Topic: Service wireway bonding with parallel conductors.

User: JP23, Location: California

Asked on: Thursday, November 13, 2025 at 10:44 am EST
Answered on: Thursday, November 13, 2025 at 10:44 am EST

Question: I'm a little confused about the exact method to bond the grounds in a wireway containing conductorstapped before the main for a solar back feed. I'm assuming these are still considered service conductorssince they are either from the solar service or utility service and tied together. Am I right in this?Four parallel of wire sets of 350 MCM conductors with one 3/0 ground for each set runningfrom the service equipment to the disconnect in a wireway. Myers hubs top and bottom from the equipment tothe wireway. The hubs in the wireway have lay-in lugs attached to them. I want to land a straightrun of 3/0 to all the hubs and land it on a lay-in lug in the wireway and then land one of the 3/0's from the setson another lay-in lug next to that one. I'm reading that each ground in multi conductor cables in wirewaysrun in parallel need to land in the wireway. Not using multiconductor cable so not sure if that applies.No big to install three more lugs but wondering if it's required.

Okay, let's break down the grounding requirements for your solar backfeed wireway setup, and address your specific questions. This is a critical area, and accurate grounding is essential for safety and code compliance.

Understanding Service Conductors and Grounding Service Conductors

You are correct in your assessment that the conductors tapped
before the main overcurrent protection device, whether from the utility grid or the solar service, are considered service conductors. This is because they carry the full available fault current of the utility or the solar array.

Grounding Importance

Because these are service conductors, the grounding requirements are stricter than for feeder or branch circuits. Effective grounding provides a low-impedance path for fault current to return to the source, tripping the overcurrent protective device and preventing dangerous voltage on equipment.

Specifics of Your Installation
Four Parallel Sets

You have four sets of 350 MCM conductors, each with a 3/0 ground wire.


Wireway

Conductors run from service equipment to a disconnect through a wireway.

Myers Hubs

You're using Myers hubs to transition from the equipment into the wireway, and the hubs have lay-in lugs attached inside the wireway.


Proposed Grounding

You're proposing running a continuous 3/0 conductor to bond all the Myers hub lugs together and then landing one of the four 3/0 equipment grounding conductors on a lug in the wireway.

Analysis and Code Requirements (NEC - National Electrical Code)


The key is to ensure that the Equipment Grounding Conductor (EGC) path is continuous and has adequate ampacity for the available fault current. Here's how the NEC applies:1. Continuity and Sizing of EGCs (NEC 250.24, 250.28, 250.122)

Each of your four parallel sets of conductors must have an effective EGC. The 3/0 ground wire in each set is sized based on the overcurrent protection of the 350 MCM conductors, according to NEC 250.122. Since these are service conductors running in parallel, 250.30(A)(6) is very important. You must comply with this section.
2.


Wireway Grounding



Metal Wireway as EGC (NEC 376.60)

A metal wireway
can serve as the equipment grounding conductor if it meets the requirements of 250.4(A)(5) and is properly installed. However, supplemental grounding is often recommended, especially with service conductors.

Myers Hubs

The Myers hubs provide a mechanical connection, but they do not automatically guarantee a reliable, low-impedance grounding path. This is why you are planning to use the lay-in lugs.3.

Bonding the Wireway (NEC 250.92)



Service Equipment Enclosures

The wireway, as an enclosure containing service conductors,
must be bonded to the service equipment grounding system. This means a solid, reliable connection back to the grounding electrode conductor (GEC) or the grounded conductor (neutral).

Why Your Proposed Method May Not Be Sufficient


While running a 3/0 conductor to bond the Myers hub lugs together is a good step, simply landing
one of the four 3/0 EGCs on a lug may not fully satisfy the requirements because it leaves the other three runs without a direct connection to the bonding point within the wireway. Here's why: Parallel Paths

The intent of running parallel conductors (including EGCs) is to create multiple parallel paths for current. By only connecting one EGC, you're essentially forcing all the fault current from all four sets of conductors to flow through that single EGC, which could overload it in a fault condition.

Fault Current Distribution

Ideally, each of the four sets of conductors should have a direct, low-impedance path back to the grounding point.

Recommended Grounding Method


Here's the recommended method to ensure proper grounding and code compliance:1. Continuous Bonding Conductor

Continue with your plan to run a continuous 3/0 copper conductor along the entire length of the wireway, connecting to the lay-in lug of each Myers hub. This will bond the wireway to the service equipment grounding system. (The size of the bonding jumper is dictated by Table 250.102(C)(1).)2.

Connect
All EGCs

This is the critical part. You
must connect each of the four 3/0 EGCs to the bonding conductor in the wireway. Here's how: Install additional lay-in lugs next to the lugs on the Myers hubs. Land each of the 3/0 EGCs onto its own lay-in lug and connect the lug to the continuous 3/0 bonding conductor. You essentially create a junction point for each EGC where it ties into the wireway grounding system.
Important

The connection of each EGC to the bonding conductor must be reliable and have sufficient ampacity for the potential fault current.3.

Grounding Electrode Conductor (GEC)

Ensure the wireway is properly bonded to the service grounding electrode system (ground rods, etc.) using a properly sized grounding electrode conductor. You should consult the appropriate sections of the NEC to verify the size of this GEC. This is a critical step. 250.166

Answer to Your Specific Question


Yes, you need to install three more lugs, so that each of the equipment grounding conductors (EGC) in the wireway are connected properly to the wireway grounding system. It's required to provide a reliable, low-impedance path for fault current for
each of the parallel conductor sets.

Additional Considerations
Torque Specifications

Ensure all connections are properly torqued to the manufacturer's specifications. Loose connections can create high resistance, defeating the purpose of the grounding system.

AHJ (Authority Having Jurisdiction)

Always consult with your local electrical inspector (AHJ) for any specific requirements or interpretations in your area. Their interpretation of the code is what matters for compliance.


Documentation

Keep detailed records of your grounding system, including conductor sizes, connection methods, and torque values. This will be helpful for future maintenance and inspections.

In Summary


You are on the right track with bonding the wireway, but you must ensure that each of the four equipment grounding conductors (3/0 copper) is properly connected to that bonding system within the wireway. This provides the multiple, parallel grounding paths required for a safe and compliant installation with parallel service conductors.Remember to consult the latest edition of the NEC and your local AHJ for specific requirements in your area. This information is for guidance only and should not be considered a substitute for professional electrical engineering advice. Flag for review