User: pedro1200, Location: Ny
Asked on: Tuesday, November 11, 2025 at 12:00 pm EST
Answered on: Tuesday, November 11, 2025 at 12:01 pm EST
Question: While watching a grounding and bonding video Mike said GEC is equipment grounding did he mis speak or is that only true in remote buildings where in service disconnect and or sds it would be system grounding
Mike Holt is a very knowledgeable guy, but in this case, it sounds like he misspoke, or perhaps the statement was taken out of context. Here's why: GEC (Grounding Electrode Conductor)
The GEC connects the system grounded conductor (typically the neutral) to the grounding electrode (ground rod, water pipe, etc.). Its primary purpose is to create a low-impedance path to earth, stabilizing the voltage to ground and providing a path for fault current.
EGC (Equipment Grounding Conductor)
The EGC connects the non-current-carrying metal parts of equipment (enclosures, conduit, etc.) back to the source (service or separately derived system). Its purpose is to provide a low-impedance path for fault current to return to the source, facilitating the operation of overcurrent protective devices (breakers, fuses) and quickly clearing ground faults.
Here's the key distinction
The
GEC is about system grounding, connecting the neutral to earth. The EGC is about equipment grounding, connecting the metal parts of equipment to the source.
Regarding Remote Buildings and SDS
You're correct that things get a little more nuanced in remote buildings with a service disconnect and/or separately derived system (SDS). Here's how:
Service Disconnect at Remote Building
If a remote building has a service disconnect, it essentially becomes its own "service" from the utility's perspective. It needs its own grounding electrode system (ground rod, etc.) and a GEC connecting the neutral to that grounding electrode system.
Separately Derived System (SDS)
An SDS (like a generator or transformer) always needs its own grounding electrode system and a GEC connecting the neutral (or grounded conductor) of the SDS to that grounding electrode system. This is because the SDS creates a new source of power that must be independently grounded.
In these scenarios (remote buildings with service disconnects or SDS), the GEC does play a role in establishing a system ground at that location. However, it's still fundamentally about system grounding, not equipment grounding. The EGC is still needed to ground the equipment.
Why the Misunderstanding Might Occur
Sometimes, the terms can get confusing because both the GEC and EGC are involved in safety and fault current paths. The GEC helps to stabilize the system voltage with respect to earth, which indirectly aids in the operation of overcurrent devices during a fault.
In summary: While the GEC plays a role in establishing a grounding system, it is not the equipment grounding conductor. The EGC is specifically for grounding equipment and providing a low-impedance path for fault current back to the source to facilitate the operation of overcurrent protective devices. Flag for review