Question: Fire alarm contractor is replacing some damaged sprinkler water gongs with 120v bells they requested 120 at a J box there. I’m electrical maintenance and was asked to run it. We currently have some other upgraded 120 bells on there own circuits somebody did in the past that is not part of the facp main circuit but all marked and labeled . I’m wondering if it’d be ok for me just to tap into those so our bells all share the same circuits. Instead of pulling power from the main FACP circuit which is over 500 ft from the furthest riser i need to get to . Opinions?
Okay, let's break this down. You have a situation where you're being asked to provide power for new 120V fire alarm notification appliances (bells) to replace damaged sprinkler water gongs, and you're considering tapping into existing, separate 120V bell circuits rather than pulling from the main Fire Alarm Control Panel (FACP) circuit.Here's my opinion and the factors you need to consider
Potential Issues and Considerations:
Code Compliance (NFPA 72, NEC)
This is the most important. Your proposed solution may violate code, depending on local AHJ interpretation.
Dedicated Circuits
NFPA 72 (National Fire Alarm and Signaling Code) typically requires fire alarm notification circuits to be dedicated and supervised. This means they're intended to only power fire alarm devices. The existing 120V bell circuits may or may not be compliant.
Supervision
Fire alarm circuits must be supervised for faults (opens, shorts, grounds). Tapping into an existing, non-supervised 120V bell circuit creates a HUGE code violation. If a fault occurred on that circuit, it wouldn't be detected by the fire alarm system, rendering the bells inoperable when needed.
NEC Article 760
This article covers fire alarm systems. It has specific requirements for wiring methods, separation from other circuits, and power sources. Even if the existing circuits used to be compliant (unlikely), adding more devices could push them over capacity or violate other requirements.
AHJ Interpretation
The Authority Having Jurisdiction (AHJ), usually the local fire marshal or building inspector, has the final say. They can interpret the codes differently. It's wise to run your plan past them before doing any work.
FACP Supervision
The primary advantage of running a circuit directly from the FACP is the FACP's ability to monitor the circuit. The FACP knows if the circuit is healthy and can report faults. This is a critical safety feature.
Load Calculation and Capacity
Even if the existing 120V bell circuits are dedicated and supervised (unlikely), you need to verify that they have sufficient capacity (amperage) to handle the additional load of the new bells. Overloading a circuit can cause breakers to trip, rendering the bells inoperable during an emergency.
Coordination with Fire Alarm Contractor
You MUST communicate your plan with the fire alarm contractor. They are responsible for ensuring the entire system is compliant with the fire alarm codes. They may not be willing to certify the system if the power source isn't to their specifications.
Labeling and Documentation
Thorough labeling is essential, regardless of the solution you choose. Document everything clearly, including circuit numbers, wire sizes, and the devices connected to each circuit.
500-Foot Run
While a 500-foot run from the FACP is long, it's not insurmountable. It will require proper wire sizing to minimize voltage drop. A larger gauge wire might be needed to compensate for the distance.
Ground Fault Protection
In some jurisdictions, ground fault protection is required for fire alarm circuits. Verify this with your local codes.
My Recommendation
Do NOT tap into the existing 120V bell circuits without verifying that they are code compliant and discussing it with both the Fire Alarm contractor and the AHJ.
Here's a step-by-step approach:1. Contact the Fire Alarm Contractor
Explain your idea to them. They may have reasons why they specifically requested a circuit at the J-box. They can advise you on the best (and most compliant) solution.2.
Research Existing Circuits
Trace them back
Determine where these circuits originate. Are they truly dedicated to the fire alarm system? Are they supervised? If so, how?
Review documentation
Check electrical drawings, panel schedules, and any other documentation you can find to understand the purpose and configuration of these circuits.
Load Calculation
Perform a load calculation on the existing circuits to determine if they have sufficient capacity.3.
Contact the AHJ
Discuss your plan with the local fire marshal or building inspector. Get their feedback and approval before proceeding. This is crucial to avoid costly rework later.4.
If the existing circuits are NOT compliant
The only safe and compliant option is to run a dedicated, supervised circuit from the FACP. Accept the challenge of the 500-foot run and do it correctly.5.
If the existing circuits MAY be compliant (after thorough investigation)
Discuss the specifics with the fire alarm contractor and the AHJ before proceeding. Make sure they both sign off on the plan.
In Summary:
While tapping into existing circuits might seem like a convenient solution, it carries significant risk of violating fire alarm codes and compromising the safety of the building occupants. The most responsible approach is to prioritize code compliance and consult with the fire alarm contractor and the AHJ.Ultimately, the goal is to ensure that the fire alarm system functions reliably in an emergency, and that means adhering to all applicable codes and standards. Flag for review