Question: My question ties into a post you made on facebook about where to bond the grounding electrode conductor and I asked about multiple outdoor panels on the same feeder that goes to a dwelling. Example got 200 amp meter and 8 ckt 200 amp main breaker panel with feed thru lugs set for homestead. But owner later placed mobile home about 80 feet away from this original master and panel so I ran 200 amp db aluminum to the mobile home but to comply with code I set a means of disconnect within 30 feet of the house and installed the same type of panel 200 amp main breaker 8 space with feed thru lugsSo I drove gr rods and tied them into the gr bar in the panel brings the panel is not first means of disconnect so no neutral to gr bond this made me question if I have a panel outside it should have ground rods??? Correct or only if they are part of the feeders?? And lastly what about a panel mounted over water on a boat dock what should you do there for lighting purposes should it have ground rods rods or no
Okay, I understand your scenario. It's a common one, especially on larger properties. Let's break down your questions point by point
1. Grounding Electrode Conductors and Multiple Outdoor Panels on the Same Feeder:
You have a 200A service at the meter, feeding the main panel at the "homestead." Then, you've extended a feeder to another panel near the mobile home. You correctly installed a disconnect within 30 feet of the mobile home and then the subpanel. Your approach to the mobile home subpanel is correct. You drove ground rods and connected them to the ground bar in the subpanel, and you did the right thing by NOT bonding the neutral to the ground bar in the subpanel. Because this is a subpanel, it is fed by a 4 wire feeder system. The ground and neutral must remain isolated in the subpanel. This is critical for safety.2. Outdoor Panels and Ground Rods: Always Required? No, ground rods are NOT always required at outdoor panels. Your statement "only if they are part of the feeders" isn't quite right, but you're on the right track. The NEC (National Electrical Code) generally requires grounding electrodes at each building or structure supplied by a feeder or branch circuit. Think of it this way: if the subpanel is feeding a separate building (like the mobile home), it needs its own grounding electrode system (ground rods, etc.). Your mobile home application is an example where this is required. Important Exception
If the feeder to the second building (mobile home in this case) also has a grounding conductor run with it back to the main panel at the "homestead", then you would need a local grounding electrode system at the second building.
Key Takeaway
If you run a 4-wire feeder (two hots, a neutral, and a grounding conductor) to a detached structure, then you must install a grounding electrode system (usually ground rods) at the detached structure and connect it to the grounding bar in the subpanel.
3. Panel Mounted Over Water (Boat Dock)
This is a special situation that requires careful consideration and usually involves more than just simple grounding rods.
Grounding Rods are NOT the Solution
You
DO NOT drive ground rods into the water for a boat dock panel. That is dangerous and completely ineffective. Water resistance is too high to provide a proper ground fault current path. What to do for Boat Docks
Equipotential Bonding
The most important thing is to create an equipotential plane. This means bonding all metal parts of the dock together (metal frame, metal pipes, metal light fixtures, etc.) to the grounding bar in the panel. This minimizes voltage differences that could lead to electric shock.
Ground Fault Circuit Interrupter (GFCI) Protection
ALL circuits serving the dock
MUST be GFCI-protected. This includes receptacles and lighting. GFCI's are life saving devices in damp or wet conditions. Grounding Conductor
A grounding conductor must be run back to the main panel, just like with a subpanel in a detached structure.
Signage
Post clear and conspicuous signage warning about electrical hazards near the water.
Local AHJ
Consult with your local Authority Having Jurisdiction (AHJ). Boat dock electrical installations have specific and often stringent requirements. Your local electrical inspector is your best resource.
In summary
Your mobile home subpanel is correctly grounded. Ground rods are generally required at a subpanel in a detached structure, provided there's a 4-wire feeder to that subpanel.* Do
NOT use ground rods in the water for a boat dock. Equipotential bonding and GFCI protection are crucial for safety.
Disclaimer: I am an AI chatbot and not a licensed electrician. This information is for educational purposes and should not be considered a substitute for professional electrical advice. Always consult with a qualified electrician before undertaking any electrical work. Flag for review