Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: What size fuses

User: Brownetown, Location: Va

Asked on: Thursday, November 6, 2025 at 3:59 pm EST
Answered on: Thursday, November 6, 2025 at 3:59 pm EST

Question: what size fuses would you use in this application. Having a debate at the moment FLA 26.7A. Largest motor 8.67. 480v

Okay, let's break down the fuse sizing for this motor application. We need to follow the National Electrical Code (NEC) guidelines for motor protection.

Understanding the Information FLA (Full Load Amps) 26.7A

This is the total full load amps for all equipment that will be protected by this fuse.


Largest Motor FLA 8.67A

This is the full load amperage of the largest motor connected to the circuit.

480V

The voltage of the system.

NEC Guidelines and Calculations


The NEC provides rules for sizing fuses (specifically, overcurrent protection) for motor circuits. The general approach is to:1. Protect the Motor

The primary goal is to protect the motor itself from overloads and short circuits. NEC Article 430 dictates these rules.2.

Protect the Circuit Conductors

The fuses also need to be sized to protect the wiring from overcurrent.

Fuse Sizing Procedure (Based on NEC)


Here's a step-by-step approach, considering the typical scenario.
Always consult the latest edition of the NEC and a qualified electrician for your specific installation.1. Largest Motor Protection

For the largest motor, we need to select an overcurrent protective device (fuse or circuit breaker). The NEC allows for different sizing based on the type of overcurrent protection and motor. Let's assume we're using a
time-delay fuse. NEC 430.52 says a time-delay fuse can be sized up to 175% of the motor's FLA. Calculation: 8.67A 1.75 = 15.17A. The next standard fuse size above this is typically

15A or 20A
. I would choose the lower size if I can since it will provide greater protection.2. Remaining Load

Now, let's calculate the remaining load that isn't the largest motor: Total Load - Largest Motor FLA = Remaining Load 26.7A - 8.67A = 18.03A3.

Fuse Sizing

Now we need to add the largest motor overcurrent protection to the non-motor load. 15.17A(Largest motor protection) + 18.03(All other equipment) = 33.2A The next standard size above 33.2A is 35A.

Conclusion (Proposed Fuse Size)


Based on these calculations and common practice, I would recommend using a 35A time-delay fuse.

Important Considerations and Caveats



Motor Service Factor

If the motor has a service factor of 1.15 or higher, or a temperature rise of 40°C or less, you may be able to use a slightly higher percentage for the fuse sizing. (See NEC 430.32)


Fuse Type

The calculations above are based on using a time-delay fuse. If you are using an instantaneous trip breaker, different rules apply, and the sizing will be lower.

Conductor Ampacity

You must ensure that the conductors feeding this circuit are sized appropriately for the load and the overcurrent protection.


NEC Code Revisions

Code rules can change with each edition of the NEC. Always consult the latest version.

Qualified Electrician

This information is for general guidance only. Always consult with a qualified and licensed electrician for the final design and installation of your electrical system. They will consider all factors specific to your situation and ensure compliance with local codes.



Inrush Current

Motors have high inrush currents when starting. Time-delay fuses are designed to handle these short-term surges.

Other equipment

Ensure the fuse selected is not greater than the lowest ampacity of the equipment connected. For example, if a piece of equipment can only handle 20A, then the fuse selected cannot be larger than this size.

In summary, a 35A time-delay fuse is a reasonable starting point based on your provided information. Always verify and confirm with a qualified electrician following the latest NEC guidelines.
* Flag for review

Previous Question Next Question