Question: I've been reading up on slash rating and maybe I'm overthinking it but some of the word is vague to me. It states it only applies when the lower value is path between line and ground and higher value is between phases. But also, any one pole does not see more than the lower value.To me this reads as for breakers the load must always be connected to gound. So, if I have a 2-pole breaker I can't connect both to a different leg of line/hot wire.But also, i that's the case why not just rate it to the lower value because It can't see more voltage than that. Is the 480Y/277, just there to help the guy spec'ing this from doing mental math or am I missing something. Because how I am currently reading this, Slash ratings make it sound like 2 pole breakers, they are just 2, 1 pole breakers that have a shared trip.
You're asking some very good and important questions about slash ratings! It's easy to get confused, and you're right to dig into the details. Let's break down the concepts to clarify things.
Understanding Slash Ratings (e.g., 480Y/277V) Purpose
Slash ratings (like 480Y/277V, 240/120V) are system ratings, not breaker ratings. They indicate the voltage levels that exist within a three-phase, four-wire electrical distribution system with a grounded neutral. The breaker itself can be rated, but the system rating tells you what is available for use.
Meaning
480V
This is the voltage between any two phase conductors (Line-to-Line).
277V
This is the voltage between any phase conductor and the neutral (Line-to-Neutral or Line-to-Ground in a properly grounded system). The "Y" in the rating indicates a wye configured system.
Why the Two Values? The dual rating exists because in a 480Y/277V system, both voltage levels are simultaneously available. Some loads need 480V (like large motors), while others need 277V (like lighting). Breaker Considerations
Breakers must be rated for the highest voltage they could experience in the system. In a 480Y/277V system, a breaker used between two phase conductors must be rated for 480V or higher. If a breaker is only used to protect a 277V Line-to-Neutral circuit, a lower voltage rating might be acceptable (depending on specific codes and standards), but in practice, it's often simpler and safer to use breakers rated for the full 480V to ensure compatibility and flexibility.
Addressing Your Specific Concerns1. "It states it only applies when the lower value is path between line and ground and higher value is between phases." This statement is generally correct in the context of a three-phase, four-wire system. The lower voltage (e.g., 277V in 480Y/277V) is always the voltage between a phase conductor and the grounded neutral. The higher voltage (e.g., 480V) is the voltage between two phase conductors.2. "To me this reads as for breakers the load must always be connected to gound. So, if I have a 2-pole breaker I can't connect both to a different leg of line/hot wire." This is NOT correct. A 2-pole breaker (in a 480Y/277V system) can absolutely be used to connect a load between two different phase conductors (i.e., for a 480V load). The key is that the breaker must be rated for at least 480V. It's NOT about forcing everything to be connected to ground; it's about ensuring the breaker can safely interrupt the highest voltage it might encounter.3. "But also, if that's the case why not just rate it to the lower value because It can't see more voltage than that. Is the 480Y/277, just there to help the guy spec'ing this from doing mental math or am I missing something." You're missing the fact that a breaker in a 480Y/277V system can "see" 480V if it's connected between two phase conductors. That's why it needs to be rated for that voltage. The 480Y/277V rating is NOT just for mental math. It's crucial for understanding the voltage levels present in the system and selecting the correct components. If you are only connecting to a line and neutral(ground) your breaker will never be exposed to a voltage greater than 277V.4. "Because how I am currently reading this, Slash ratings make it sound like 2 pole breakers, they are just 2, 1 pole breakers that have a shared trip." While 2-pole breakers do indeed have a shared trip mechanism (so that both poles trip simultaneously in case of an overload or fault on either pole), they are NOT simply two independent 1-pole breakers. The key difference is that a 2-pole breaker is designed and rated to interrupt the higher voltage present between phases. You cannot simply gang up two single-pole breakers in most jurisdictions and use them as a replacement for a proper 2-pole breaker.
Analogy
Think of it like a highway. The highway itself has a speed limit (the system voltage). Cars (breakers) need to be able to handle that speed (voltage). Some cars (breakers) might only need to travel at a lower speed (277V), but if they're going to be on the main highway, they need to be able to handle the full speed limit (480V).
Key Takeaways Slash ratings (e.g., 480Y/277V) describe the voltage levels in a three-phase, four-wire system. Breakers must be rated for the highest voltage they could encounter in the system. 2-pole breakers can be used for both Line-to-Line (480V) and Line-to-Neutral (277V) loads if rated appropriately. 2-pole breakers are NOT just two 1-pole breakers with a shared trip. They are designed to interrupt higher voltages.* Always consult electrical codes (NEC in the US) and local regulations for specific requirements.