to the grounding system only at the service disconnect. This creates a single point where the neutral and ground are connected.

In Summary:


Never rely solely on the neutral conductor for bonding between the meter can and the service disconnect. A dedicated equipment grounding conductor (EGC) is absolutely essential for safety and is required by code. The scenario you described creates a severe electrocution hazard in the event of a lost neutral. Flag for review