Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: GEC run within a feeder conduit?

User: marmathsen, Location: Seattle, Washington ...ish

Asked on: Saturday, November 8, 2025 at 10:18 am EST
Answered on: Saturday, November 8, 2025 at 10:18 am EST

Question: Can a grounding electrode conductor be run within the same conduit as a feeder? Not a separate buildingIf so then you would also still need an equipment grounding conductor as well within the same conduit?And at the sub panel side would the GEC need to be kept separate from other EGCs, or could it be spliced to extend it to the electrode using the ground bar within the sub panel?I have a couple projects that have very limited access from the service to the grounding electrode but being able to use the feeder conduit would make a world of difference.Rob GSeattle

Okay, Rob, let's break down the NEC rules regarding running a grounding electrode conductor (GEC) in the same conduit as a feeder, particularly in a single building, and clarify the requirements for equipment grounding conductors (EGCs) and connections at the subpanel.

Can a GEC be run in the same conduit as a feeder in a single building? Yes, generally. The NEC does not prohibit running a grounding electrode conductor within the same raceway or conduit as the feeder conductors in a single building. There are some caveats, though, which are outlined below.

Do you still need an EGC in the same conduit with the feeder and GEC?
Yes. Absolutely. This is where a critical distinction comes in. The Grounding Electrode Conductor is for grounding the building's grounded (neutral) conductor to the grounding electrode. The Equipment Grounding Conductor is for grounding the metallic enclosures and non-current-carrying metal parts of electrical equipment. They have different purposes and are both essential.

Subpanel side GEC and EGC connections



GEC Termination at the Subpanel

The GEC can be connected to the ground bar within the subpanel.

However, this is only allowed if the subpanel is the first means of disconnect in the building.
If this is the case, the neutral bar and ground bar are bonded together and this type of installation is compliant. In this case there should also not be a grounding connection in the main service panel. EGC Termination at the Subpanel

The EGC must be connected to the ground bar at the subpanel. The ground bar and the neutral bar are kept separate (isolated) in the subpanel.

Important Considerations and Caveats


Conduit Material

If using metal conduit, the conduit itself can serve as the Equipment Grounding Conductor (EGC), provided it is installed per NEC 250.118 (e.g., rigid metal conduit, intermediate metal conduit, electrical metallic tubing with listed fittings). If you are relying on the conduit as the EGC, you must ensure all connections are tight and made with appropriate fittings listed for grounding. If using non-metallic conduit (PVC), you must run a separate EGC (insulated wire) within the conduit alongside the feeder conductors and the GEC.2.

GEC Sizing

The GEC size is determined by NEC 250.66 based on the size of the service entrance conductors. Note that the GEC only needs to be as large as the largest grounding electrode (ie, 6 AWG to rod/pipe/plate or 3 AWG to concrete encased electrode).
3.


GEC Material

While copper is common, you can use other materials approved for grounding electrode conductors, like aluminum (check NEC 250.64(A) for restrictions on aluminum GECs).
4.


Continuity and Protection

The GEC must be continuous (or spliced according to NEC 250.64(C)) and protected from physical damage (NEC 250.64(B)). If running it within conduit, that generally satisfies the protection requirement.
5.


Voltage Drop

While not directly related to the GEC/feeder conduit issue, remember to calculate voltage drop for the feeder conductors, especially with long runs, to ensure adequate voltage at the subpanel (NEC 215.2).

Summary for your "Limited Access" Scenario


Run both the feeder conductors, the GEC, and the EGC (if not using metal conduit as the EGC) within the same conduit.
2. Ensure the EGC is sized appropriately according to NEC 250.122, based on the feeder overcurrent protection.3. Make sure the GEC is sized according to NEC 250.66 and properly connected to the grounding electrode.4. Terminate the GEC and EGC on the grounding bar of the subpanel.5. Verify proper bonding/separation of the neutral and ground bars at the subpanel according to the rules above.Important Warning: Always consult the latest edition of the NEC and local amendments for the most up-to-date and accurate information. When in doubt, consult a qualified electrical inspector or licensed electrician in your area. Electrical work can be dangerous and should only be performed by qualified individuals. Improper grounding can create shock hazards and fire risks.By following these guidelines and exercising caution, you can potentially use the feeder conduit for the GEC in your limited access scenarios while maintaining a safe and code-compliant installation. However, make sure your local inspector agrees with the method. Flag for review