Question: Question, in the attached picture, you will see that the parallel conductors have a fuse in each conductor, the other end terminates with both wires of the phase on one terminal, is this a good practice? I'm thinking that if a fuse would blow than the other conductor would have to carry the entire load? I have never seen parallel conductors installed in this manor before! What do you all think?
You're right to question this setup. It's generally not a good practice and could be potentially dangerous. Here's a breakdown of why: Overload on Remaining Conductor
As you correctly pointed out, if one fuse blows, the remaining conductor has to carry the entire load for that phase. If the load is above the ampacity of that single conductor, it will be overloaded, overheat, and potentially cause a fire. This defeats the purpose of paralleling conductors in the first place, which is to increase current-carrying capacity.
Unequal Current Sharing
Even if the remaining conductor can handle the load after a fuse blows, there's no guarantee of equal current sharing between the conductors to begin with. Slight differences in impedance (length, connections, conductor properties) can cause one conductor to carry more current than the other. Blowing a fuse only exacerbates this problem.
Difficult Troubleshooting
When one fuse blows, it's difficult to immediately determine the cause. Was it a genuine overload, or a faulty fuse? Is there a hidden problem causing unequal current sharing? This complicates troubleshooting and repair.
Code Compliance Issues
Many electrical codes (like the NEC in the US) have specific requirements for paralleling conductors, including: All conductors must be the same length, conductor material, cross-sectional area, insulation type, and be terminated in the same manner.
Overcurrent protection must be arranged to protect each conductor individually. This setup violates that requirement.
Why is this done sometimes?
Sometimes, this might be done by someone trying to "get by" with using existing equipment without fully understanding the implications. For example, perhaps the equipment was originally designed for a single, larger conductor, and someone tried to parallel smaller conductors to avoid replacing the equipment entirely. This is a bad practice and should not be done.
Best Practices for Paralleling Conductors
Use Identical Conductors
All parallel conductors must be the same length, material, size, and insulation.
Terminate Properly
Terminations must be made to ensure equal current distribution. Using properly sized lugs and torqueing to the manufacturer's specifications is critical.
Individual Overcurrent Protection
Each parallel conductor must have its own overcurrent protection (fuse or circuit breaker) sized to protect that individual conductor.
Qualified Installation
Paralleling conductors should only be done by qualified electricians who understand the code requirements and best practices.
In Conclusion:
The installation shown in the picture is not a good practice and is likely a code violation. It creates a dangerous situation and should be corrected by a qualified electrician. The electrician should evaluate the load requirements and ensure that the conductors and overcurrent protection are properly sized and installed according to code. Flag for review