User: AylmerQc, Location: Canada
Asked on: Thursday, November 13, 2025 at 10:50 am EST
Answered on: Thursday, November 13, 2025 at 10:50 am EST
Question: I normally do maintenance so I don't get too much hands on experience ordering material.Located in Nunavut, in a small remote hamlet so I don't have access to an electrical wholesaler and everything needs to be figured out on what is needed then ordered then shipped or flown in.The pressure washer draws 85 amps 208 V 3phase (from the specs label).The pressure washer is located in a garage between bays and will be used to clean trucks and heavy equipment.The manual advises that it be on a GFCI, or a twist-lock connection or hardwired.Hardwired isn't really a good option since I'd need to run the Teck cable overhead and down to the pressure washer.I've chosen to use SOOW with Hubble pin and sleeve connector/socket so that the cable can be rolled up when the machine isn't in use.I've planned on a 100 amp 3P breaker and 60 feet of Teck cable to a 100 amp disconnect with an attached pin-sleeve 100 amp receptacle.On site we have 3C #3 AWG Teck cable. Wo don't have the SOOW cable although in our system inventory database it list 4C #2 AWG SOOW.My questions are:can I use #3 Teck cable up to the disconnect then # 2 for the cab tire or do I need to stick to all one size AWG?Does the disconnect need to be fused?Thanks in advance...
Okay, let's break down the electrical requirements for your pressure washer installation, keeping in mind the unique challenges of your location.
Understanding the Requirements Pressure Washer Load
85 Amps, 208V, 3-Phase
Location
Garage, remote hamlet (Nunavut)
Connection Method
Pin and Sleeve Connector (chosen for flexibility)
Available Materials
3C #3 AWG Teck Cable, possible access to 4C #2 AWG SOOW (verify)
Addressing Your Questions1. Can I use #3 Teck cable up to the disconnect then #2 for the cab tire or do I need to stick to all one size AWG? No, you CANNOT decrease conductor size. You must maintain or increase the conductor size from the breaker to the load. You are decreasing the conductor size from #3 AWG to #2 AWG. NEC 240.4(D) has conductor ampacity rules. A #3 AWG copper conductor rated for 75 degrees Celcius is rated for 85 amps. There are exceptions to this that can increase this amperage, however, the code is very clear about where those exceptions apply, and using SOOW cord in a general-use application is not an exception. Reasoning
The goal is to protect the wiring from overheating. Using a smaller conductor after a larger one creates a bottleneck. If the pressure washer draws its full 85 amps, the #3 AWG cable will be at it's maximum allowed load. The #2 AWG conductor is able to handle 95 amps.
Solution
Use #2 AWG Teck cable from the breaker to the disconnect switch. Then, use #2 AWG SOOW from the disconnect to the pin and sleeve connector. If you have access to 4C #2 AWG SOOW, verify its availability and condition.2.
Does the disconnect need to be fused? Not necessarily, but it is highly recommended. Without fuses
The breaker upstream provides overcurrent protection. A non-fused disconnect just acts as a switch to isolate the pressure washer.
With fuses
Fuses in the disconnect provide additional and more localized protection. If a fault occurs in the SOOW cable or the pressure washer itself, the fuses will blow before the upstream breaker trips, potentially limiting the damage.
Recommendation
Install a fused disconnect switch. It's a worthwhile investment for safety and equipment protection, especially in a remote location where repair parts can be difficult to obtain. Make sure the fuses are sized appropriately (slightly above the pressure washer's 85 amp draw, and based on the current-carrying capacity of the #2 AWG conductors if the conductor is your limiting factor). The fuse should be a time-delay fuse (like a Class RK5) to handle the inrush current of the motor.
Additional Considerations and Recommendations GFCI Protection
The manual's recommendation for GFCI protection is crucial. However, GFCI protection for 3-phase equipment, especially at this amperage, can be tricky and expensive. You'll need a 3-pole GFCI breaker designed for industrial applications. Research the availability and cost of a 100-amp 3-pole GFCI breaker and ensure it meets local electrical codes. The GFCI requirement may also be fulfilled by using a GFCI rated receptacle, or at the disconnect.
Overcurrent Protection
The pressure washer's rating plate should give the "Max Overcurrent Protection" (MOCP) size. This dictates the maximum size breaker or fuses you can use. In no case can you exceed that value. This is to protect the internal components of the machine.
Voltage Drop
With 60 feet of cable, voltage drop could be a concern at 85 amps. While #2 AWG copper will likely be acceptable, calculate the voltage drop to ensure it's within acceptable limits (typically 3% for power circuits). Online voltage drop calculators are readily available. You may need to increase the conductor size to #1 AWG if voltage drop is excessive.
Amperage and Wire Sizing
#2 AWG wire is rated for 95 amps. Because the pressure washer is only rated for 85 amps you are fine in this case. The wire should be rated for the appropriate temperature which is generally 75 degrees Celcius for building wiring, however local electrical codes dictate if there are different requirements.
Receptacle and Plug
Ensure the pin and sleeve connector is rated for the appropriate voltage (208V 3-phase), amperage (100A is fine), and is NEMA 4 or better (watertight) for the garage environment. Hubble is a good brand. Ensure that the plug and receptacle are rated for the appropriate amperage and voltage.
SOOW Cable
Ensure the SOOW cable is rated for outdoor use and is oil-resistant. Also, be sure to verify that the 4C #2 AWG SOOW cable actually exists in your inventory and is in good condition. A visual inspection is necessary.
Teck Cable Grounding
Make sure the Teck cable is properly grounded according to code. The armor of the Teck cable must be terminated properly with approved fittings to ensure a reliable ground path.
Local Electrical Codes
This is critical. While the information provided here is based on general electrical principles, you must consult with your local electrical inspector or a qualified electrician familiar with Nunavut electrical codes. They can provide specific guidance based on local regulations and environmental conditions.
Bill of Materials (Example - Adapt to your situation and verified inventory) 100A 3-Pole Breaker (if needed to upgrade existing breaker) 60 feet of 3C #2 AWG Teck Cable (Confirm Inventory and Condition) Teck Cable Connectors (appropriate for #2 AWG Teck) 100A Fused Disconnect Switch (240V 3-Phase) Fuses for Disconnect Switch (sized appropriately - see above) 4C #2 AWG SOOW Cable (Length as needed - Confirm Inventory and Condition) Hubble 100A Pin and Sleeve Receptacle (208V 3-Phase, NEMA 4) Hubble 100A Pin and Sleeve Plug (208V 3-Phase, NEMA 4) Cable Grips/Strain Relief for SOOW cable connections Grounding Connectors as needed Warning Labels (Voltage, Amperage, GFCI Protection - if installed)Steps to Take1. Verify Inventory
Absolutely confirm the availability and condition of the #3 Teck and #2 SOOW cable.2.
Consult Local Authority
Contact your local electrical inspector or a qualified electrician familiar with Nunavut codes. Discuss your plan and obtain their approval.3.
Calculate Voltage Drop
Use a voltage drop calculator to ensure your cable length and conductor size are adequate.4.
Gather Materials
Order any necessary materials not already in stock.5.
Installation
Have a qualified electrician perform the installation, adhering to all applicable codes and manufacturer's instructions.6.
Testing
Thoroughly test the installation after completion to ensure proper operation and safety.
Important Note: Electrical work can be dangerous. If you are not a qualified electrician, do not attempt this installation yourself. Hire a professional. Flag for review