Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Sauna Install and 250.32

User: trevorm, Location: Central Washington

Asked on: Monday, November 10, 2025 at 10:33 pm EST
Answered on: Monday, November 10, 2025 at 10:34 pm EST

Question: Hi Folks,I'm looking at running electrical to a sauna that's been built by a shop class. It has a Siemens spa pack mounted on the side that supplies the sauna heater with built in controls plus a couple breakers for a light & receptacle. It sits on skids and is small than the local authority requires a building permit for. Aside from the fact that the internal wiring will need to be inspected to ensure it meets code I'm trying to figure out if this sauna is classified as a "building or structure"If its a building or structure then that spa pack needs its own grounding electrode system. I've only ever installed spa packs attached to the same building that it is fed from. Also gets me thinking, if one mounts a spa pack on a post on the way to the sauna or hot tub it shouldn't need a grounding electrode system because its not mounted on a structure?Not sure if i'll take this one on due to the complications of the home built sauna but I'm still want to know thoughts on GEC system required for it or not?Thanks in advance!

You've hit upon a common and often confusing area of the NEC! Let's break it down

Is the Sauna a Building or Structure?

This is the KEY question. The NEC definition is what matters, not necessarily local building permit requirements (though local interpretation can influence this). NEC Definition of Building (Article 100)

"A structure that stands alone or that is separated from adjoining structures by fire walls with all openings therein protected by approved fire assemblies."


NEC Definition of Structure (Article 100)

"That which is built or constructed other than equipment."Here's the breakdown of how these definitions might apply to your situation:

Yes, a Building or Structure

If the sauna is intended to be permanently placed in its location, and is "built or constructed" (which it clearly is), then it's likely a
structure in the eyes of the NEC. The fact that it's on skids does not automatically exempt it. While "portable" buildings are a grey area, the intent matters and the manner it is connected. If you permanently connect power to it, and someone intends for it to be a permanent structure it should be treated as a building.

No, Not a Building or Structure

This is unlikely, but possible if the sauna is truly intended to be temporary and easily movable without any modification to its electrical connection (e.g., powered by a temporary cord & plug connection). A truly portable sauna on skids would likely be exempt but it would need to be readily movable.

Grounding Electrode System (GES) Requirements
Separate Building/Structure

If your sauna
is considered a separate building or structure,

NEC 250.32
mandates a grounding electrode system (GES) at the sauna. This means driving ground rods, connecting to a metal water pipe (if available and properly bonded), etc., at the sauna itself.

Mounted on a Post (Away from Building/Structure)

This is where it gets tricky! If the spa pack is not mounted on the sauna structure itself but on a separate post, and the spa pack is fed from the main panel,

you might be able to argue that the spa pack does not need a separate GES. This is because the post itself isn't necessarily considered a structure requiring its own GES. However, the AHJ (Authority Having Jurisdiction) could still require a GES if they consider the post to be a support for a permanent electrical installation. Furthermore, any metal components of the post structure would have to be bonded to the grounding system.

Key Considerations & Recommendations


Consult with the AHJ



This is the MOST IMPORTANT step! Call your local electrical inspector or permit office before you do any work. Explain the situation in detail and ask for their specific interpretation of the NEC and local amendments regarding separate structures and grounding requirements. Their decision is the final word.2.

Intent Matters

The intended permanence of the sauna influences whether it's considered a structure. Is it meant to be a permanent fixture?3.

Accessibility

Ensure the sauna is installed in a way that allows access for inspection and maintenance.4.

Safety First

Even if a GES isn't strictly required, consider the safety benefits of installing one. It provides an additional path for fault current to flow back to the source, helping to trip breakers and protect occupants.5.

Bonding

Regardless of whether a GES is required, ensure all metallic parts of the sauna, spa pack enclosure, and any associated equipment are properly bonded together.

Why the Confusion?The ambiguity stems from the grey area between "portable" equipment and permanent structures. The NEC aims to protect people from electrical hazards. Installing a GES at a separate structure provides an additional layer of protection.

In summary, I strongly advise you to consult with the AHJ before proceeding. Their interpretation of the code will dictate whether a GES is required for the sauna. If the AHJ says it needs a GES, install it. It's the safest and most code-compliant approach. Flag for review

Previous Question Next Question