Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Number of disconnects separate structure

User: xguard, Location: Baton Rouge, LA

Asked on: Thursday, November 6, 2025 at 5:12 am EST
Answered on: Thursday, November 6, 2025 at 5:12 am EST

Question: I have a building housing communication equipment for a toll bridge on a platform next to the bridge. The service is 500 feet away and supplies a 480 VAC feeder to the structure that lands in a junction box on the platform right outside the building on a free-standing rack.The feeder splits at the junction box and supplies two disconnects. The two disconnects are right next to each other. One is for roadway lighting and the other feeds a transformer that steps the voltage down to 240 VAC before entering the building.Is an additional disconnect needed before the junction box?

Let's break down the NEC requirements to determine if an additional disconnect is needed before the junction box.

NEC Considerations



NEC 225.31 Disconnecting Means
- _General._ Means shall be provided to disconnect all ungrounded conductors that supply or pass through the building or structure. NEC 225.32 Location. The disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the conductors. The disconnecting means shall be suitable for use as service equipment. NEC 225.33 Maximum Number of Disconnects. (A) General. Each building or structure shall be supplied by only one feeder or branch circuit unless permitted in 225.30(B) through (E). Each feeder or branch circuit shall have only one disconnecting means to disconnect all ungrounded conductors, unless permitted in 225.33(B) through (D).

Analysis of your scenario


The Structure

The building housing the communication equipment on the platform is a structure. Therefore, NEC Article 225 applies.2.

Feeder

The 480 VAC supply is a feeder to this structure.3.

Disconnecting Means

You have two disconnects after the junction box; one for roadway lighting and one for the transformer.4.

Location of the Disconnects

The disconnects are on the platform outside the building and are readily accessible. This would seem to meet the intent of NEC 225.32. They are outside the building and near the point of entrance of the conductors (into the junction box).
5.


Number of Disconnects

NEC 225.33 (A) states there should only be one feeder or branch circuit to the structure with only one disconnecting means. However, the exception 225.33 (B) states "Additional Disconnecting Means. Where more than one feeder or branch circuit supplies a building or structure, the disconnecting means specified in 225.31 shall be grouped." Also, NEC 225.33(D) states the following as an exception to the requirements: "Different Characteristics. Additional services, feeders, or branch circuits shall be permitted to supply equipment for different purposes or locations, or both, under single management."

Conclusion

Based on the information provided, you probably DO NOT need a disconnect
before the junction box, as long as the two disconnects meet the following conditions:1.

Readily Accessible

They are readily accessible, meaning they can be reached quickly without obstruction. Being on a free-standing rack outside is generally considered readily accessible.2.

Grouped

They are grouped together (right next to each other).3.

Suitable for Service Equipment

The disconnects must be rated for use as service equipment. Usually, this means they are service-entrance rated, meaning they can be used as the main disconnect.4.

Different Purposes
Assuming the roadway lighting is truly separate from the communications equipment and considered to be for different purposes, then having a dedicated disconnect for the roadway lighting is acceptable.

Important Considerations



Local AHJ (Authority Having Jurisdiction)

The final decision rests with the local electrical inspector. They may have specific interpretations or local amendments to the NEC. Consulting with them is crucial.

Safety

Even if not strictly required by code, adding a disconnect
before the junction box might be a good practice from a safety standpoint. It would allow for a complete shutoff of power to the entire system at that point. However, it adds cost and complexity.

Accessibility

Ensure the junction box itself is also accessible for maintenance and inspection.

Recommendation

Consult with your local electrical inspector to confirm they agree that your setup meets their interpretation of the NEC. If they are fine with the current setup, document their approval. If they require a disconnect before the junction box, be prepared to install one.

Disclaimer:
This information is for educational purposes only and should not be substituted for the advice of a qualified and licensed electrician or electrical engineer. Flag for review

Previous Question Next Question