Question: Hey all,I've got a client that needs to be able to power their security camera system in the event of a power failure for up to a few hours. I have not been able to find a battery back-up that can provide power for more than 30 minutes. However, there are battery powered power banks that can provide hours of power for electronics however they don't come On automatically like a UPS would. I've been trying to find an ATS that could switch from house power to a power bank automatically in the event of power loss but haven't had any luck. Does anyone know if there is such a device? or if there is another way to accomplish this. Thank you
You've identified a common problem and the core components needed: a battery power source and an automatic transfer switch (ATS). Here's a breakdown of why you're having trouble finding a simple solution and several potential approaches
Why it's Tricky & Key Considerations:
Low Voltage vs. AC Power
Most security camera systems require low voltage DC power (e.g., 12V, 24V) rather than standard 120V AC. Battery banks usually output 5V USB or some higher voltage DC, or they invert to 120V AC. This means voltage conversion is likely necessary, adding complexity and inefficiency.
UPS Design for AC Load
Traditional UPS units are designed to switch over to AC power derived from their batteries. Using a UPS to power your camera system would involve:1. UPS converting DC battery power to AC.
2. AC to DC power adapter/converter supplying the camera system. This is inherently less efficient than staying in DC.
"Automatic" Switching Complexity
A true ATS needs to sense the power failure and then reliably switch over without glitching and causing a camera reboot. Simpler auto-switching solutions may not be fast enough, causing a momentary power interruption.
Power Consumption
How many cameras? What's the power draw of each camera (in Watts or Amps)? This is critical for determining battery capacity and runtime. Don't just guess; measure it with a multimeter or kill-a-watt type device if possible. Also consider the power draw of any recorders (NVRs or DVRs) that you would like to keep running.
Possible Solutions & Approaches
1.
Modified UPS for DC Power
This is often the best approach, although it might require some tinkering:
Find a UPS that you can modify
Look for a small, cheap UPS. Many have 12V batteries inside. The goal is to bypass the AC inverter and directly connect the camera's power supply to the battery when the mains power fails.
Rewire for DC
Carefully identify the battery terminals inside the UPS. The goal is to create a circuit that: Uses the UPS's charging circuit to keep the battery topped up while mains power is present. Automatically switches to the battery voltage to supply the camera's DC power supply (12V, 24V, whatever it needs) when mains power is lost.
Protection
Include a fuse in your modified circuit to protect against short circuits.
Voltage Regulation
Depending on the battery voltage and the camera's required voltage, you might need a DC-DC buck converter (step-down) or boost converter (step-up) to ensure the correct voltage is supplied to the camera.2.
Dedicated DC UPS Solution
Look for "DC UPS" or "Mini UPS"
Search online for "DC UPS," "Mini UPS," or "12V UPS" (or the specific voltage your camera system needs). These are specifically designed to provide uninterrupted DC power.
Pros
Easier to set up than modifying a standard UPS. They are built for DC devices.
Cons
May be more expensive than modifying a standard UPS, and selection might be limited. Ensure the amperage output is sufficient for all your cameras.3.
DIY ATS with a Dedicated Battery and Charger
Components
12V Battery (or appropriate voltage)
Deep-cycle battery is best. Sizing depends on the power draw and desired runtime.
Battery Charger
Smart charger to keep the battery topped up. Choose one that's designed for long-term float charging.
Relay
A double-pole double-throw (DPDT) relay. This will do the switching.
Power Supply
For your security camera system.
Wiring
The "normally closed" (NC) contacts of the relay connect to the output of your regular power supply. The "normally open" (NO) contacts connect to the battery voltage (possibly through a DC-DC converter). The relay coil is powered by the mains AC power. Normal Operation: When mains power is present, the relay is energized, connecting the security camera system to the regular power supply. Power Failure: When mains power is lost, the relay de-energizes, switching the security camera system over to the battery.
Important Considerations
Choose a relay with a switching speed fast enough to prevent the cameras from rebooting. You'll need to experiment. Also, ensure the relay can handle the current draw of the camera system.4.
Power Bank (less ideal but a possible option)
Find a power bank that can charge and discharge simultaneously. Some power banks will stop outputting power when charging, which defeats the purpose. This feature is often called "pass-through charging" or "uninterrupted power supply (UPS) mode". Use a USB to DC converter. Find a converter that boosts or bucks the 5V USB output to the appropriate voltage for your security cameras. Connect the power bank to the cameras. Plug the power bank into a wall outlet. This will keep the power bank charged and will automatically switch to battery power in the event of a power outage. Test thoroughly. Make sure the power bank switches over seamlessly without causing the cameras to reboot. Pros
Potentially cheaper than a dedicated UPS.
Cons
Less reliable and not specifically designed for this purpose. Limited selection of power banks with true pass-through charging. Voltage conversion adds inefficiency.
Important Considerations for All Solutions
Calculating Battery Size
Total Power Consumption
Add up the wattage (or amps x voltage) of all devices you want to power.
Desired Runtime
How many hours do you need the system to run?
Battery Capacity
Amp-Hours (Ah) = (Total Wattage x Hours) / Voltage (e.g., if using a 12V battery) Then, double the Ah needed to prevent over-discharging the battery. Deep cycle batteries prefer shallow discharge cycles.
Voltage Matching
Ensure all voltages are compatible. If your camera system needs 12V, and your power source is 24V, you
must use a DC-DC converter to step down the voltage. Overvoltage will damage your equipment. Safety
Use fuses in your circuits to protect against short circuits. Properly insulate all connections. If you're not comfortable working with electricity, hire a qualified electrician.
Testing
Thoroughly test your chosen solution under simulated power outage conditions to ensure it works as expected before deploying it for your client.
Recommendation:
Start by determining the exact power requirements of the security camera system. Then, consider the modified UPS or dedicated DC UPS solutions first. They offer a good balance of cost, reliability, and ease of implementation. If budget is a primary constraint, the modified UPS approach is worth exploring.Remember to prioritize safety and thorough testing! Flag for review