Topic: Flickering LED bulbs.

User: Greg Gniewkowski, Location: Ford Motor Company

Asked on: Tuesday, November 11, 2025 at 7:32 pm EST
Answered on: Tuesday, November 11, 2025 at 7:32 pm EST

Question: Hello. Looking for advice & counsel for the following problem I have in our home. All of the LED bulbs will 'flicker' slightly but enough to be noticeable - no strobe effect. Like watching the light level click up or down by a factor of 1; nothing major but slightly annoying. Some background on our home; built 1971 with all aluminum wiring from meter socket to main panel and all throughout the home. Standard 120/240VAC 150A service. It is more noticeable when a resistive load is plugged in (clothes iron, coffee pot, dryer) or when the HVAC fan motor runs. I have done a thermal scan of the main with a FLIR camera I have and also checked the incoming V with a Fluke True RMS DMM - did not notice any significant changes in temp with FLIR, and V levels fluctuated @ 0.4~0.8 with the DMM held steady on the main lugs for @30 seconds. I am making an educated guess that what is happening is - due to minor V level fluctuations that older Incandescent bulbs would not have been affected by, that the V level changes are causing the internal circuitry of the LED bulbs to constantly adjust due to V levels and that this is causing the current problem. Can I correct this problem by putting an SPD in the main panel or is there some other method I should consider. Any advice I can get would be appreciated. Thank You.

Okay, this is a common and frustrating issue with LED lighting in older homes, especially with aluminum wiring. Your detective work so far is excellent. Let's break down the problem and potential solutions

Understanding the Issue

Your hypothesis about voltage fluctuations affecting the sensitive electronics in LED bulbs is likely correct. Here's why: Aluminum Wiring

Aluminum wiring is known to expand and contract more than copper with temperature changes. This can lead to loose connections at outlets, switches, and in the panel. Loose connections introduce resistance, causing voltage drops when loads are applied.


LED Sensitivity

LED bulbs are solid-state devices. They have internal drivers (small circuits) that regulate the current flowing through the LED. These drivers are designed to operate within a specific voltage range. Even small voltage variations outside that range can cause the driver to adjust, resulting in the flicker you see.

Resistive Loads

Resistive loads (like irons, coffee pots, and dryers) draw significant current. When these loads switch on, they cause a momentary voltage drop in the circuit, exacerbating the problem with aluminum wiring.


HVAC Motors

Starting an HVAC motor also causes a voltage dip. Motors draw a large inrush current when starting up, which will also impact the V level.

Is it an SPD (Surge Protective Device) Issue?


While an SPD is always a good idea for protecting electronics from voltage surges (lightning, utility switching), it is unlikely to directly solve the flickering problem you're experiencing. An SPD is designed to clamp down on transient voltage spikes, not constant voltage fluctuations.

Possible Solutions

Here's a breakdown of steps you should consider, in roughly the order of importance and cost:1. Address Aluminum Wiring Connections (Most Important)



Professional Inspection



This is critical.
You must have a qualified and licensed electrician experienced with aluminum wiring thoroughly inspect all connections in your home: Main panel Sub-panels (if any) Outlets Switches Light fixtures (especially junction boxes) Corrective Measures

The electrician will likely recommend one or more of the following:


CO/ALR Connectors

Replace existing connections with CO/ALR (Copper to Aluminum Rated) connectors. These are specifically designed to handle the different expansion/contraction rates of copper and aluminum. They use a special anti-oxidation compound to prevent corrosion. This is the most common and recommended solution.



Pigtailing with Copper

Pigtail (joining) copper wires to the existing aluminum wires using CO/ALR connectors at each connection point. This allows you to use standard copper-rated outlets, switches, and fixtures.


Complete Rewiring

In extreme cases, rewiring the entire house with copper might be necessary, but this is a very expensive and disruptive option.

Do NOT attempt to fix aluminum wiring connections yourself if you are not a qualified electrician. Improperly handled aluminum wiring can create a serious fire hazard.2.

Voltage Regulation (Possible, but Less Likely to be the Only Solution)



Line Conditioner/Voltage Regulator

You
could try installing a line conditioner or voltage regulator specifically designed for the entire house or a problematic circuit. These devices actively maintain a stable output voltage despite input voltage fluctuations. This is a more expensive solution and not always guaranteed to eliminate the flicker entirely, especially if the underlying aluminum wiring issue isn't addressed.

AVR UPS

If you only have one or two fixtures that are really bad, you can plug them into a AVR UPS. This may be overkill for only a single fixture.3.

Check Neutral Connections



Neutral Wire Issues

Problems on the neutral wire of your electrical system can also cause voltage fluctuations and flickering. This is especially true in shared neutral circuits. Have your electrician thoroughly inspect the neutral connections in the main panel and any sub-panels.4.

LED Bulb Selection



Higher Quality Bulbs

Some LED bulbs are more tolerant of voltage fluctuations than others. Consider trying a different brand or model that is known for better performance and a wider input voltage range. Look for bulbs with "flicker-free" or "stable light output" claims.

Dimmer Compatibility

If you have any dimmer switches, ensure that the LED bulbs are specifically rated as compatible with LED dimmers. Incompatible bulbs can flicker or buzz. Consider replacing older dimmers with LED-compatible dimmers.


Wattage

Use the correct wattage bulbs for the fixtures.5.

Monitor Voltage Over Time



Long-Term Voltage Monitoring

Borrow or rent a power quality analyzer (if possible) to monitor the voltage at your main panel
over a 24-hour period. This will give you a much more detailed picture of the voltage fluctuations and when they occur. This can help pinpoint the source of the problem.6.

Contact Your Utility Company



Utility Voltage Issue

In rare cases, the problem might originate from the utility company's side. If you've ruled out other causes, contact your utility and ask them to check the voltage at your meter.

Why Not Just an SPD? (Again)An SPD protects against short-duration voltage spikes. The issue you're describing is continuous voltage fluctuations. An SPD won't address that.

In Summary:The most likely cause of your LED flickering is voltage fluctuations due to loose connections associated with aluminum wiring. Your first and most critical step is to have a qualified electrician inspect and repair the aluminum wiring connections. Only after addressing that should you consider other solutions like voltage regulators or different LED bulbs.Good luck! Be safe, and don't hesitate to ask follow-up questions. Flag for review