Question: I'm installing a Residential service with a 320 /400 amp meter combo disconnect . poco will switch to underground service in my 3" pvc trench ..I have a 200 amp breaker to the house and a 150 amp breaker to a new Garage . My question : is the water GEC requirement for 400 amps? (1/0) or 320 continuous amps ?(#2) copper? ......... of course the water meter is 80' away across the basement. Thanks !!
Okay, let's break down the Grounding Electrode Conductor (GEC) sizing for your situation. This is based on the National Electrical Code (NEC), which is the standard for electrical installations in the US. Always consult with a licensed electrician and local code requirements for your specific location, as they take precedence.Key Considerations
The Service Entrance Conductor Size is the Determining Factor
The NEC doesn't directly base the GEC size on the meter or the breaker sizes. Instead, it's based on the size of the service entrance conductors.
Parallel Conductors
This is very important. With a 320/400 amp service, you almost certainly have parallel conductors for the service entrance. You need to calculate the equivalent size of the parallel conductors.
Table 250.66
This is the crucial NEC table that tells you the minimum size of the GEC based on the size of the service entrance conductors.
How to Determine the GEC Size1.
Identify Service Entrance Conductor Size
You need to know the actual AWG or kcmil size of each of the parallel conductors feeding your 320/400 amp meter base. For example, you might have two sets of 3/0 copper conductors in parallel.2.
Determine the Equivalent Size
Add the ampacities of the parallel conductors to get the total ampacity. Then, refer to NEC Table 310.16 (or the appropriate table for the conductor type and insulation rating you're using) to find the single conductor size that would have that same ampacity. This is your equivalent conductor size.
Example
Let's assume you have two parallel sets of 3/0 AWG copper conductors per phase. According to Table 310.16 (75°C column), 3/0 copper has an ampacity of 200 amps. Two in parallel gives you a total ampacity of 400 amps. Looking back at Table 310.16, a 600 kcmil copper conductor has an ampacity of 420 amps. Thus your equivalent conductor size for GEC sizing purposes is 600 kcmil copper.3.
Use NEC Table 250.66 to Find GEC Size
Once you have the equivalent service entrance conductor size, consult Table 250.66 to find the minimum GEC size.
Example (Continuing from above)
With a 600 kcmil copper service entrance conductor (equivalent size), Table 250.66 requires a 1/0 AWG copper GEC.
Regarding Your Specific Question
Is it based on 400 amps or 320 continuous amps? Neither. It's based on the service entrance conductor size, which is dictated by the calculated load and the 320/400 amp rating (which is a factor in determining the conductor size). The 320A rating is the continuous load rating (80% of 400A).
Important Considerations and Clarifications
Distance to Water Meter
The 80-foot distance is a significant factor. While you can run the GEC that distance to the water meter (assuming it's properly bonded to the metallic water piping system for at least 10 feet and made electrically continuous), it's often better to supplement the water pipe electrode with an additional electrode such as a ground rod or ground ring. This is to improve the overall grounding system impedance.
Supplemental Electrode
NEC 250.53(D)(2) requires a supplemental electrode if the grounding electrode conductor to the water pipe is not accessible or the connection to the water pipe is made more than 5 feet from the point of entrance to the building. Even if it's not strictly required, it's generally good practice.
Bonding
You'll need to bond the metallic water piping system as close as practical to the point where it enters the building (within 5 feet if possible). This bonding jumper must be sized according to Table 250.102(C)(1) based on the service entrance conductor size not the GEC size.
Concrete Encased Electrode (Ufer Ground)
If you have a concrete-encased electrode (Ufer ground) in your footing/foundation, that also needs to be connected to the grounding system and can be used as one of the required electrodes.
In Summary
1. Determine the size and number of service entrance conductors.
2. Calculate the equivalent size of the parallel conductors.3. Use NEC Table 250.66 to determine the minimum GEC size.4. Consider a supplemental electrode (ground rod or ground ring), especially given the long distance to the water meter.
5. Ensure proper bonding of the metallic water piping system.
WARNING:Electrical work can be dangerous. This information is for general guidance only and is not* a substitute for the expertise of a qualified, licensed electrician. Improper grounding can lead to serious shock hazards and equipment damage. Always consult with a professional before starting any electrical project. Also, local codes may differ from the NEC, so always check with your local electrical inspector. Flag for review