User: Alwayslearningelec, Location: NJ
Asked on: Sunday, November 9, 2025 at 11:26 am EST
Answered on: Sunday, November 9, 2025 at 11:37 am EST
Question: Don't have hoist data sheet but I'm going to feed it with 200A at 480v. Have a 120/277v source so will need step up xfmr.Seems pretty obvious but looks like need 225kva xfrm to deliver proper power to hoist, correct?
Yes, a 225 kVA transformer is likely the right size for your application, but let's break down the reasoning and consider some caveats.
Reasoning
Power Calculation
Your hoist requires 200A at 480V. The apparent power (kVA) required is calculated as: kVA = (Volts Amps √3) / 1000 (√3 is used for three-phase systems, which is highly probable for a hoist of this size) kVA = (480V 200A √3) / 1000 kVA = 166.28 kVA
Transformer Sizing
While 166.28 kVA is the calculated load, you don't want to run a transformer at 100% capacity continuously. Transformers have losses and derating factors to consider. A good rule of thumb is to add a buffer, often around 20-30%. 166.28 kVA 1.3 = 216.16 kVA
Standard Transformer Sizes
Transformers are typically available in standard sizes. The next common size up from 216.16 kVA is 225 kVA.
Therefore, a 225 kVA transformer seems appropriate.Important Caveats and Considerations
Hoist Data Sheet is CRITICAL
The absolute best way to determine the required transformer size is to consult the hoist's data sheet. The data sheet will provide:
Exact Voltage and Current Requirements
Don't assume 480V. Verify it!
Starting Current (Inrush Current)
Hoists, especially those with motors, can have very high inrush currents when starting. This can significantly impact transformer sizing. A transformer that is sufficient for running load may be undersized for starting. The data sheet will specify the Locked Rotor Amps (LRA) or similar specification. You might need a transformer designed to handle high inrush currents, or a larger kVA rating than calculated above.
Power Factor
The power factor (PF) affects the relationship between apparent power (kVA) and real power (kW). If the hoist has a low power factor (e.g., 0.8), you'll need a larger kVA transformer to deliver the required real power.
Duty Cycle
How often and how long will the hoist be running at full load? Continuous heavy use may require a larger safety margin.2.
Transformer Impedance
The impedance of the transformer is important, especially when dealing with motor starting. High impedance can cause voltage dips during startup. Ensure the transformer impedance is compatible with the hoist's requirements.3.
Transformer Taps
Many transformers have taps to adjust the output voltage slightly. This can be helpful to compensate for voltage drops in the wiring.4.
Wiring and Overcurrent Protection
Size the wiring and overcurrent protection (circuit breakers or fuses) for both the primary (120/277V) and secondary (480V) sides of the transformer. This must be done according to electrical codes (NEC in the US, or your local equivalent). This is critical for safety.5.
Environment
Consider the environment where the transformer will be installed (temperature, humidity, ventilation). Derating factors may apply in harsh environments.6.
Professional Consultation
Highly recommended. Given the voltage and current levels involved, and the critical nature of a hoist, consult with a qualified electrical engineer or electrician. They can properly assess the hoist's requirements, perform load calculations, select the appropriate transformer, and ensure that the installation complies with all applicable codes and safety regulations.
In summary:
While a 225 kVA transformer is a good starting point based on your initial information, you MUST get the hoist data sheet and ideally consult with an electrical professional to ensure a safe and reliable installation. Failure to do so could result in equipment damage, power outages, or even safety hazards. Flag for review