User: Aistobasbistoc9, Location: Texas
Asked on: Wednesday, November 12, 2025 at 9:37 am EST
Answered on: Wednesday, November 12, 2025 at 9:38 am EST
Question: Hi,I have a situation where there is a disconnect before the panel on the secondary of a 480-208 3PH step down transformer. The GEC on the transformer is a #6 (30kVA unit), and the secondary feeder is a to a 100A disconnect and also has a #6 gnd. wire. Does the feeder after the disconnect to the panel also require a #6 gnd. wire? Or can this be a typical #8 gnd. that would be minimum for a 100A feeder?Thank you
Okay, let's break this down according to the NEC (National Electrical Code). Your situation involves a separately derived system (SDS) due to the transformer, and the rules for grounding electrode conductors (GECs) and equipment grounding conductors (EGCs) are different.Here's the relevant NEC information and how it applies to your situation
Understanding the Key Differences
Grounding Electrode Conductor (GEC)
Connects the separately derived system's grounded conductor (typically the neutral) to a grounding electrode (e.g., ground rod, building steel). Its size is based on the size of the derived phase conductors or derived ungrounded conductors and found in
NEC 250.66. This is the #6 you already have connecting the transformer neutral to ground. Equipment Grounding Conductor (EGC)
Connects the non-current-carrying metal parts of equipment (enclosures, raceways, etc.) back to the source (transformer neutral in this case). Its size is based on the overcurrent protective device (OCPD) protecting the circuit. This is the conductor that runs with the feeder conductors, and is found in
NEC 250.122.
Your Specific Scenario1. Transformer GEC
You have a #6 GEC running from the neutral point of the 480-208Y/120V transformer to a grounding electrode. This appears correct, assuming the ungrounded conductors feeding the primary are not bigger than 1/0awg (see 250.66)2.
Feeder TO the Disconnect
You mention the feeder going to the 100A disconnect includes a #6 ground wire. This likely means you intended to use the #6 as an EGC.3.
Feeder FROM the Disconnect to the Panel
This is the crucial part. This is where your question focuses.
Analysis and NEC Requirements NEC 250.122 dictates the minimum size of the EGC based on the size of the overcurrent protective device (OCPD) protecting the circuit. In your case, the feeder is protected by a 100A disconnect. Consult NEC Table 250.122. For a 100A OCPD, the minimum size EGC is #8 AWG copper or #6 AWG aluminum.
Answer to Your Question
The minimum acceptable EGC from the disconnect to the panel is #8 AWG copper (or #6 AWG aluminum). You are not required to continue using a #6 EGC from the disconnect to the panel.
Important Considerations and Clarifications Grounding Electrode Conductor (GEC) vs. Equipment Grounding Conductor (EGC)
Do not confuse these. The GEC is for grounding the system neutral. The EGC is for fault current path for equipment safety.
Larger EGC is Allowed
You can always use a larger EGC than the minimum required. Using a #6 EGC from the disconnect to the panel would be code-compliant, but it's not required.
Raceway as EGC
If the feeder is installed in metallic conduit (RMC, IMC, or EMT) and all connections are made per NEC 250.118, the conduit itself can serve as the EGC. However, you MUST ensure proper bonding at all connections. This is less common for subpanels from transformers because a wire type EGC is almost always preferred.
Bonding
Ensure proper bonding of all metal enclosures, including the transformer enclosure, the disconnect enclosure, and the panel enclosure.
Local Amendments
Check with your local electrical inspector or authority having jurisdiction (AHJ). Local codes may have amendments or stricter requirements than the NEC.
In summary
You're safe to use a #8 copper EGC from the 100A disconnect to the panel.
Disclaimer: Consult with a qualified electrician or electrical engineer for specific project guidance and to ensure compliance with all applicable codes and regulations. Flag for review