Question: I’ve seen the #8 pool bond run back a couple times to the pool subpanel now. Am I correct and saying it is not required, but not prohibited either?
You are generally correct. Here's a breakdown of the rules and reasoning
Background - What is a Pool Bond?
Purpose
Bonding aims to create an equipotential plane, meaning that all metallic parts around the pool are at the same voltage. This significantly reduces the risk of electric shock.
Materials
Typically, a solid copper conductor (#8 AWG is common) is used to bond together: Metallic parts of the pool structure (rebar, metal walls) Metallic parts within a specified distance of the pool (e.g., metal fences, light fixtures) Electrical equipment (pump motors, heaters, metal conduit, junction boxes) Pool water (through a listed pool water bonding device, if used)
The Question: Running the #8 Bond Back to the Subpanel Not Required
The National Electrical Code (NEC), specifically Article 680, does not require you to run the #8 bonding conductor back to the subpanel. The purpose of the bond is to create an equipotential grid around the pool, not necessarily to tie it directly to the electrical panel's grounding system.
Not Prohibited (Usually)
While not required, it is generally not prohibited to run the #8 bonding conductor back to the subpanel. However, there are a few caveats:
Proper Termination
If you do run the #8 back to the subpanel, it must be properly terminated to the grounding busbar (the one that's bonded to the enclosure and connected to the grounding electrode conductor). Don't just haphazardly connect it.
Don't Use as a Grounding Conductor
The #8 bonding conductor is not a substitute for the equipment grounding conductor (EGC) that must run with the circuit conductors supplying power to the pool equipment. The EGC's job is to provide a low-impedance fault current path back to the source so the overcurrent device (breaker or fuse) will trip in the event of a short circuit.
Redundancy
In some cases, running the #8 back to the subpanel might be considered redundant if you already have a robust bonding grid and proper grounding system in place. Some inspectors might question the purpose in those situations, but it's unlikely to be a violation as long as it's properly connected.
NEC Considerations NEC 680.26(C): Common Bonding Grid. This is the core requirement. All the specified metallic parts must be connected to a "common bonding grid." The code doesn't dictate that this grid must be connected to the subpanel. NEC 680.26(B): Pool Water Bonding. This is also important, if you are using a device to bond the pool water. NEC 680.21(A)(3): Grounding. This section deals with the equipment grounding conductor (EGC), which is required and runs with the power conductors to the pump, heater, etc. This is separate from the bonding conductor.
Why Might Someone Run it Back to the Subpanel? Perception of Improved Safety
Some people believe it provides an extra layer of safety by further tying the equipotential grid to the grounding system.
Local Practices
Local codes or inspectors might have their own preferences (though they should be based on the NEC).
Key Takeaways and Recommendation1. Focus on a Robust Bonding Grid
Ensure that all required metallic parts around the pool are properly bonded together using the #8 AWG copper conductor. This is the most important part.2.
Proper Grounding is Essential
Make sure that all electrical equipment has a properly sized equipment grounding conductor (EGC) running with the circuit conductors.3.
If You Run it Back, Do it Right
If you choose to run the #8 bonding conductor back to the subpanel, make sure it's properly terminated to the grounding busbar.4.
Consult Your Local Inspector
Always check with your local electrical inspector. They have the final say and can clarify any local requirements or interpretations of the NEC. They can also provide advice specific to your installation.5.
Documentation: Keep records of all bonding and grounding connections made for future reference.In summary, running the #8 bonding conductor back to the subpanel is generally not required by the NEC but is usually not prohibited as long as it's done correctly and doesn't create a hazard or violate other code sections. The most important thing is to ensure a properly installed and complete equipotential bonding grid around the pool area. Always consult with your local electrical inspector for specific guidance. Flag for review