Topic: bathtub or shower space

User: darekelec, Location: nyc

Asked on: Monday, November 10, 2025 at 6:55 am EST
Answered on: Monday, November 10, 2025 at 6:55 am EST

Question: is this graphic correct?or should 3' vertical line extend to the floor?2020 nec(C) Bathtub and Shower Space. Receptacles shall not beinstalled within a zone measured 900 mm (3 ft) horizontallyand 2.5 m (8 ft) vertically from the top of the bathtub rim orshower stall threshold. The identified zone is all-encompassingand shall include the space directly over tl1e tub or shower stall.Exception: In bathrooms with less than the required zone the recepta-cle(s) shall be permitted to be installed opposite the bathtub rim orshower stall threshold on the Jarthest wall within the room.

You're asking about whether the 3-foot horizontal boundary in the NEC's bathtub/shower receptacle rule extends to the floor.Based on the 2020 NEC language you provided, and the general understanding of this rule: Yes, the 3-foot horizontal line should extend to the floor.Explanation

The code says:
"... a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold."This means you measure 3 feet outward horizontally from the edge of the tub/shower. That 3-foot distance applies throughout the vertical zone. The vertical zone extends down from the 8-foot mark to the floor.

In other words, imagine a box that's 3 feet wide, 8 feet tall, and extends outward from the tub/shower. Receptacles aren't allowed within that box.
Key Considerations



Floor

If a receptacle is within 3 feet horizontally of the bathtub rim or shower threshold at floor level, it is not compliant.


All-Encompassing

The code emphasizes that the zone is "all-encompassing."*

Space Directly Over

Including the space directly above the tub or shower further reinforces the intent to restrict receptacles close to water sources.

Therefore, to be consistent with the NEC, the 3-foot horizontal line in your graphic should indeed extend vertically down to the floor.
Flag for review