Question: We have 4 Solis 10k inverters, parrelleled, 4g thhn from inverter to breaker on each inverter. 4/0 aluminum wire runs from combiner box up to disconnect whis is 300 feet. This disconnect is tapped into lines below meter whis is all 4/0. If we power up 2 inverters, they get up to 8000 watts, the line voltage goes up to 258.0 volts at inverters, 252.0 volts at disconnect. If we power 3rd inverter up, voltage ramps up over 264.0 volts and shuts inverter down.New wire, connections all tight, check line resistance in the 4/0 as well.If no inverters are turned on, the voltage is 248.0 at both the disconnect and at combiner box at inverters.Any ideas?

This is a tricky problem, but here's a breakdown of possible causes and troubleshooting steps, based on the information you provided

Key Issues and Potential Causes:
Overvoltage Tripping

The primary symptom is the inverters shutting down due to overvoltage. Grid-tied inverters are designed to protect themselves and the grid by disconnecting when voltage exceeds a certain threshold. 264V is definitely high for a 240V system.


Voltage Rise with Increased Generation

The voltage at the inverter increasing significantly as more inverters come online is a telltale sign of voltage rise on the line. This can be caused by impedance (resistance and reactance) in the wiring, or the grid itself being higher than acceptable.

300-Foot Run

A 300-foot run with 4/0 aluminum is long and can definitely contribute to voltage drop/rise. Even with good connections, impedance can still cause problems.


Utility Grid Strength (Source Impedance)

The utility grid itself might be the culprit. If the grid at your connection point has high impedance, the voltage will fluctuate more drastically as you feed power into it. Inverters push power into the grid, and if the grid has trouble "absorbing" it, the voltage will rise.

Troubleshooting Steps & Considerations


Recheck all Connections

This might seem obvious, but double-check

every single connection
– inverter terminals, combiner box connections, breaker connections, disconnect switch connections, taps at the service. Use a torque wrench to ensure connections are tightened to the manufacturer's specifications. Even a slightly loose connection can create resistance and heat. Look for any signs of oxidation or corrosion. Consider using an infrared (IR) thermometer to scan connections while the inverters are running. Hot spots indicate high resistance.2. Verify Wire Gauge and Type



Double-check

Confirm that the wire gauge (4/0 aluminum for the long run) and insulation type (THHN for the inverter to breaker) are correct for the amperage and voltage of the system, considering the distance and temperature rating. Make sure the 4/0 is rated for at least 75 degrees C.
Aluminum has higher resistance than copper.3.

Check for Neutral Issues



Open Neutral

A missing or loose neutral connection on the utility side can cause significant voltage imbalances and high voltage on one leg.
This is a dangerous situation and needs to be addressed immediately by a qualified electrician and the utility company. Use a multimeter to carefully check the voltage between each hot leg and neutral at the disconnect. The voltage should be close to 120 volts in both cases. If one leg is significantly higher, suspect a neutral problem.

High Neutral Impedance

Even if the neutral is present, high impedance in the neutral conductor can cause voltage issues.4.

Measure Voltage at Multiple Points Simultaneously

This is crucial for pinpointing the source of the voltage rise. Use multiple multimeters to measure the voltage at the same time at the following locations: Inverter terminals (each inverter) Combiner box input and output Disconnect switch At the utility service entrance (before your tap) Record these values as you turn on each inverter, one at a time. This will help you isolate where the voltage rise is most significant.5.

Measure Current

Use a clamp meter to measure the current on each phase of the 4/0 aluminum wire. This will help you verify that the load is balanced and that the current is within the allowable limits for the wire gauge.6.

Voltage Drop Calculations

Use a voltage drop calculator (many are available online) to estimate the voltage drop on the 300-foot run of 4/0 aluminum wire. Factor in the total current from all four inverters at full output. This will tell you if the wire gauge is adequate. Online calculators are abundant. Remember to use the actual length of the wire run, not just the straight-line distance.

Consider Increasing Wire Size

If the voltage drop calculation shows excessive drop, upgrading to a larger wire size (e.g., 250 kcmil or 300 kcmil aluminum) might be necessary.

Consider Copper Conductors
Copper conductors are much more efficient at carrying energy at a smaller diameter.7. Monitor Voltage Over Time

Use a data logger or multimeter with data logging capabilities to monitor the voltage at the inverters and disconnect over a period of several hours or days. This can help you identify patterns and see if the voltage issues are related to specific times of day or grid conditions.8.

Check Inverter Settings



Voltage Ride-Through Settings

Some inverters have adjustable "voltage ride-through" settings that determine how they respond to voltage fluctuations. Make sure these settings are appropriate for your grid conditions. (Consult the Solis manual for details.) However, don't simply raise the voltage trip point significantly without addressing the underlying problem.


Power Factor

Inverters can sometimes be configured to adjust their power factor. If possible, try setting the inverters to unity power factor (1.0). This can sometimes help reduce voltage rise.
9.


Contact the Utility Company



Crucial Step

The most important step! Explain the problem to the utility company and request that they investigate the grid voltage and impedance at your connection point. They may need to perform measurements at their transformers or substations to determine if there are any issues on their side. They may also have specific requirements or limitations for grid-tied solar systems. They also may be able to adjust the voltage at the transformer feeding your location to bring your voltage down. This may include lowering the high side voltage of the transformer.


Inform them that your inverters are shutting down due to overvoltage
and that you suspect a problem with the grid's ability to accept power. Documentation

Keep detailed records of all your measurements, observations, and communications with the utility company.10.

Reduce Inverter Output (Temporary Solution)

As a temporary measure, you might be able to reduce the output power of the inverters through their configuration settings. This would reduce the amount of power you're feeding into the grid and potentially lower the voltage rise. This is not a permanent solution, but it might allow you to keep the system running while you troubleshoot the underlying problem.

Important Safety Precautions



Work with qualified professionals

All electrical work should be performed by licensed and experienced electricians who are familiar with solar PV systems and grid interconnection requirements.


De-energize equipment

Always disconnect power to the system before working on any electrical components.

Follow safety procedures

Wear appropriate personal protective equipment (PPE), such as gloves, safety glasses, and insulated tools.


Be aware of arc flash hazards

Working on energized electrical equipment can create arc flash hazards. Take appropriate precautions to protect yourself from these hazards.

In summary:
The high voltage rise indicates an impedance issue. Isolate the location of the voltage rise with simultaneous measurements. The most likely cause is a utility grid problem, long cable run, undersized conductors, or a combination of all three. Contact the utility company immediately and be prepared to provide them with detailed information about your system and the voltage issues you are experiencing. Flag for review