Question: So when doing a brand new service 230.67 talks about surge protection and the exception says it’s only needed at the panels downstream if it’s not at the service but 215.18 makes it seem like it’s required everywhere. Obviously one doesn’t reference the other section so which one do you follow. I’d rather just put it at the outside service and be done with it.
You've highlighted a common point of confusion regarding surge protection requirements in the NEC. Here's a breakdown to clarify the requirements and how to approach them
Understanding the Code Sections
230.67 (Surge Protection): This section specifically addresses surge protection for dwelling unit services. The general rule requires a surge protective device (SPD) be installed at the service equipment. The exception allows you to omit the service SPD if an SPD is installed at each downstream panelboard and meets specific performance criteria. 215.18 (Surge Protection): This section addresses surge protection for feeder conductors supplying dwelling units. It mandates that an SPD be installed on the feeder conductors at the origin of the feeder.
Reconciling the Requirements
Here's how to reconcile these sections:1. Scope
230.67 deals with the
service equipment of a dwelling unit. 215.18 deals with the feeder conductors that supply a dwelling unit (the feeder is the conductors between the service equipment and the panelboard in the dwelling unit).2. Sequential Application
First
Comply with 230.67. This means either: Install an SPD at the service equipment. Install SPDs at all downstream panelboards within the dwelling unit (meeting the performance requirements of 230.67(B)). This is the "exception" to installing it at the service.
Second
Comply with 215.18. This section says that an SPD must be installed on the feeder conductors. The feeder conductors run from the service equipment to the panel board within the dwelling unit. So in most residential applications, this would not apply.
Practical Application and Recommendation Simplest and Most Common Solution
Install a surge protective device at the service equipment. This satisfies both 230.67 (the main rule) and, likely, 215.18 because the feeder conductors are located inside the service equipment (the SPD can be connected to those conductors inside the service equipment).
Multiple Buildings
If the dwelling unit consists of multiple buildings (e.g., a house and a detached garage fed from the same service), you might have a panelboard in each building. In this case, if you choose not to install an SPD at the service, you would need to install SPDs at each of those panelboards to meet the exception in 230.67 and you would need to install an SPD on the feeder conductors that run to each building to comply with 215.
18. This approach is usually more costly and complex than simply installing an SPD at the service.
In summary, installing an SPD at the service equipment is the simplest and often most cost-effective approach to meet the requirements of both 230.67 and 215.18 in most typical residential installations. It provides comprehensive surge protection at the point of entry to the building, protecting the entire electrical system.
Important Considerations
SPD Ratings
Ensure the SPD you select has an appropriate surge current rating for the service size and the expected surge environment in your area.
SPD Type
Choose an SPD that is listed for the intended application (e.g., Type 1 or Type 2, depending on the installation location).
Local Amendments
Always check for any local amendments to the NEC that may further clarify or modify surge protection requirements in your jurisdiction. The local AHJ (Authority Having Jurisdiction) has the final say.
Coordination
If you're unsure about the best approach for a particular installation, consult with a qualified electrician.
Disclaimer: I am an AI Chatbot and not a licensed electrician. This information is for general guidance only and does not constitute professional electrical advice. Always consult with a qualified and licensed electrician for specific installation requirements and to ensure compliance with all applicable codes and regulations. Flag for review