Question: Can I temporarily wire something in a Class 1 Div 1 area using TC-ER-HL if I need to zip tie it or would it have to be Armor Clad if I do it at all? I would rather have a permanent fix but I am just wondering because it is outdoors and I have no cable tray if I am even allowed to do this?
Okay, let's break down the situation and the code requirements for temporary wiring in a Class 1 Division 1 hazardous location.
Understanding the Requirements Class 1 Division 1
This is a hazardous location where ignitable concentrations of flammable gases or vapors are present continuously, intermittently, or periodically under normal operating conditions. It's the most restrictive classification.
TC-ER-HL Cable
TC
Tray Cable. It's designed for use in cable trays.
ER
Exposed Run. This allows it to be run without conduit or cable tray in some applications, typically between a cable tray and a piece of equipment.
HL
Hazardous Location. This means the cable is tested and approved for use in certain hazardous locations, but not necessarily all Class 1 Division 1 locations.
Armor Clad Cable (e.g., MC Cable with an overall jacket for hazardous locations)
MC cable provides mechanical protection and, when properly selected with a suitable overall jacket, can provide the necessary protection for some hazardous location applications.
Zip Ties
Non-metallic zip ties are generally not allowed for permanent support of wiring in hazardous locations. Metallic straps or clamps may be permitted if they are compatible with the cable jacket and suitable for the environment (e.g., corrosion-resistant).
Temporary Wiring
The NEC does allow for temporary wiring under certain conditions. However, the same safety principles apply as for permanent wiring, maybe even a higher level of inspection.
The Issues with Your Proposal1. TC-ER-HL Adequacy
Check the Cable Listing
The critical question is this: Is the specific TC-ER-HL cable you intend to use explicitly listed and marked for use in Class 1 Division 1 locations? The 'HL' designation alone isn't a guarantee. You MUST refer to the cable's documentation and listings.
Exposure
Even if the cable is rated for Class 1 Division 1, you need to ensure that the conditions match. For instance, the cable might be rated for certain chemicals or temperatures but not others.2.
Support
Prohibited Support
Zip ties are almost certainly not permitted for permanent or temporary support in a Class 1 Division 1 area. They are not considered an approved method of securing cable, particularly in a location where mechanical integrity is critical for safety.
Outdoor Environment
The outdoor environment adds another layer of complexity. UV exposure, moisture, and temperature extremes can degrade zip ties quickly.3.
NEC 501.10(A)(1): Wiring Methods, Class I, Division 1. "All wiring and equipment shall be installed in accordance with Article 500 and shall also be installed in threaded rigid metal conduit, threaded steel intermediate metal conduit, or Type MI cable with fittings approved for the location."4. Lack of Cable Tray
TC-ER cable is intended to transition from a cable tray to equipment. Running it for an extended distance without a cable tray, and outdoors, is likely a violation of its intended use and the NEC.
What You NEED to Do Before Anything1. Consult the Cable's Listing
Obtain the manufacturer's specification sheet and listing information for the exact TC-ER-HL cable you plan to use. Look for explicit statements about its suitability for Class 1 Division 1 locations.2.
Hazardous Location Expertise
Consult with a qualified electrical engineer or inspector experienced in hazardous location wiring. This is not a DIY situation. They can properly assess the environment, interpret the code, and specify appropriate wiring methods and equipment. They also would be aware of any local amendments to the NEC.3.
Permitting and Inspection
Even for temporary wiring, you will likely need a permit and inspection from the local authority having jurisdiction (AHJ). This is a critical safety step.
Alternatives and Recommendations1. Rigid Conduit or MI Cable
The most common and generally accepted method for Class 1 Division 1 is threaded rigid metal conduit (RMC) or threaded steel intermediate metal conduit (IMC) with explosion-proof fittings. Type MI cable (Mineral Insulated) with approved fittings is also allowed.2.
Armor Clad Cable with Proper Listing
If RMC/IMC is impractical, investigate armor clad cable (e.g., MC cable) that is explicitly listed and marked for Class 1 Division 1 use. Ensure the fittings used are also approved for the location.3.
Cable Tray with Approved Cable
Install a cable tray system if you have long runs of cable. Use cable listed for use in the tray and approved for Class 1 Division 1, and ensure the tray itself is properly grounded.4.
Temporary Wiring Requirements
If you must use temporary wiring, adhere to the NEC's requirements in Article 590 and all the requirements for Class 1 Division 1 locations. The temporary nature does not exempt you from safety regulations. This likely means you'll still need conduit or an appropriately rated cable.5.
Proper Support
Use metallic straps or clamps designed for the cable type and suitable for the hazardous location. Ensure they are installed per the manufacturer's instructions and provide adequate support.6.
Remove all power from the area to prevent an Arc Flash from occuring while working.In summary
Your proposed method is highly unlikely to be compliant. You MUST consult with a qualified professional.* Prioritize safety and code compliance over convenience. The consequences of a failure in a Class 1 Division 1 location can be catastrophic.
Disclaimer: I am an AI chatbot and cannot provide definitive electrical code interpretations or engineering advice. Always consult with qualified professionals. Flag for review