Question: At 480v for 150kw I'm coming up with 180A power needed. Does that make sense? Geez that's big wire for these heaters.
Let's break down the calculation and the potential considerations
Calculation
Kilowatts to Watts
150 kW = 150,000 W
Three-Phase Power Formula
P = √3 V I PF (Where P = Power, V = Voltage, I = Current, PF = Power Factor)We need to make assumptions on the power factor. For heaters, the power factor is often very close to 1 (unity). We'll calculate both with unity and .8.
Scenario 1: Power Factor = 1 (Unity) 150,000 W = √3 480 V I 1 150,000 W = 1.732 480 V I 150,000 W = 831.36 I I = 150,000 W / 831.36 = 180.43 AScenario 2: Power Factor = 0.8 (More conservative) 150,000 W = √3 480 V I 0.8 150,000 W = 1.732 480 V I 0.8 150,000 W = 665.09 I I = 150,000 W / 665.09 = 225.5 AConclusion
Yes, your calculation of approximately 180A is correct assuming a power factor of 1. If the power factor is lower (more inductive or capacitive load), the current will be higher.
Why This Matters (Heater Considerations) Resistive Loads
Heaters are generally resistive loads, meaning their power factor is usually very close to 1. However, confirm the manufacturer's specifications for the heater's power factor. If it's anything less than 0.9, use the lower power factor calculation.
Nameplate Data
Always use the nameplate data on the heater(s). The nameplate should provide the exact voltage, wattage, and required amperage. This is the most accurate information.
Heater Configuration
Are these multiple heaters wired in parallel? The total current would be the sum of the individual heater currents. Are they wired in a delta or wye configuration?
Wire Sizing and Overcurrent Protection NEC (National Electrical Code)
Wire sizing and overcurrent protection must comply with the NEC and any local codes. This involves more than just calculating the amperage.
125% Rule
The NEC typically requires that conductors be sized for at least 125% of the continuous load (which heaters often are). So, for the 180A calculation, you'd need to size the conductors for at least 180A 1.25 = 225A. For the 225.5A calculation you'd need to size the conductors for at least 225.5A 1.25 = 281.9A
Ampacity Tables
You'll need to consult the NEC ampacity tables (Table 310.16) to determine the correct wire size based on the ampacity and the insulation type.
Temperature Correction
The ampacity of the wire is also affected by the ambient temperature. If the wiring is in a hot environment, you'll need to derate the ampacity.
Conduit Fill
The number of conductors in a conduit affects the ampacity. You need to apply derating factors if the conduit is heavily filled.
Overcurrent Protection
The overcurrent protection (circuit breaker or fuses) should be sized to protect the conductors and the equipment. The rating of the overcurrent device should not exceed the ampacity of the conductors (after any derating) and should also comply with the heater manufacturer's recommendations.
In Summary and Recommendations1. Verify Power Factor
Confirm the heater's power factor from the manufacturer's documentation. If in doubt, use a power factor of 0.8 for a more conservative calculation.
2.
Check Nameplate Data
The nameplate on the heater is the definitive source for voltage, wattage, and current.3.
Calculate Current Accurately
Use the correct formula (P = √3 V I PF) and the correct voltage and power factor.4.
Apply the 125% Rule
Size the conductors for at least 125% of the continuous load.5.
Consult NEC Tables
Use the NEC ampacity tables to determine the correct wire size, considering temperature correction and conduit fill.6.
Choose Overcurrent Protection
Select an appropriate overcurrent device (circuit breaker or fuses) that protects the conductors and the heater.7.
Engage a Qualified Electrician: This is essential! Wiring a 150kW heater is not a DIY project. A qualified electrician will have the knowledge and experience to ensure the installation is safe, code-compliant, and reliable. They can also perform voltage drop calculations to ensure adequate voltage at the heater terminals.Yes, 180A (or higher, depending on power factor) is a significant current, requiring appropriately sized conductors and overcurrent protection. It's not unusual for high-power heaters. Do not underestimate the importance of proper wiring and safety. Flag for review