Topic: Electrodes Bonding Jumper VS Grounding Electrodes Conductor

User: zemingduan, Location: Philadelphia,PA

Asked on: Thursday, November 6, 2025 at 5:14 pm EST
Answered on: Thursday, November 6, 2025 at 5:14 pm EST

Question: 1. The conductor circled in above screenshot is bonding jumper instead of grounding electrode conductor according to the NEC definition. Do you size this conductor according to 250.66 or 250.102? I see many people size it according to 250.66 (B) and use #4 Cu. But I think per code it should be sized according to 250.102. And 250.102 requires it to be larger than 3/0 Cu depending on the incoming service conductors size.2. When you bond the building steel to the concrete encased electrodes, the bonding jumper from building steel to the concrete encased electrodes shall follow the 250.102 and may be required larger than #3/0 Cu depending on the service conductor size. However the GEC from neutral to the building steel (not shown in the screen shot above but if we have one) follows 250.66 and is not required to be larger than #3/0 Cu. Why?Besides when you connect the neutral conductor directly to the concrete encased electrodes, the GEC is not required to be larger than #4 Cu according to 250.66 (B).I know they are code requirements, but i can not understand the logic/insight behind it. It doesn't make sense to me. Can someone explains it to me?Thanks!

Okay, let's break down the sizing of bonding jumpers vs. grounding electrode conductors (GECs) and the reasoning behind the differing requirements in the NEC.1. Sizing the Conductor in the Screenshot

You are correct. Based on the scenario depicted in the screenshot (which I can't see, but I'll assume is a bonding jumper connecting the neutral point to the service equipment enclosure), the conductor in question is a bonding jumper, specifically a main bonding jumper (MBJ). It is NOT a grounding electrode conductor.Therefore, it must be sized according to NEC 250.28 and 250.102, not 250.66. 250.28 (Main Bonding Jumper and System Bonding Jumper) clarifies where to install the bonding jumpers. 250.102 (Equipment Bonding Jumpers) This section dictates the size of the main bonding jumper. It requires that the main bonding jumper be sized based on the size of the service entrance conductors, per Table 250.102(C)(1). This table generally will require a larger conductor than a #4 Cu if you have large service conductors (as you pointed out, often 3/0 Cu or larger).

Why the confusion?

People often mistakenly use 250.66 because they incorrectly view the main bonding jumper as a GEC. This is a dangerous misunderstanding because it can lead to undersized conductors. The crucial difference is what the conductor is connecting to. GEC (250.66)

Connects the system (typically the neutral point) to a
grounding electrode system (e.g., ground rod, concrete-encased electrode, metallic water pipe). The grounding electrode provides a path to earth.

Main Bonding Jumper (250.28 and 250.102)

Connects the system (typically the neutral point) to the service equipment enclosure and other metal parts. This jumper ensures that all metal parts are at the same electrical potential as the neutral. This is critical for clearing ground faults and preventing dangerous voltage differences.

2. Bonding Steel to Concrete-Encased Electrode vs. GEC from Neutral to Steel


This is a great question that highlights the difference in function and the logic behind the different sizing requirements.Here's the breakdown: Bonding Jumper: Steel to Concrete-Encased Electrode (Per 250.102)

This connection's primary purpose is to create a
low-impedance path for fault current to return to the source (transformer) and trip the overcurrent protective device (circuit breaker or fuse) quickly. The idea is to minimize the time the fault current flows, reducing the risk of shock and fire. Since the fault current will likely be quite high, the bonding jumper needs to be able to handle it. Therefore, its size is related to the service entrance conductor size.

GEC: Neutral to Steel (Per 250.66)

This conductor's primary purpose is to connect the neutral to the grounding electrode system. The current flow through this path is not as high as the fault current, so a smaller conductor is acceptable. Also, the steel can function as a grounding electrode itself. According to 250.66, it is not required to be larger than #3/0.

Why the Size Difference?


The key is understanding what kind of current each conductor is expected to carry. Bonding Jumpers (250.102)

These are designed to carry
fault current. Fault current can be very high, especially in large services. The size of the jumper is tied to the size of the service conductors because larger services are capable of delivering larger fault currents. The goal is to provide a path for these currents that is low enough impedance to ensure the overcurrent protection device trips quickly.

GECs (250.66)

These primarily carry grounding current, which is generally much lower than fault current. Their primary purpose is to connect the electrical system to the earth (or other grounding electrodes) to help stabilize the system voltage and provide a path for lightning and other transient currents. A smaller conductor is adequate for this purpose.

3. GEC to Concrete-Encased Electrode from Neutral


You are correct. According to 250.66(B), the GEC is not required to be larger than #4 when connected to a concrete-encased electrode. This is because concrete-encased electrodes generally provide good grounding performance, and the code recognizes this.

In Summary Function dictates size. The primary function of a conductor (fault current path vs. grounding path) determines the appropriate sizing requirements. Bonding jumpers are for fault current. They must be large enough to handle the high fault currents expected in a system and are therefore sized according to the service entrance conductor size. GECs are for grounding. They provide a connection to the grounding electrode system, which helps stabilize the system voltage and provide a path for lightning and other transients. Since the currents they are expected to carry are generally lower, a smaller conductor is often permitted. Don't confuse the terms. Carefully distinguish between "bonding jumper" and "grounding electrode conductor" and understand the purpose of each. This will help you apply the correct code sections.I hope this explanation clarifies the code requirements and the logic behind them. Always refer to the latest version of the NEC for the most up-to-date information and consult with a qualified electrician for specific installation requirements. Flag for review