Topic: GEC for parallel conductors

User: aelec84, Location: Los Angeles

Asked on: Saturday, November 8, 2025 at 3:35 pm EST
Answered on: Saturday, November 8, 2025 at 3:36 pm EST

Question: forum,I have (2) parallel sets of 400kCMIL copper conductors and the GEC is connected to common ground bus and it is extending it to other electrodes. I believe equivalent area has to be considered which would be 800 kCMIL requiring 2/0 gec. Is this right? Thanks,

You are on the right track, but there are a few nuances to consider. Let's break it down

Understanding the Requirements
Service Entrance Conductors (SECs)

The size of the Grounding Electrode Conductor (GEC) is based on the
size of the largest ungrounded service-entrance conductor. This is crucial. We don't add the sizes of parallel conductors to determine GEC size.

Parallel Conductors

When you have parallel conductors, you effectively have one larger conductor.

NEC Table 250.66

This table is what you use to determine the minimum size of the GEC for grounded systems.

How to Apply It to Your Situation
1. Determine Equivalent Conductor Size

Since you have two 400 kCMIL conductors in parallel, you need to consider this equivalent size when referencing Table 250.66. 400 kCMIL x 2 = 800 kCMIL.
2.


Use NEC Table 250.66

Go to Table 250.66. Look for the column that specifies copper conductors and locate the row with the conductor size nearest 800 kCMIL.
If 800kCMIL does not exist in the chart, go to the next highest size listed which in this case would be over 500 kCMIL through 1100 kCMIL which requires a 2/0 copper GEC.

Therefore, you are correct in your assessment that a 2/0 copper GEC is required.
Important Considerations Material of the GEC

Your example assumes the GEC is copper. If you are using aluminum or copper-clad aluminum, refer to the
correct column in Table 250.66.

Terminations

Ensure the terminations for your GEC are properly rated for the conductor size.

Local Amendments

Always check for any local code amendments that may modify or add to the NEC requirements.


If the GEC is connected to a concrete-encased electrode (250.66(A), a ground ring (250.66(C), or a rod/pipe/plate electrode (250.66(B), there is often a maximum size limit for the GEC. Review these sections carefully. For example, if you're connecting to a ground rod, the GEC only needs to be a #6 copper, even if the table would normally require a larger conductor.


In SummaryYou are on the right track by considering the equivalent area of the parallel conductors. Use Table 250.66 of the NEC, considering the material of your GEC, and pay attention to the specific limitations of bonding to different electrodes. The GEC size is based on the

largest equivalent size of the parallel ungrounded conductors. Double check the electrode that the GEC is connected to. Flag for review